Question Overheating/tripping electrical panel 110v AC breakers

2019 Keystone Montana High Country 331RL on 50 amp.

I have 2 ceiling HVAC units. Each pulls about 13amps. If I run one, the 20 amp breaker will get up to about 97 degrees. If I run both, eventually both breakers get up to over 105 and eventually trip due to heat, even with nothing else running that pulls many amps.

The units are on different phases of the panel. I verified that I'm not pulling more than 13 amps each. Voltage is 115-118 on both phases. I took the cover off, placed a small fan to blow on the panel, and moved the breakers further apart so they can dissipate heat better.

This is a new rv. I'm in North Carolina and it's only in the low 90s here. My site is in the sun. I plan to spend time in places much hotter. But I don't see how I can if the ACs can't keep up with the demand without overheating breakers.

How do other RVs run both HVAC units in 105-110 without tripping breakers?

Any advice? Thanks
__________________

fixpro256 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-05-2019, 04:59 AM   #2
Senior Member
 
jeepfreak's Avatar
 
Join Date: Mar 2003
Location: Home is where we park it
Posts: 460
The first thing I would do is shut off the power outside, pull the panel cover and tighten every screw on the circuit breakers. One of main causes of warm or melted wires is bad connections. Also check the plug that goes into the post. If it warm might have a bad 50 amp receptical.
__________________

__________________
2007 Allegro 34wa .WH w20 8.1 6speed. 2020 Jeep Gladiator Rubicon Toad.
jeepfreak is offline   Reply With Quote
Old 07-05-2019, 06:11 AM   #3
Senior Member
 
Join Date: Apr 2015
Posts: 1,440
Once you get it solved, dont expect too much from RV ACs when parked in the sun on a hot day. The ACs struggle to keep things cool in that scenario. Park in the shade on a hot day and it will be a major difference on how cool the RV will be.
__________________
2014 Raptor 300MP, 2014 Cowboy Cadillac - Ram 3500 Crew Cab Long Bed Longhorn 6.7 Cummins Turbo Diesel DRW 4.10 Rear End, 5588 Payload, Firestone Airbags, Curt Q20, TST507
raineman is offline   Reply With Quote
Old 07-05-2019, 10:48 AM   #4
Senior Member
 
Join Date: Mar 2018
Posts: 1,537
Heat is amperage lost. You have a problem. Potentially a BIG problem. Like Jeep said. Pull the panel and check all the connections.
__________________
Professional mechanic.
2018 Ram 2500 HD Mega cab.
mobilemike is offline   Reply With Quote
Old 07-05-2019, 12:33 PM   #5
Senior Member
 
Tha_Rooster's Avatar
 
Join Date: Aug 2008
Location: Georgia
Posts: 5,693
My son just purchased the 373rd and plugged into 50 amps has no problems. He also has run both on a 30 amp.
__________________
2007 Fleetwood Revolution LE 40V
Tha_Rooster is offline   Reply With Quote
Old 07-05-2019, 10:08 PM   #6
Senior Member
 
Rhagfo's Avatar
 
Join Date: Aug 2013
Posts: 494
Quote:
Originally Posted by fixpro256 View Post
2019 Keystone Montana High Country 331RL on 50 amp.

I have 2 ceiling HVAC units. Each pulls about 13amps. If I run one, the 20 amp breaker will get up to about 97 degrees. If I run both, eventually both breakers get up to over 105 and eventually trip due to heat, even with nothing else running that pulls many amps.

The units are on different phases of the panel. I verified that I'm not pulling more than 13 amps each. Voltage is 115-118 on both phases. I took the cover off, placed a small fan to blow on the panel, and moved the breakers further apart so they can dissipate heat better.

This is a new rv. I'm in North Carolina and it's only in the low 90s here. My site is in the sun. I plan to spend time in places much hotter. But I don't see how I can if the ACs can't keep up with the demand without overheating breakers.

How do other RVs run both HVAC units in 105-110 without tripping breakers?

Any advice? Thanks
Quote:
Originally Posted by jeepfreak View Post
The first thing I would do is shut off the power outside, pull the panel cover and tighten every screw on the circuit breakers. One of main causes of warm or melted wires is bad connections. Also check the plug that goes into the post. If it warm might have a bad 50 amp receptical.

