Load humming from power distribution cabinet
Hi all, we have a 2014 Montana 5th wheel (38' front living) there is a humming sound that seems to be getting louder over the years, coming from the power distribution cabinet, any ideas what that is and how to correct? I removed the access panel in the basement and saw nothing loose! Humming only happens when plugged into shore power!
__________________
2014 F 350 SD 4 wheel drive
2014 38' Montana 5 th wheel
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
07-01-2019, 10:17 AM
|
#2
|
Senior Member
Join Date: Apr 2012
Location: In the boonies outside Sarnia, Ontario, Canada
Posts: 332
|
Likely the cooling fan is getting noisy bearings
Try pulling the cover off on interior side. Fan should be visible.
Sometimes you can remove fan pull sticker off the hub and add a few drops of oil.
RoadrunnerII
__________________
TV: 2016 F250 Lariat Screw 6.7 PSD
Trailer:2017 Jayco Eagle 321RSTS
|
|
|
07-01-2019, 10:29 AM
|
#3
|
Senior Member
Join Date: Oct 2017
Location: Estacada Oregon
Posts: 2,001
|
Quote:
Originally Posted by RoadrunnerII
Likely the cooling fan is getting noisy bearings
Try pulling the cover off on interior side. Fan should be visible.
Sometimes you can remove fan pull sticker off the hub and add a few drops of oil.
RoadrunnerII
|
Maybe I didn't explain properly, it's the cabinet that houses the switches for lights and tank monitoring system, no fan visible from basement all I see when panel removed is main power in and out!
__________________
2014 F 350 SD 4 wheel drive
2014 38' Montana 5 th wheel
|
|
|
07-01-2019, 10:34 AM
|
#4
|
Senior Member
Join Date: Apr 2012
Location: In the boonies outside Sarnia, Ontario, Canada
Posts: 332
|
Have you tried removing pedistal 120 Volt AC power and disconnecting battery and tightening all connections?
Could be a loose connection on anything from a breaker to a buse bar
RoadrunnerII
__________________
TV: 2016 F250 Lariat Screw 6.7 PSD
Trailer:2017 Jayco Eagle 321RSTS
|
|
|
07-01-2019, 11:24 AM
|
#5
|
Senior Member
Join Date: Nov 2015
Posts: 26,838
|
Quote:
Originally Posted by Mr Mustang
Hi all, we have a 2014 Montana 5th wheel (38' front living) there is a humming sound that seems to be getting louder over the years, coming from the power distribution cabinet, any ideas what that is and how to correct? I removed the access panel in the basement and saw nothing loose! Humming only happens when plugged into shore power!
|
Converter......
What brand/model is yours?
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
|
|
|
07-01-2019, 12:31 PM
|
#6
|
Senior Member
Join Date: Jan 2018
Posts: 117
|
It's likely coming from your converter. It's taking 120V AC and converting it to 12V DC. It requires a transformer to step the voltage down from 120 to 12, and a rectifier to switch from AC to DC.
Depending on how bad it is, it could be normal. Transformers make some hum in operation. It's just the layers of the laminated iron core vibrating together. They get noisier when they wear out.
__________________
John Morgan
1996 Western RV Alpenlite 31RL Augusta
1999 Ford F-350 XLT Crew 7.3 Powerstroke, ATS torque converter, Edge Products Juice Box
|
|
|
07-01-2019, 01:39 PM
|
#7
|
Senior Member
Join Date: Jul 2014
Posts: 35,441
|
If its the converter, it may be working harder, and getting louder, if your batteries are aging.
|
|
|
07-01-2019, 01:49 PM
|
#8
|
Senior Member
Join Date: Oct 2017
Location: Estacada Oregon
Posts: 2,001
|
Thanks everyone for your support! Will try things later! Will post with results ✌️
__________________
2014 F 350 SD 4 wheel drive
2014 38' Montana 5 th wheel
|
|
|
07-01-2019, 06:19 PM
|
#9
|
Senior Member
Join Date: Oct 2017
Location: Estacada Oregon
Posts: 2,001
|
All better!
__________________
2014 F 350 SD 4 wheel drive
2014 38' Montana 5 th wheel
|
|
|
07-01-2019, 07:37 PM
|
#10
|
Registered User
Join Date: May 2015
Posts: 683
|
Quote:
Originally Posted by Mr Mustang
|
Had a transfer switch start increasing in hum noise on a KZ toy hauler a few years back. Had it looked at and was told “it’s normal”. A few weeks later smelled smoke in the coach, tracked it down to...the transfer switch. Cooked one of the connections inside. Just mentioning for you to keep an eye on it.
|
|
|
07-01-2019, 09:17 PM
|
#11
|
Senior Member
Join Date: Jun 2016
Location: Nine Mile Falls WA / Arizona City AZ
Posts: 1,066
|
Power that runs through switches create a magnetic field... to the 60 cycle sine wave... the same way some light flicker... this field can make the breaker vibrate thus the sound...
The important issue... is that the panel shouldn't be warm or hot... a warm or hot panel means a bad connection, that heat is a resistance and later a fire.... if its warmer than the rest of the panel or hot.... FIX IT NOW
__________________
Retired Business Owner, Re-manufacturing HD Clutches, Brake Shoes, Air Compressors, Sales & Installation of PacBrake and other Industrial Friction
|
|
|
07-02-2019, 08:19 AM
|
#12
|
Senior Member
Join Date: Oct 2017
Location: Estacada Oregon
Posts: 2,001
|
Quote:
Originally Posted by redhooker
Had a transfer switch start increasing in hum noise on a KZ toy hauler a few years back. Had it looked at and was told “it’s normal”. A few weeks later smelled smoke in the coach, tracked it down to...the transfer switch. Cooked one of the connections inside. Just mentioning for you to keep an eye on it.
|
Thank you for the response, will keep an eye on it.
__________________
2014 F 350 SD 4 wheel drive
2014 38' Montana 5 th wheel
|
|
|
07-02-2019, 08:23 AM
|
#13
|
Senior Member
Join Date: Oct 2017
Location: Estacada Oregon
Posts: 2,001
|
Quote:
Originally Posted by jelag
Power that runs through switches create a magnetic field... to the 60 cycle sine wave... the same way some light flicker... this field can make the breaker vibrate thus the sound...
The important issue... is that the panel shouldn't be warm or hot... a warm or hot panel means a bad connection, that heat is a resistance and later a fire.... if its warmer than the rest of the panel or hot.... FIX IT NOW
|
Wow! What is this panel you speak of? Thanks for the response!
__________________
2014 F 350 SD 4 wheel drive
2014 38' Montana 5 th wheel
|
|
|
07-11-2019, 11:17 PM
|
#14
|
Senior Member
Join Date: Nov 2011
Location: Montgomery, Texas
Posts: 108
|
Sounds like the convertor, I had the same problem it got louder over a couple months and then went out completely.
|
|
|
|
|