How can I test furnace operation of my Carrier Air V A/C-heat pump-furnace system? The manual says the heat pump will run and the furnace should start when the temp is below 40. It as not been that cold yet so I don't know if the furnace works. I'd like to know that it functions before I really need it. There should be a way to over-ride the system and run the furnace but I have not found it.
Anyone know how?
Thanks,
Dave
__________________

__________________
Big Red -- '99 F-350 PSD

Carri -- '05 Carri-Lite 36KSQ
Dualy Driver is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-30-2005, 11:30 AM   #2
Member
 
Join Date: Nov 2004
Location: FL Gulf Coast
Posts: 37
How can I test furnace operation of my Carrier Air V A/C-heat pump-furnace system? The manual says the heat pump will run and the furnace should start when the temp is below 40. It as not been that cold yet so I don't know if the furnace works. I'd like to know that it functions before I really need it. There should be a way to over-ride the system and run the furnace but I have not found it.
Anyone know how?
Thanks,
Dave
__________________

__________________
Big Red -- '99 F-350 PSD

Carri -- '05 Carri-Lite 36KSQ
Dualy Driver is offline   Reply With Quote
Old 02-02-2005, 11:05 AM   #3
Member
 
Join Date: Dec 2004
Posts: 56
there isn't an override on the unit vent? ( the part in the ceiling)?? i know you can over ride the AC that way
__________________
Daniel and Jennifer

San Antonio, Texas
DanJenn is offline   Reply With Quote
Old 02-02-2005, 05:28 PM   #4
Member
 
Join Date: Nov 2004
Location: FL Gulf Coast
Posts: 37
DanJenn,
With the "Emergency" button, I can force the unit into "heat" mode but not into "furnace mode". The manual says the auxiliary heat (furnace) will come on if the heat pump coil temperature/ambient temperature combination would cause coil freeze up. I haven't been able to simulate those conditions.
I also wonder how I would get heat if I didn't have "shore power" to run the heat pump. I may test it that way.
Dave
__________________
Big Red -- '99 F-350 PSD

Carri -- '05 Carri-Lite 36KSQ
Dualy Driver is offline   Reply With Quote
Old 02-03-2005, 02:45 AM   #5
Community Moderator
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,062
To bypass the heat pump is the way I would test the furnace. All you have to do is go to the furnace and the two wires that go to the t'stat can be seperated from the t'stat and jumped together. After the fan delay relay has heated up the fan will start and the furnace should begin it sequence to ignite and heat. This bypassing will not check the control circuits of the heat pump; ie, the outside coil temp and relays on the heat pump to control the furnace but will insure the furnace is operating when told by the control circuits.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Old 02-12-2005, 04:21 AM   #6
Member
 
Join Date: Nov 2004
Location: FL Gulf Coast
Posts: 37
Last night it got cold enough for the furnace to light. All systems worked as designed!
Dave
__________________

__________________
Big Red -- '99 F-350 PSD

Carri -- '05 Carri-Lite 36KSQ
Dualy Driver is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heat Pump and Gas Furnace dengraham Winnebago Industries Owner's Forum 10 02-28-2009 02:55 PM
Carrier Heat Strip max49 MH-General Discussions & Problems 5 09-12-2008 11:22 AM
Propane furnace vs. heat pump operating costs John_Canfield Winnebago Industries Owner's Forum 12 01-03-2008 05:44 AM
Heat Pump - No Heat - 2002 Journey PULLEY MH-General Discussions & Problems 5 09-12-2006 05:07 PM
Carrier Remote Controled AC and Furnace max49 RV Systems & Appliances 6 03-20-2006 08:02 PM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:13 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.