Posts: 29
|
5er wiring upgrade
Has anyone done/seen a 5er converted from 30amp to 50amp service? I have experience wiring houses with my father but have never attempted this kind of project. We have an '04 Cameo that is 30amp and are wanting the additional amperage due to running nearly everything off shore power (unlimited electric at our site). It seems to me that I'd have to install the 50amp box, divide the zones better, and swap out the 30amp connector on the side of the 5er. Any ideas/comments/recommendations? Will the factory wiring from the outside connector to the box support such an upgrade?
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
05-27-2014, 06:59 AM
|
#2
|
Senior Member
Join Date: Aug 2004
Location: Wherever we are
Posts: 4,288
|
__________________
'16 40QBH Phaeton
'21 Sahara HA toad
'15 38RSSA Mobile Suites--traded
'05 36TK3 Mobile Suites--retired but not forgotten
|
|
|
05-27-2014, 08:52 PM
|
#3
|
Senior Member
Join Date: Sep 2012
Posts: 4,232
|
Done it before. Some are easy, some cost more money. It depends on where the breaker box is and how hard it is to run a new wire from the shore connector.
|
|
|
05-28-2014, 05:42 AM
|
#4
|
Junior Member
Join Date: Apr 2014
Posts: 29
|
Great info wingnut. Thank you.
Jesilvas, what all did you do on yours?
One question I didn't ask...wouldn't it be a better idea for me to simply add a 50amp box/line/plug? I could divide up my zones better and provide much greater flexibility for all future electrical usage. My current campground (and most I've heard of) offer both 50 and 30 amp service. Wouldn't it be acceptable to use both at the same time?
|
|
|
05-28-2014, 08:21 AM
|
#5
|
Senior Member
Join Date: Sep 2012
Posts: 4,232
|
Wasn't mine but I've wired a couple.
I've completely replaced the power center with a 50A box because it was easy; plug was close to box.
I've added a separate box that then fed the OEM 30A box because it was a long way to run wiring and just easier.
Best thing is to change out the shore cord plug to a 50A, don't use 30A and 50A at the same time.
|
|
|
05-28-2014, 05:51 PM
|
#6
|
Senior Member
Join Date: May 2001
Location: Spicewood, Tx
Posts: 708
|
Buying a 50 amp shore power cord is the biggest expense. Last one I did was pretty ez and inexpensive. Mounted a $10 8 slot breaker box near the existing power center and ran the 50 amp cable to it. The existing box became a sub panel and I moved several circuits to slots on the new box to balance the load. There was plenty of excess wire length on most of the circuits, so no splicing or junction boxes. As a bonus, the 12V convertor had shared a breaker with other items and I was able to put it on a dedicated breaker.
__________________
Larry Day, Texas Baptist Men volunteer
'13 Silverado LT 3500HD D/A CCSB 2wd, custom RKI bed
'19 Starcraft Telluride 292RLS
|
|
|
05-30-2014, 11:49 AM
|
#7
|
Senior Member
Join Date: Jan 2014
Location: Houston TX
Posts: 103
|
I have seen some of these upgrades , mostly the 50 amp units use 12ga. wire for every outlet. Where 30 amp use 12,14,16 ga. It wasn't meant to handle the loads as a 50. Check your wall plates and such to be sure your upgrading far enough.
Jon
|
|
|
05-30-2014, 03:17 PM
|
#8
|
Senior Member
Join Date: Sep 2012
Posts: 4,232
|
All the trailers I've seen, 50A or 30A, still use 14ga wire for 15A circuits, 12ga wire for 20A circuits, and 8ga for 30A, and 6ga for 50A
|
|
|
05-30-2014, 04:08 PM
|
#9
|
Senior Member
Join Date: Jan 2014
Location: Houston TX
Posts: 103
|
The Teton and Carriage had 12ga, On almost all of the outlets. And I havent tore into any of the newer fifth wheels.
|
|
|
05-31-2014, 07:06 AM
|
#10
|
Senior Member
Join Date: Sep 2012
Posts: 4,232
|
Quote:
Originally Posted by jonbrown
The Teton and Carriage had 12ga, On almost all of the outlets. And I havent tore into any of the newer fifth wheels.
|
That's good to know. The majority (Keystone, Forest River) don't do that.
|
|
|
05-31-2014, 07:18 AM
|
#11
|
Senior Member
Join Date: May 2001
Location: Spicewood, Tx
Posts: 708
|
Quote:
Originally Posted by jonbrown
I have seen some of these upgrades , mostly the 50 amp units use 12ga. wire for every outlet. Where 30 amp use 12,14,16 ga. It wasn't meant to handle the loads as a 50. Check your wall plates and such to be sure your upgrading far enough.
Jon
|
Wire gauge can never be less than the breaker protecting an individual circuit. The gauge can be more, but not less. That is code, both residential and RV. Upgrading to 50 amp main service does not involve replacing existing individual breakers with higher amperage breakers. There are cases where a single breaker protects two separate circuits, but again the breaker must have a lower amperage rating than either wire gauge. I had that case with the converter and another circuit sharing a 15 amp breaker. With a low battery, the converter would draw almost 15 amps, leaving nothing for the other circuit.
Anyway, the primary reason for a 50 amp upgrade is not to provide higher amperage on an individual circuit, but to allow more circuits to operate near their individual rating capacities at the same time, like running the A/C, microwave, water heater and a hair dryer all at the same time.
__________________
Larry Day, Texas Baptist Men volunteer
'13 Silverado LT 3500HD D/A CCSB 2wd, custom RKI bed
'19 Starcraft Telluride 292RLS
|
|
|
06-02-2014, 01:38 PM
|
#12
|
Senior Member
Join Date: Sep 2013
Posts: 596
|
How many amps are you drawing now? Are you popping circuit breakers? If the problem is that too many outlets are on the same CB , it could be very expensive and time consuming to rewire them separately.
|
|
|
|