Front ac unit 13.5 on jayco pinn. 36rsqs 2013

I am having problem with my ac ducted unit in my front bedroom .when I have ac unit running it shuts off every five minutes or so and turns back on in thirty seconds .the unit is domestic penguin 13.5 unit with wall thermostat.when I have down draft door open on unit it works great but when I close down draft door to run through duct work it starts acting up .i feel air coming through bathroom duct and kitchen duct from that unit running so it is moving air alright and in living room .my back unit 15 btu works fine with down draft door open or closed. The front unit water drip pan on ac unit works great and drain away from unit to roof and down down spouts great .let me know if anybody has this problem .
Rcnewell11 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-08-2013, 09:37 PM   #2
Senior Member
 
Join Date: Sep 2012
Posts: 4,232
You could have an issue with freezing due to lack of airflow.
There's tests that should be run to rule everything out.
jesilvas is offline   Reply With Quote
Old 07-08-2013, 09:55 PM   #3
Senior Member
 
sc3283's Avatar
 
Join Date: Aug 2011
Posts: 1,126
sure sounds like lack of air flow through the ductwork beings it works with the "dump" open
__________________
96 Dynasty 36' that does NOT wander, thanks to RuppParts.com and their superior "poly" suspension bushings
sc3283 is offline   Reply With Quote
Old 07-08-2013, 09:59 PM   #4
Senior Member
 
Join Date: Apr 2009
Posts: 128
We had problems with our Jayco Pinnacle's bedroom A/C Freezing up all the time.
There is only one duct line on the front A/C and there was very little air flow.
The Rear A/C has two duct lines one both sides so it has much better air flow.
I added a couple of vents to the duct up front and added a short duct and vent on the other side, cooling and freezing problem fixed, works good now
__________________
Robert & Bale the Wonder Dog
2014 Redwood 38FL
2012 GMC 3500HD DRW
Rob_Fla is offline   Reply With Quote
Old 07-09-2013, 06:32 AM   #5
Member
 
Rcnewell11's Avatar
 
Join Date: Feb 2013
Posts: 56
Sounds like a lot of work to make work like tearing out ceiling to run duct lines and vents but might try if works.
Rcnewell11 is offline   Reply With Quote
Old 07-09-2013, 08:48 AM   #6
Senior Member
 
hjsdds's Avatar
 
Join Date: Apr 2013
Posts: 330
Air conditioning companies and and hot air heating systems companies publish manuals, tips and design guides for air flow movements, air volume, duct sizes forward and return, plenum sizes, etc., etc to make these work reliably and efficiently. Understanding these falls under two categories, either engineering or practical experience.
I'm surprised because Jayco is an old and pretty good company, but in this instance it seems they turned over the "design" to some kid on the line or someone they hired out of the rehab. "Hey, throw in some ducting between that front AC and that hole in the ceiling we cut".

hjs
hjsdds is offline   Reply With Quote
Old 07-09-2013, 07:46 PM   #7
Member
 
Rcnewell11's Avatar
 
Join Date: Feb 2013
Posts: 56
I ran front unit today only and ran great but when I run back unit at same time when it starts quit running normal unless I open draft door and dump air in bedroom then it runs great with both ac going 50amp service .the temperature today in Indiana was about 85 degrees and high humidity .i think air is pushing in trunk line at each other and not moving much and unit is freezing up and giving me problems with not enough air flow from front unit.
Rcnewell11 is offline   Reply With Quote
Old 07-09-2013, 09:10 PM   #8
Senior Member
 
Join Date: Apr 2009
Posts: 128
Quote:
Originally Posted by Rcnewell11 View Post
Sounds like a lot of work to make work like tearing out ceiling to run duct lines and vents but might try if works.
Was not much work to do the mods to ours, took about a hour.

Such a shame as I believe Jayco is better than this, our Pinnacle has been a great unit, guess the bean counters are getting their way and pinching penny's.
__________________
Robert & Bale the Wonder Dog
2014 Redwood 38FL
2012 GMC 3500HD DRW
Rob_Fla is offline   Reply With Quote
Old 07-10-2013, 06:20 AM   #9
Member
 
Rcnewell11's Avatar
 
Join Date: Feb 2013
Posts: 56
Rob_fla did u plug duct going to back of unit when u made modifications to your front unit ducts and vents or leave open to help cool back of unit .just wondering
Rcnewell11 is offline   Reply With Quote
Old 07-10-2013, 06:30 AM   #10
Senior Member
 
Jimooo's Avatar
 
Winnebago Owners Club
Join Date: Jun 2011
Location: Amite, La.
Posts: 289
Sounds like your unit is short cycling due to low refrigerant or blocked /plugged evaporator coil.

When was your coils cleaned ?

Are your fans working?

Hope this helps,

James
Jimooo is offline   Reply With Quote
Old 07-10-2013, 09:26 AM   #11
Senior Member
 
hjsdds's Avatar
 
Join Date: Apr 2013
Posts: 330
Quote:
Jimooo Sounds like your unit is short cycling due to low refrigerant or blocked /plugged evaporator coil.

When was your coils cleaned ?

Are your fans working?

Hope this helps,

James
Good advice, a lot of problems with air conditioners is solved with good coils cleaning and/or with filter replacement/cleaning. Although your problem sounds more and more like louse ducting "design (?)"

hjs
hjsdds is offline   Reply With Quote
Old 07-11-2013, 05:48 AM   #12
Member
 
Rcnewell11's Avatar
 
Join Date: Feb 2013
Posts: 56
New unit 2013 dometic low pro 13.5 clean coil and filter already checked
Rcnewell11 is offline   Reply With Quote
Old 07-12-2013, 05:31 AM   #13
Senior Member
 
Join Date: Apr 2009
Posts: 128
Quote:
Originally Posted by Rcnewell11 View Post
Rob_fla did u plug duct going to back of unit when u made modifications to your front unit ducts and vents or leave open to help cool back of unit .just wondering
We did not plug any ducts at all, was trying to get better air flow by adding registers.
Added one register on the front of the duct line where it ends towards the front closet and made a short duct on the TV side by carving out Styrofoam and lined with foil tape then added a register.
Much better air flow, works great.
I thing in the pictures of the newer Pinnacles, Jayco is now putting in two duct lines up front.
__________________
Robert & Bale the Wonder Dog
2014 Redwood 38FL
2012 GMC 3500HD DRW
Rob_Fla is offline   Reply With Quote
Old 07-12-2013, 05:49 AM   #14
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
Quote:
Originally Posted by Rcnewell11 View Post
New unit 2013 dometic low pro 13.5 clean coil and filter already checked
It sounds like your Dometic is "short cycling". Typically, this is caused by a bleed of cold air into the warm air side. Pull the trim piece from the bottom and look into both the warm air side and up thru the "dump" side. The aluminum tape should be intact all around the baffle (the divider) and the tape should totally seal the ducts where they come into the distribution box.

If you have the newer style baffle (a heavy dense foam piece) make sure the foam seals on the edges are intact and in full contact with the sides of the roof cutout. Also check that the baffle is within the groove on the template (the heavy metal plate on the bottom).

A short cycle is less likely to occur when the dump register is open because there is no back pressure to cause a bleed to the warm air side.

Did this occur before the unit was replaced?

Was the entire unit replaced or just the topside?

It is possible that the duct design is undersized and causing the short cycle .... but unlikely.
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 09:28 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.