Onan 12.5 KW Generator

We have nothing but problems with this generator. Now needs the fourth set of brushes. Stator has been replaced. Now we are told it needs a rotor. Only 700 hours on the unit. Onan WILL NOT cover any of this because it has over 500 hours. Is this Onan's policy: Put bandaids on problems until warranty is up; then deny any responsibiity for manufacturing defects?
__________________

__________________
2018 Newmar Dutch Star 4369, Spartan K2 Chassis,
Cummins ISL 450HP, Allison 3000

2015 F-150 King Ranch LB 3.5 L twin turbo Ecoboost Toad, Texas Boomers RV Club
FMCA F292298, NRA Benefactor, Newmar KK Lone Stars South
Dutch Star David is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-27-2017, 03:21 PM   #2
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 6,317
Blog Entries: 1
My Onan has performed flawlessly and has been no problem, but then again, I am currently at about 150 hours. My fingers are crossed that I have years of no problem. Because of the no-problems, I have not had any experience with working with the company (sorry).

Seems to me that you have essentially 2 choices: repair it, or not repair it. I would be frustrated with the cost because I would expect that most generators should be able to run for thousands of hours before needing major overhauls.

Good luck....

Gary
__________________

__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5Fi
Gary.Jones is offline   Reply With Quote
Old 08-27-2017, 03:41 PM   #3
Senior Member
 
DSL417's Avatar
 
Entegra Owners Club
Join Date: Sep 2012
Posts: 6,375
Blog Entries: 2
I am approaching 500 hours on mine...once the Command 30 was fixed, no problems with the whole system.
__________________
Dave and Beth
2015 Cornerstone 45J
Ford F-150 and 2016 Polaris Razor
DSL417 is online now   Reply With Quote
Old 08-27-2017, 05:02 PM   #4
Senior Member
 
Dieselgem's Avatar
 
Join Date: Sep 2007
Location: PA & FL
Posts: 797
I have over 1200 hrs on ours, use it hard and service it every 250 hours. We run it a lot to replace the insufficient dash air.
__________________
2015 Cornerstone (Classic) 45B Topaz
2017 JKU Rubicon
Dieselgem is offline   Reply With Quote
Old 08-27-2017, 05:16 PM   #5
Senior Member
 
brobox's Avatar


 
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 21,443
Dave, that does not sound normal at all. Out of curiosity, have you let the generator warm up for 2 minutes before putting a load on it, then taking the load off 2 minutes before shutting down?
__________________
Chuck in SW FL
A "Digital" 2019 Cornerstone "B"
A "Classic" 2014 Anthem 42 RBQ---Sold
2016 Colorado Z71 PU
brobox is offline   Reply With Quote
Old 08-27-2017, 05:24 PM   #6
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Winnebago Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 36,390
Quote:
Originally Posted by brobox View Post
Dave, that does not sound normal at all. Out of curiosity, have you let the generator warm up for 2 minutes before putting a load on it, then taking the load off 2 minutes before shutting down?
Mine has a delay built in for starting but I just shut the gen down when done. I have just over 400 hrs on mine.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '14 Jeep JKU Dragon Edition
Mr_D is offline   Reply With Quote
Old 08-27-2017, 05:50 PM   #7
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 6,317
Blog Entries: 1
I should not say this...... but I have not worried about a load or no load on the generator for whatever period of time anyone says.... If this really was a problem, Onan or the Command 30 would build this "in". I have said before, but will repeat......a first year electrical engineer (or many 10th graders in high school) would take no more than 30 minutes to design the circuit and make the circuit board to accomplish the initial delay and the shut down cool down period. This has to be a "wives tale". These generators are designed to handle 12.5 Kw of power. I have a 50 Kw Onan totally automatic natural gas powered generator powering my whole house with two computer controlled 200 amps of 240 V load shedding transfer switches, and it idles about 30 seconds before it takes the entire house at full power (engine is a Ford V-6), and it idles down for about 30 sec after a continuous 2 day hurricane power episode.

My Command 30 does not throw the load to the genny until about 40 seconds after start. I have not worried about shut down. Now I may regret writing this, but so far so good.

If this ever made any sense, I would guess it was at the period of time when we were advised to let our Cummins cool down and gradually warm up, and I believe everyone knows that Spartan now says, no need for any of that ..... that was a recommendation on "old" diesel technology, but not current models.

