Old 05-31-2019, 06:59 PM   #1
Senior Member
 
Outdoors RV Owners Club
Join Date: Mar 2019
Posts: 125
Electrical limits

Hey everyone,

I have recently moved to a local farm with my TT. It is a 30amp trailer. The trailer is parked about 100ft from the house and electrical plug in.

Note: the electrical plug in is just to a standard 3 prong indoor outlet.

I am using 10g extension cord plus the 10g hook up to trailer, so I would figure about 115ft of cord.

I have the 15/30 adapter as well to cover the standard extension cord male end to the 30amp rv female.

When I plug in I am getting 115-118 volts at my outlet.

Question is will I have issues running my AC and fridge at the same time? Will I harm any of the units by using under 120volts?

Thank you!
TT_TR250RDS is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-31-2019, 07:19 PM   #2
Senior Member
 
Join Date: Jul 2014
Posts: 35,438
Get them both running and test the voltage. If its down below 110 volts, That's not good.
twinboat is offline   Reply With Quote
Old 05-31-2019, 07:27 PM   #3
Senior Member
 
ret60sp's Avatar
 
Fleetwood Owners Club
Join Date: Sep 2017
Location: Jefferson, GA
Posts: 147
Blog Entries: 4
Quote:
Originally Posted by TT_TR250RDS View Post
Hey everyone,

I have recently moved to a local farm with my TT. It is a 30amp trailer. The trailer is parked about 100ft from the house and electrical plug in.

Note: the electrical plug in is just to a standard 3 prong indoor outlet.

I am using 10g extension cord plus the 10g hook up to trailer, so I would figure about 115ft of cord.

I have the 15/30 adapter as well to cover the standard extension cord male end to the 30amp rv female.

When I plug in I am getting 115-118 volts at my outlet.

Question is will I have issues running my AC and fridge at the same time? Will I harm any of the units by using under 120volts?

Thank you!

You'll be fine as long as your voltage at the TT stays at or above 110VAC.


You need to pay close attention to the plug end connections of your extension cord. Start by spraying them with dielectric grease to prevent dissimilar metal corrosion as well as corrosion due to humidity and oxidation. Then pay attention to the heating created by a full load. Expect to trip a breaker as you exceed 15 amps of load at the TT, as the actual load at the power point (breaker) will include all of the line load and losses at the plug points.



Shade the extension cord as much as possible. Higher outdoor temperatures will cause the wire to be unable to dissipate heat. Too much heat will make the wire less efficient with carrying the load.


You would be better served to actually change the extension cord ends to true 30 amp connectors. The reason is the metal conductor is twice the size of a standard outlet, making heat dissipation much better.


If you plug into an outlet that trips often, try plugging into an outlet with no other loads on the same line, or an outlet that has a shorter homerun to the breaker panel. Remember, your residential grade outlet is possibly served with a #14 AWG wire, making for a potential fire hazard for the home or location you are plugged into. Try to find a source that is #10AWG if possible or at least #12AWG. Or if possible find a NEMA 15/50 amp plug and size down instead of up.
ret60sp is offline   Reply With Quote
Old 06-01-2019, 07:27 AM   #4
Senior Member
 
Join Date: Feb 2012
Posts: 175
You might be ok running 15 amps thru that 115’ of 10 gauge, I would not recommend it. Do yourself a big favor, make a 30 amp extension cord with 3, 6 gauge wires, blk, wht, and gr. Pay CLOSE attention to what color goes where. Then install a 30 amp outlet at the house on it’s own breaker.
Spoonsize is offline   Reply With Quote
Old 06-01-2019, 10:31 AM   #5
Senior Member
 
ret60sp's Avatar
 
Fleetwood Owners Club
Join Date: Sep 2017
Location: Jefferson, GA
Posts: 147
Blog Entries: 4
Quote:
Originally Posted by Spoonsize View Post
You might be ok running 15 amps thru that 115’ of 10 gauge, I would not recommend it. Do yourself a big favor, make a 30 amp extension cord with 3, 6 gauge wires, blk, wht, and gr. Pay CLOSE attention to what color goes where. Then install a 30 amp outlet at the house on it’s own breaker.

