I was going to post this as I returned from 2 months with the Gkids touring the southwest. However, I decided to wait and see if I settled down. Well, it's been a month + and I'm not settled down. The issue is power (the electric kind). This trip I lost the circuit board on the W/D and a start/run capacitor for the rear HVAC unit. It was because of low power. Consistently, from New Mexico to California back to Utah. Almost every CG we stayed at had low power. I realize this is summer in the desert and the A/C was always running (it seemed that way). However, the CGs were no more than 20% occupied, really. These CGs were having a bleak year. If it were not for me and the Europeans renting all the class C coaches, there would have been nobody at these CGs. When inquiring inquiring about low power most staff were quite helpful. Several of the parks, where I was tripping their main panel breaker for the section we were in showed me their master panel (please understand, with all my high draw appliances running I can draw only about 52 AMPS). In every single case I counted the main CG breakers. To make a long story as short as possible how can a 150 + site CG have only 800 AMPs coming into it? Are these people just cheap or totally ignorant? Is this a way to lower the electric bill? This was the trend, not a single incident. I also received the usual comments like "we have this problem all the time". In each case, I put my cheater cable on the line and I was drawing 37 +/- AMPs. This popped their section main breaker or my site breakers! This is on a supposedly 50 AMP service!

The cure? I did something I've said I'd never do. I purchased a voltage regulator. So, I am out the $s for the broken appliances and I'm out $600+ for the voltage regulator. I'm also out all the aggravation and suffering to work through all this. If you want some excitement, get on your coach roof, in the desert, in the summer.

I forgot to mention, throughout all this my Surge Guard was cutting power to the coach, from time to time. And turning off the A/C is not the answer in the desert with consistent 110+ F temps.

If there are any CG owner/operators reading this, I'd like to know your view of buying the correct size electric service for your CG. Do you? If not, why not.

I rarely sound off, but his really has me irritated. Thanks for listening.
__________________

__________________
Gary
2005 Newmar KSDP 3910 + GMC ENVOY XUV 37K lbs Moving Down The Road
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
GaryKD is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-11-2009, 07:27 AM   #2
Senior Member
 
read & learn's Avatar
 
Newmar Owners Club
Join Date: Sep 2006
Location: Edgewater, NJ-Now touring the USA
Posts: 955
Gary
When we were in CA we had the same type of problem, but we were there over the winter months. While we were there the temperture did go into the upper 80's low 90's a few times. We just blamed it on CA as not having enough power and we were having brown outs. NM and AZ temps were 70's so really did not notice problem.
Remember DW asking a couple of times if we had 30 or 50 amps.
Texas ate the surge protector Hmmm.
__________________

__________________
2005 KSDP 3910-----2007 Jeep Liberty

THE MIND IS LIKE A PARACHUTE, IT MUST BE OPEN TO WORK
read & learn is offline   Reply With Quote
Old 09-11-2009, 07:49 AM   #3
Registered User
 
Excel Owners Club
Join Date: Jan 2007
Location: North of the Mason Dixon Line
Posts: 1,565
Gary, Itís the old saying you get what you pay for. The cheaper costing camp groundsí are charging less for a reason.
__________________
BookIIRoadtrash is offline   Reply With Quote
Old 09-11-2009, 08:12 AM   #4
Senior Member
 
GaryKD's Avatar
 
Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 12,322
Hi Highplains Drifter,
Why do you assume I was staying in cheap CGs? From New Mexico through southern AZ, to California and back through Nevada, northern AZ and up into Utah the CGs we stayed at had quite a variety. From family operated CG along the Interstates to KOAs, casino sponsored and such long established CGs as 29 Palms. It mattered not the brand or cost of the site (over $60/nite at Gouldings). The problem was the same.

For me, it is obvious CG owners put in 50 AMP pedestals and advertise 50 AMP service. Unfortunately, they did not purchase a larger electric service to compliment all the 50 AMP CG infrastructure. So, now customers are stuck with, what amounts to fraud. CGs can't deliver what they advertise. The incoming electric service is the same as it was when the pedestals were all 30 AMP.

As a private citizen, I can not get away with this. When I replaced my stick house HWH with a tank less HWH the electrician said I didn't have enough power into the house! The installation would not pass the Village inspection. The bottom line I had to go to a 400 AMP service (from a 200 AMP service). It is unfortunate CG owners are not having to comply with the same kind of code enforcement.
__________________
Gary
2005 Newmar KSDP 3910 + GMC ENVOY XUV 37K lbs Moving Down The Road
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
GaryKD is offline   Reply With Quote
Old 09-11-2009, 08:29 AM   #5
Registered User
 
Excel Owners Club
Join Date: Jan 2007
Location: North of the Mason Dixon Line
Posts: 1,565
I hear ya Gary, but I have seen it many times the installers don’t speak English, but they are hard workers and cheap!
__________________
BookIIRoadtrash is offline   Reply With Quote
Old 09-11-2009, 11:21 AM   #6
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,799
There is a device called an autoformer.. A few different companies make them, Mine is a Hughes. What this does is measure the voltage and if it's low it "Boosts" the voltage but cutting in a transformer winding.