On a different aspect of this thread, I generally do not need to run the genny during travel, even during the summer in the south. Since there are only of two of us and we are "always" belted into our official chairs when moving, we have found the dash AC (now that it has been fixed) keeps the cab comfortable. We have added roof ACs a couple of time when the outside temp is literally up in the 100s and the cab dash just can't do the job.

Gary



Gary
__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5Fi
Gary.Jones is offline   Reply With Quote
Old 08-27-2017, 05:59 PM   #8
Senior Member
 
lowejug's Avatar
 
Join Date: Oct 2013
Location: st george
Posts: 1,298
Yes. This also seems not right to me.. these generators are designed to run ... I have seen some of these over 4,000 hours and only basic services were done... at 500 hours it's probably not even broke in.
Seems you have something going on causing your continued issues
IMO
lowejug is offline   Reply With Quote
Old 08-27-2017, 06:20 PM   #9
Senior Member
 
brobox's Avatar


 
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 21,443
For those that do not follow the owners manual, that's OK. However, here is the copy and paste from the current Onan 12500 owners manual. I figured Cummins wrote this procedure for a reason.

10
Starting And Stopping Procedures
Your Cummins Onan generator can be started and stopped from the integral
control panel on the generator, or from the optional remote control panel inside the
vehicle if your RV is so equipped. Your Operator’s Manual outlines the simple steps
for starting and stopping. Remember to:
• Before starting the generator, turn off air conditioners and large electrical loads.
• Before starting in cold weather, turn off all appliances for best long-term
performance.
• Prime by holding stop (all Quiet Diesels, Quiet Gas 3600-7000).

To start
- press and hold start at the control panel or at the set.
- Quiet Diesel: auto pre-heat flash, then crank/start
- Don’t over-crank with no start
• Before turning on appliances, let the generator warm up for a few minutes.

Turn off air conditioners and large electrical loads and allow the generator to run
for 3-5 minutes before stopping, to allow the generator to cool down.

Link to Cummins manual https://power.cummins.com/sites/defa.../F-1123-EN.pdf
__________________
Chuck in SW FL
A "Digital" 2019 Cornerstone "B"
A "Classic" 2014 Anthem 42 RBQ---Sold
2016 Colorado Z71 PU
brobox is offline   Reply With Quote
Old 08-27-2017, 06:35 PM   #10
Senior Member
 
philnail's Avatar


 
Entegra Owners Club
Join Date: Aug 2012
Location: Full Time - Most of the time we are lost.
Posts: 446
I have around 1500 hours on mine. Only issue I have had is I start generator and right away it stops with error code. Easy fix. I pull out generator and pull side cover. Take 3 number 10 screws out which holds the radiator bottle and slide it out. Then I remove the wire harness connector from the brain and reseat it. Generator fires right up and I am good for another 300 hours till it happens again
__________________
BBQ-Guy
philnail is offline   Reply With Quote
Old 08-27-2017, 06:57 PM   #11
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 6,317
Blog Entries: 1
Chuck, I'll give you a progress report in 5 years and we can compare notes.

Gary
__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5Fi
Gary.Jones is offline   Reply With Quote
Old 08-27-2017, 08:14 PM   #12
Senior Member
 
Join Date: Sep 2014
Location: Land of 10k Lakes, MN
Posts: 150
I recently had the fuel pump fail 1 month out of warranty with ~975 hours on it. Failure seemed premature to me.
__________________

__________________
W. Family
2013 Entegra Cornerstone 45k w/Bunkhouse Mod
2014 GMC Savana 3500 4x4 Toad
xtechgeek is offline   Reply With Quote
Reply

Tags
generator, onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
5500 Onan vs 7000 Onan HUGHP MH-General Discussions & Problems 10 07-16-2016 08:09 PM
Onan 6.5 Onan Emerald Plus Fuel Filter Afubar RV Systems & Appliances 13 01-13-2016 09:40 PM
What's the difference: Onan 5.5 Marquis Gold, Vs. Onan QG 5.5? 1943D18 RV Systems & Appliances 2 05-07-2013 02:22 PM
Retrofit Onan Carb with Commercial Onan Fuel Injection? DrLew iRV2.com General Discussion 10 01-23-2012 10:34 AM
Onan Generator Repairs pdrduz Class A Motorhome Discussions 3 01-06-2009 12:57 AM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 10:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
×