I agree with Spoon.
ret60sp is offline   Reply With Quote
Old 06-01-2019, 02:22 PM   #6
Senior Member
 
Outdoors RV Owners Club
Join Date: Mar 2019
Posts: 125
The only issue is, it’s not my house. I can ask the owner how he feels about all that, but I am also no electrician.

How would I make 30 amp extension cord with 6 gauge where black and green and sheath it?

Also, what if I can hook into a 220 wash and dryer line? Could I just get an adapter to knock it down in power?
TT_TR250RDS is offline   Reply With Quote
Old 06-01-2019, 02:41 PM   #7
Senior Member
 
Join Date: Mar 2019
Posts: 246
"NO" on the 50amp plug.


Since it is not your place and making changes is iffy and you show 115VAC for now you are OK just monitor the voltage if below 110VAC you will have to do something.
Also for the next few days feel the plugs at both ends if they are hot you may have to do something.
You will have to limit what you use at any one time. Best to have hot water on propane or manage when you turn it on and off. You do know you can not run microwave, AC or hairdryer at the same time.
__________________
Garry
garry1p is offline   Reply With Quote
Old 06-01-2019, 02:42 PM   #8
Senior Member
 
Outdoors RV Owners Club
Join Date: Mar 2019
Posts: 125
Quote:
Originally Posted by ret60sp View Post
You'll be fine as long as your voltage at the TT stays at or above 110VAC.


You need to pay close attention to the plug end connections of your extension cord. Start by spraying them with dielectric grease to prevent dissimilar metal corrosion as well as corrosion due to humidity and oxidation. Then pay attention to the heating created by a full load. Expect to trip a breaker as you exceed 15 amps of load at the TT, as the actual load at the power point (breaker) will include all of the line load and losses at the plug points.



Shade the extension cord as much as possible. Higher outdoor temperatures will cause the wire to be unable to dissipate heat. Too much heat will make the wire less efficient with carrying the load.


You would be better served to actually change the extension cord ends to true 30 amp connectors. The reason is the metal conductor is twice the size of a standard outlet, making heat dissipation much better.


If you plug into an outlet that trips often, try plugging into an outlet with no other loads on the same line, or an outlet that has a shorter homerun to the breaker panel. Remember, your residential grade outlet is possibly served with a #14 AWG wire, making for a potential fire hazard for the home or location you are plugged into. Try to find a source that is #10AWG if possible or at least #12AWG. Or if possible find a NEMA 15/50 amp plug and size down instead of up.

Great info! Thank you for taking the time to respond.

If I change the extension chord ends to 30amp. The one which connects to the house hold outlet still needs to be a regular 3 prong plug is so I guess in theory that area would still be a fire hazard, correct?

We found out late last night that the breaker that the outlet is plugged into is a 20amp breaker that runs the electrical fences and the basement.

I spoke briefly with the owner and there is a 30amp breaker on the panel that is not being used. The cable runs out to the barn, however something went wrong with the cable in the ground so it doesn’t work. He said I can reperpose that 30amp break. Get about 6ft if cable and run it outside with a 30amp plug. I still would required to use the 100+’ of 10g extension cord, but at that point can switch the ends to 30amp ends, correct? At that point it should be ok?

Or

If the owner wanted to run 220 aluminum wire to the barn. He said we can collaborate (expenses and joint time) on that and possibly set it up to the barn then with a 50amp connection outlet and I can just get the 50 amp to 30amp adaptor.