See Items in red above!
You stated move further apart, well they should already be seperated by the 50 amp double main. If they are next to each other, they are on the same phase and could be part of your problem. I would also re-seat the breakers on the buss.
__________________
Russ & Paula, Portland, OR. The Beagle Belle.
2016 Ram Laramie 3500 DRW Aisin 4X4 14,000# GVWR.
2005 Keystone Copper Canyon 293FWSLS Rear Kitchen 12,360 GVWR
Rhagfo is offline   Reply With Quote
Old 07-06-2019, 02:19 AM   #7
YC1
Senior Member
 
YC1's Avatar


 
Holiday Rambler Owners Club
Join Date: Jun 2011
Posts: 7,067
Is the panel mounted in a closet or behind a door? Mine is mounted in a closet and a door that is very close to the face of it. The closet can get very hot and the breaker panel itself can get even hotter under those conditions. If parked with the panel more North it is not as bad or in the shade it is fine. I resorted to leaving the closet door open with a vent blowing on the face of the panel.

Opening the panel and using an infrared thermometer it was apparent they were getting extremely hot. So hot I believe that contributed to the total failure of the EMS load shedding control board with the relays on it.

A fan is not a viable solution for mine. What has worked is putting very slim washers at the corners of the panel. This tiny air gap seems to do the trick. In Sacramento Valley direct sun I still open the closet for good measure but have far less breaker tripping.

My AC's are the larger versions so draw around 16 amps which is close to the tripping point on a hot breaker it seems.
__________________
Myron & Deborah
08 HR Endeavor 40 SKQ
2012 Ford Edge Limited FWD 3.5L
Aluminator tow bar, Demco base plate
YC1 is offline   Reply With Quote
Old 07-06-2019, 01:18 PM   #8
Junior Member
 
Join Date: Jul 2019
Posts: 2
I'm a new member. Was going to go back and correct some mistakes I made in my original post, but can't figure it out. I guess this forum doesn't allow that.
fixpro256 is offline   Reply With Quote
Old 07-06-2019, 02:09 PM   #9
Senior Member
 
Rhagfo's Avatar
 
Join Date: Aug 2013
Posts: 494
Quote:
Originally Posted by fixpro256 View Post
I'm a new member. Was going to go back and correct some mistakes I made in my original post, but can't figure it out. I guess this forum doesn't allow that.

Best to just add a post to the thread, editing the original just causes confusion. Although you can edit any post you have made.
__________________
Russ & Paula, Portland, OR. The Beagle Belle.
2016 Ram Laramie 3500 DRW Aisin 4X4 14,000# GVWR.
2005 Keystone Copper Canyon 293FWSLS Rear Kitchen 12,360 GVWR
Rhagfo is offline   Reply With Quote
Old 07-06-2019, 02:17 PM   #10
Senior Member
 
spdracr39's Avatar


 
Monaco Owners Club
Join Date: Jul 2016
Location: Cabot, Arkansas
Posts: 2,165
Check the connections on the a/c units also. a bad connection anywhere in the circuit can cause an overheat/overload condition. I would also verify that the wire size they installed is suitable for the load. Just because it is new doesn't mean they did it correctly. You could just replace the breakers if all other inspections are good. It is possible there was a bad batch.

Just FYI posts are only editable for a limited amount of time then they are locked in.
__________________
2004 Beaver Monterey Laguna/2015 Chevy Equinox
2014 Chaparral 327RLKS 5'er (FOR SALE)
2017 GMC 2500HD SLE 6.0L Z71 4x4 Standard Bed
https://wordpress.com/posts/enjoying-life.net
spdracr39 is offline   Reply With Quote
Old 07-06-2019, 03:53 PM   #11
YC1
Senior Member
 
YC1's Avatar


 
Holiday Rambler Owners Club
Join Date: Jun 2011
Posts: 7,067
Quote:
Originally Posted by fixpro256 View Post
I'm a new member. Was going to go back and correct some mistakes I made in my original post, but can't figure it out. I guess this forum doesn't allow that.
You have a limited time to be able to edit your posts. If past that, you can Quote your own post with the corrections which will refresh the readers minds.
__________________

__________________
Myron & Deborah
08 HR Endeavor 40 SKQ
2012 Ford Edge Limited FWD 3.5L
Aluminator tow bar, Demco base plate
YC1 is offline   Reply With Quote
Reply

Tags
breaker, electric, electrical, heat, heating, overheating, panel



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
General Guardian RV 5500 Circuit Breakers Tripping - Driving and Not Running vettenuts Class A Motorhome Discussions 8 06-06-2018 02:28 PM
110v electrical panel circuit breakers Cariboutrail Thor Industries Owner's Forum 4 07-07-2014 10:25 AM
AC Breakers Tripping Curtisgeiger Entegra Owner's Forum 60 05-17-2014 02:49 PM
Electrical breakers tripping preventive checks powerboatr MH-General Discussions & Problems 3 06-27-2011 10:33 PM
Tripping Breakers stardalo Winnebago Industries Owner's Forum 14 12-11-2010 09:35 PM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 04:17 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
×