Anyone know how to hook up the loss of site power off for the generator auto start wires in a 2014 Anthem and where to connect them.
|
We have a 14 Anthem and I added the shore power sense wiring to make the AGM start with loss of shore power.
I added a single 15 amp breaker to the left side of the breaker panel above the driver. The left side is shore power. I ran romex from the breaker panel around the front of the cap behind the cabinets to the cavity behind the instrument panel above the entry door. Terminated it with a 120 v receptacle and plugged in a 12v transformer to supply the shore sense power.
Remove the EC30 panel and on the back there is a connector with 16 cavities. cavity 14 should be the 12+ for shore power sense and cavity 13 is the shore power sense ground. these are the two you need.
You also need to know Cummins Power Generation (574) 262-4611. Hopefully Grover Simpson is still there. He (or his fill-in) is who you will need to talk to.
The AGM autostart with loss of shore power would not work by simply hooking up the wires as described. The module needed to have the software or calibration updated to 4.0 for the AGM to work correctly when shore power is lost. My module was "obsolete" and would not accept 4.0. I had to buy a new module and have Grover reprogram it for me. He helped orchestrate the new module purchase and intercepted it before it was sent to me and updated the software to 4.0.
Possibly if you simply purchase the latest and greatest replacement command 30 module it has the 4.0 in it already as 4.0 was "new" at the time back in 2014.
Once plugged into the new module with 4.0 the shore power loss AGM worked perfectly. We have had it activate a number of times due to campground power outages and it always has worked perfectly.
Look at your module to see if the terminals are numbered. They are not numbered logically. 14 is the third cavity from the left on the bottom row and 13 is the fourth cavity from the left.
This is all from ancient notes from when I did the mod years ago so your results may vary! Good luck but definitely contact Cummins Power Generation (formally known as Onan) to check the details of your command 30 module