Any thoughts?
TT_TR250RDS is offline   Reply With Quote
Old 06-01-2019, 02:58 PM   #9
Senior Member
 
richard5933's Avatar
 
Join Date: May 2019
Posts: 2,392
The fire hazard is not just the plugs or cord ends, it's that the conductors themselves are not thick enough to carry the voltage over that length without building heat. Bigger conductor size equals less heat buildup equals less risk.
__________________
Richard
1994 Excella 25-ft (Gertie)
1999 Suburban LS 2500 w/7.4L V8
1974 GMC 4108a - Custom Coach Land Cruiser
richard5933 is offline   Reply With Quote
Old 06-01-2019, 03:18 PM   #10
Senior Member
 
Join Date: Nov 2009
Posts: 324
Quote:
Originally Posted by twinboat View Post
Get them both running and test the voltage. If its down below 110 volts, That's not good.
Good advise, voltage drop is the killer here, when a motor load starts (like an a/c compressor) it draws more current than after it's running. If the voltage drop is severe enough, it can damage the compressors and anything else thats voltage sensitive. You also have to take into account how far from the electrical panel the outlet on the house is. Since the OP said it was on a 20 amp breaker, one would assume it is #12 wire to that point, so that must be taken into account when doing voltage drop calculations.
hillbilly3 is offline   Reply With Quote
Old 06-02-2019, 12:04 AM   #11
Senior Member
 
Outdoors RV Owners Club
Join Date: Mar 2019
Posts: 125
So since the original hookup was to 20amp breaker an had other draws on it besides trailer. The simplest option at this point is to use the available 30amp breaker in the house panel, run 10 gauge wire from 30amp breaker, out to the back side of the house and into a standard outdoor 3 prong outlet. This will shorten the overall length of extension cord being used to 100’. (Numbers were wrong on original entensjkn cord measure. Length is 150’ of extension cord.)

Plus now it will be on its own 30amp breaker with no other draws besides trailer.

Does this seem like an ok option? I believe the owner will eventually still want to run 220 out to the barn right next to trailer. However Idn when, so in the mean time this seems to be best option.
TT_TR250RDS is offline   Reply With Quote
Old 06-02-2019, 12:42 AM   #12
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
The option of having your own 30a circuit from the house would be a good way to go. Inexpensive and easy to do on the house end. Then #8 or preferable #6 the RV location. Direct burial cable or THWN in conduit. Put a 3' piece of 4x4 PT in a hole with a bag of concrete and mount a RV30 receptical there.

If you do the 240v run to the barn it will be more involved. A subpanel will be needed there, with a 30a branch circuit for the RV.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 06-02-2019, 10:36 AM   #13
Senior Member
 
Outdoors RV Owners Club
Join Date: Mar 2019
Posts: 125
So leveraging the following should be no problem?
-30 amp panel breaker in house
-10/3 Romax from breaker out to a standard 3 prong outlet
-100’ of 10g heavy duty extension cord
-15/30 adaptor
-Hughes autoformer (30)
TT_TR250RDS is offline   Reply With Quote
Old 06-02-2019, 10:47 AM   #14
Senior Member
 
Join Date: Jul 2014
Posts: 35,438
If your running 30 amps you shouldn't be using a 20 amp outlet. You will have a tough time wrapping the wire around it.

Run a 120 volt, 30 amp twist lock outlet. Then go from there with 30 amp boat cables to your RV cord with 1 adaptor.
twinboat is offline   Reply With Quote
Reply

Tags
electric, electrical



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Limits on Winnebago Installed Receiver Hitch JD Allen Winnebago Industries Owner's Forum 9 05-24-2011 02:38 AM
2004 Dolphin Twing limits? G. SEEFIELD National RV Owner's Forum 6 01-13-2009 01:38 AM
Limits on Coach Square Footage? Why not published? JavaJelly MH-General Discussions & Problems 4 09-10-2007 08:12 AM
Dinghy Guide "Speed" limits Nonno Toads and Motorhome Related Towing 9 02-19-2007 06:00 AM
Government Price Limits on Fuel? Hitchhiker iRV2.com General Discussion 16 09-04-2005 01:23 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:35 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.