Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > THE OWNER'S CORNER FORUMS > Entegra Owner's Forum
Click Here to Login
Register FilesVendors Registry Blogs FAQ Community Calendar Today's Posts Search Log in
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 10-23-2018, 01:49 PM   #1
Registered User
 
Join Date: Jan 2018
Posts: 1,385
GFI's?

Today I drove the coach to get fuel, and to Speedco for an oil change.

When I got back, I noticed the Trav'ler wouldn't power up.
I looked in the right side (inverter) breaker panel and saw both the Living Room and Kitchen GFI Breakers were popped. I reset them and they popped again.
The Magnum panel indicated "inverting" as it should.

I plugged the coach into shore power, and I was able to reset the breakers and everything is normal.

I'll unplug again tomorrow and test, but does this ring any bells with anyone?
oneknight is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-23-2018, 04:52 PM   #2
Member
 
jobobjet's Avatar
 
Join Date: Sep 2015
Posts: 90
No help here but you are not alone. I have been trying to isolate this issue for a couple of months now. So far, I can't reproduce the problem.
__________________
Jonny
2017 Aspire 44B
jobobjet is offline   Reply With Quote
Old 10-23-2018, 05:00 PM   #3
Senior Member
 
TurboDaveTX's Avatar
 
Entegra Owners Club
Spartan Chassis
Join Date: Mar 2011
Location: Dallas, TX
Posts: 550
Had a similar problem earlier this month. At first I thought it was a breaker, but found the GFI kicked. Reset it and it kicked again. Unplugged everything on that line and it kicked again. Only thing in that line was USB charger outlet. No such outlet was available in the area we were in, so I replaced it with a standard 15A outlet. Problem solved! Ordered a replacement USB outlet from Amazon and installed it when we returned home. USB outlet works with no GI kicking. Don’t know if there is a way of checking a USB charger outlet for ground faults!
__________________
F78957
2015 Entegra Cornerstone 45B - Cayenne
2020 F150 Raptor SVT "Lead Foot"
TurboDaveTX is offline   Reply With Quote
Old 10-23-2018, 05:22 PM   #4
Senior Member
Commercial Member
 
Join Date: Aug 2012
Posts: 726
GFCIs will not reset if no power is being applied. You need a meter to verify the 120vac is actually coming from your Inverter. Also, your Inverter may have a breaker on it that needs reset.
__________________
Traveling RV Doctor
https://www.facebook.com/Traveling-R...5780632151951/
shiggs68 is offline   Reply With Quote
Old 10-24-2018, 04:01 PM   #5
Registered User
 
Join Date: Jan 2018
Posts: 1,385
I found time to do some testing today.

When I unplug from shore power, the 2 GFI breakers in the inverter circuit panel trip.
Today I'm able to reset them while unplugged and they stay reset.
Other breakers in this panel are not affected, the microwave isn't losing it's time, the fridge doesn't blink, The inverter inverts, nuttin else wrong.
oneknight is offline   Reply With Quote
Old 11-08-2018, 10:27 AM   #6
Registered User
 
Join Date: Jan 2018
Posts: 1,385
I did some further testing on this today, and got out my voltmeter.

The inverter is working fine.

I have 7 volts AC nuetral to ground on every outlet (inverter and non inverter) in the bus on shore power.
Without shore power, I get 1.5 to 2 volts neutral to ground on the outlet in the bedroom, it's the only one I could easily access that is on the inverter but on the tripped gfi breakers.

Something seems to have come loose. any ideas?
oneknight is offline   Reply With Quote
Old 11-08-2018, 10:41 AM   #7
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
In theory you should have no difference between neutral and ground. The generator has them bonded (connected) at the generator. The shore cord should have them connected at the socket along with a connection to a ground rod. That leaves the Inverter. Assuming it switches both the neutral and hot leads or has a neutral common buss I would be looking for a bad connection there.

It would help if you had a schematic of the Inverter or could call their help line with your problem. If you can do that I would tell them what you found and see if they have an answer. I'm hesitant to tell you to just connect neutral to ground as the Inverter might have a current sensor in the return side of the AC line. Shorting that out might not be a good idea. In fact it is probably a bad idea assuming it is there.
nothermark is offline   Reply With Quote
Old 11-08-2018, 01:25 PM   #8
Senior Member
 
Join Date: Jul 2017
Location: Cypress, Tx.
Posts: 1,160
I agree that there should be no voltage between neutral and ground. I would first go to the pedestal and see if you have a difference there. If there is a difference there I would get where you are staying's owners involved so they can get the problem fixed before someone dies of electrical shock.