I understand there is at least one make which can also, in the event of HIGH voltage, "Buck" (Switch the same coil in in reverse)

How well do they work? Not sure

As I said, I have one.. Installed.. About 5 weeks or so ago I was plugged into a 30 amp site and the air conditinoer kept tripping it's breaker

now there are only 3 things that can cuase that

Bad AC
Bad Breaker
LOW VOLTAGE

when I moved to a a new park, Plugged into a nice NEW 50 amp outlet (less than a year old) ... No more CLICK of darkness.

(it was the branch breaker, not the post breaker, tripping)
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 09-11-2009, 12:01 PM   #7
Senior Member
 
GaryKD's Avatar
 
Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 12,322
Hi wa8yxm,
There are several different brands of voltage regulators to choose from. Hughes is one of the brands. They all work the same basic way, via a transformer. Each brand has its' own way of specing out the transformer and how, when and how much it will adjust (boost) the power. Each brand also has their own way of displaying what is going on with the power.

I'm not an EE so bear with me. As best I know, they do not boost the power. They adjust the AMPS which raises the volts. WATTS remain constant because the appliance will draw the WATTS it is rated for. If WATTS is constant and volts drop, AMPS must increase. The transformer remedies this situation. Okay, any EEs want to jump in here? If you do, keep it simple for the rest of us.
__________________
Gary
2005 Newmar KSDP 3910 + GMC ENVOY XUV 37K lbs Moving Down The Road
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
GaryKD is offline   Reply With Quote
Old 09-11-2009, 12:50 PM   #8
Community Administrator
 
Route 66's Avatar


 
Newmar Owners Club
Retired Fire Service RVer's
Spartan Chassis
Join Date: May 2000
Location: Newark, DE
Posts: 25,611
I think that's backwards.

Transformers either raise or lower voltage.

These units are transformers and they are used to raise the voltage, which causes the amps to drop.

Volts X Amps = Watts

From Surge Guard's website.

Quote:
The (SGVR) continuously monitors line voltage conditions and
uses a unique implementation of a special transformer to increase the
incoming voltage to an acceptable level when low incoming line
conditions exist. In the Boost mode the (SGVR) raises the output
voltage by 10% over the incoming line voltage.

From the Hughes Autoformer website.

Quote:
What it is doing is changing the voltage - amperage relationship, lowering the amperage and raising the voltage. Since appliances run better on higher voltage, lower amperage, less overall power is used from the park, and better service is enjoyed from your RV
__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, previously 4 years as a fulltimer in a '07 DSDP

Route 66 is online now   Reply With Quote
Old 09-12-2009, 08:07 AM   #9
Senior Member
 
Bob (WA0MQE)'s Avatar
 
Monaco Owners Club
Join Date: Jun 2003
Location: Between Colorado Springs, CO & Fulton, TX
Posts: 1,515
Blog Entries: 1
Yes, but GaryKD is correct that if you boost the voltage the current available will drop, and vice/versa. It's pure physics in the sense that you can't get something without giving up something else. At least when it comes to electrical systems.

But at least it could make a difference in damaging electrical appliances/components.
__________________
Bob 2006 Monaco Camelot 40PDQ
US Navy Carrier Battlegroup 1959/1963
Summer in Colorado, Winter Texas Gulf Coast
Bob (WA0MQE) is offline   Reply With Quote
Old 09-21-2009, 12:56 AM   #10
Senior Member
 
porscheracer's Avatar
 
Join Date: Apr 2008
Location: Back at the stix'n'brix - East End, AR.
Posts: 553
Quote:
Originally Posted by Bob (WA0MQE) View Post
Yes, but GaryKD is correct that if you boost the voltage the current available will drop, and vice/versa.
Replace "available" with "required" and you have it.

In my area, 325A service is the largest "residential" pipe available. Going to 400 puts you at a commercial rate.

Which brings up a potential answer to the "why not" question. In many areas, service above certain levels (800A, maybe?) puts you into an industrial classification. In many areas, also, industrial is based on peak load - not actual KWH usage. And the load measured is the daily high. Each day's billing depends solely on that number.
__________________
Norm & Janet

FMCA; WIT; FCOA; Good Sam; Passport
porscheracer is offline   Reply With Quote
Old 09-21-2009, 06:34 PM   #11
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 22,799
The one time I measured low voltage.. Was the middle of winter. Park was nearly empty. Next door was a "Wind Farm" They make electricity using wind power) 100mph "Breeze" (I am not kidding)

Another time I am sure of low voltage but I did not measure it.. About 20 feet from where I"m typing.

Some parks I have stayed at had a "NO AUTOFORMERS" Policy. I guess if you plug in an autoformer they either bill you more or ask you to leave

So.. My autoformer is installed.. where you can't see it.
__________________

__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
5th Wheel--can't power slideout/refrig yet can power microwave, wall outlets. Huhhh?? doodlebug52 5th Wheel Discussion 9 04-28-2009 10:47 PM
KVH Trackvision Power Switch Replacement Mike R Technology: Internet, TV, Satellite, Cell Phones, etc. 3 04-24-2009 06:48 PM
No aux power from house batteries John Trent Winnebago Industries Owner's Forum 7 02-17-2008 11:59 AM
Shore Power sjcaldal11 Newmar Owner's Forum 4 02-10-2008 06:35 AM
No Eletrical Power from Power Tech Generator Field Trip Newmar Owner's Forum 5 09-27-2005 06:23 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:49 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.