On a side story I have a friend the owns a campground in Bolivar Texas. He has a customer tell him that he was getting shocked when he touched his RV when he was standing on the ground. My friend said he has seen the problem before and grabbed his volt meter to go help his customer. Turned out that the problem was coming from the power company. He called the power company and after talking to a few people he got someone that understood what he was saying. A crew from Energy came out and found that the salt air from the gulf had caused tracking between the neutral and the ground. They ended up washing down a few of their poles and the problem went away.
__________________
2014 Foretravel IH45
Houston (Cypress), TX.
Turbojack is offline   Reply With Quote
Old 11-08-2018, 11:49 PM   #9
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
The problem with large Inverters is that they also contain a second transfer switch that can interrupt the neutral as well as the hot leads. That isolates them from the bonding at the power pole.
nothermark is offline   Reply With Quote
Old 11-09-2018, 03:55 AM   #10
Senior Member
 
MRUSA14's Avatar
 
Entegra Owners Club
Join Date: Nov 2012
Posts: 8,137
It could be the GFI outlet itself. I have had to to replace bad ones in my home. New outlets solved the issue
__________________
Marc and Jill, Wellington FL
2013 Entegra Anthem 44SL
2018 Lincoln MKX
MRUSA14 is online now   Reply With Quote
Old 11-09-2018, 11:23 AM   #11
Registered User
 
Join Date: Jan 2018
Posts: 1,385
OK.

In the main fuse panel, I turned off the breaker feeding the inverter.
the magnum 2800 switched smoothly from "float charging" to "inverting"
Nothing tripped. Everything still has power.

I turned off the 50 amp breaker on the shore pole. No change

I turned the inverter feed breaker back on. No change.

I turned shore power back on. No change.

I turned shore power off. The "living room" and "kitchen" GFI breakers both tripped and would not reset.
No matter what I did, these breakers tripped, until I restored shore power.
oneknight is offline   Reply With Quote
Old 11-09-2018, 01:58 PM   #12
Senior Member
 
voltdoc's Avatar
 
Entegra Owners Club
Join Date: Oct 2010
Location: East Greenwich, RI
Posts: 2,300
GFCI will trip if:

1) there is any difference in the power sensed flowing thru the hot conductor and the neutral conductor.
2) if the ground and neutral are shorted on the load side of the GFCI (because it creates the imbalance mentioned in #1)

Have you unplugged everything from every outlet and tested for normal behavior?

By code, shorepower electrical if wired properly bonds the Neutral and ground at the primary service panel. There can be only one place where neutral and ground are bonded. So when shorepower is disconnected the inverter takes over and also internally bonds neutral and ground together at the inverter. For further reading on how the Inverter does this see section 2.65 in the manual.

If neutral and ground are bonded elsewhere at the same time it can cause ground loops and possible erratic behavior of devices like GFCI.

Not easy to check, but one possibility is an additional ground to neutral bond exists in the breaker panel itself. This could be an accidental short as the neutral and ground buss bars are very close together in those panels (bottom of photo). Likewise, if the panels come stock with a ground/neutral bonding strap perhaps it wasn't removed.

BTW, I checked an outlet on my coach (which does not have any issue like this) and the neutral to ground voltage using an RMS meter was 3.2v. Not sure if that is relevant.

Good luck!
__________________
Rob & Linda https://MyQuantumDiscovery.com
2017 Entegra Aspire 44B - 2021 Jeep Grand Cherokee L Overland
2013 Entegra Aspire 42RBQ
voltdoc is offline   Reply With Quote
Old 11-10-2018, 06:05 AM   #13
Registered User
 
Join Date: Jan 2018
Posts: 1,385
Thanks Rob, everything helps, particularly from someone who owns a similar (identical) coach!

This affects BOTH GFI breakers in the inverter subpanel. The kitchen breaker all the time, the living room breaker most of the time.

It has not always been this way, this is new behavior.

What in the world could affect both inverter GFI circuits (but not affect the basement or bathroom GFI circuits in the other (main) panel)?

This is kinda a pain, as the coach is basically not useable unless I have shore power.
Also, the dishwasher drawer isn't locking during travel (since it doesn't have power)
oneknight is offline   Reply With Quote
Old 11-10-2018, 06:38 AM   #14
Senior Member
 
Join Date: Sep 2012
Posts: 8,055
The voltage between neutral and ground bothers me. It tells me there is no bonding because a connection is open somewhere. That is probably what is tripping the GFCI's.
nothermark is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Convert GFI to non-GFI RV Vagabond iRV2.com General Discussion 28 12-14-2016 06:55 AM
GFI Problem Vette Racer 5th Wheel Discussion 9 09-12-2007 04:18 PM
Bye-Bye GFI 56Nomad Toy Haulers Discussion 4 09-26-2005 07:28 PM
GFI Problem and Cure Roy W. 5th Wheel Discussion 3 09-06-2005 04:29 AM
GFI and other outlet problems Journey Greg Winnebago Industries Owner's Forum 3 07-26-2005 09:20 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:10 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.