Old 05-22-2008, 01:09 PM   #1
Junior Member
 
Join Date: May 2008
Posts: 6
I have a seldom used 5th wheel (Carriage Carri Lite 28') That is on blocks with a hard skirting around it ( Had to do that to make it a "dwelling" for a permit, long story)

My electric service is 250' from the 5th wheel, I have a 50 amp box there.

Can I run 250' of 30 AMP cord and use an adapter to plug into the 50 AMP box?

Not planning on using too much electric at once i.e. nothing plugged into outlets while using the microwave, fridge on LP etc...

Any thoughts would be appreciated.
__________________

Slow Low is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-22-2008, 01:09 PM   #2
Junior Member
 
Join Date: May 2008
Posts: 6
I have a seldom used 5th wheel (Carriage Carri Lite 28') That is on blocks with a hard skirting around it ( Had to do that to make it a "dwelling" for a permit, long story)

My electric service is 250' from the 5th wheel, I have a 50 amp box there.

Can I run 250' of 30 AMP cord and use an adapter to plug into the 50 AMP box?

Not planning on using too much electric at once i.e. nothing plugged into outlets while using the microwave, fridge on LP etc...

Any thoughts would be appreciated.
__________________

Slow Low is offline   Reply With Quote
Old 05-22-2008, 03:24 PM   #3
Senior Member
 
GaryKD's Avatar
 
Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 12,784
Hi slow,
Welcome to iRV2. Is the 5'ver a 50 or 30 AMP coach? If it is a 30 AMP coach, your okay with a 30 AMP cord. Except for the last paragraph of this post. If it is a 50 AMP coach, I'd go for the extra cost and run a 50 AMP cord.

A 50 AMP line is really 100 AMPS (50 AMPS on each leg). 100 AMPS is a bunch more than 30. I know you said you'd be using the electric wisely; after time if someone gets careless you could have a problem.

Another thing to consider is that there will be a voltage drop during the 250' run. Go here to calculate the voltage drop. Once you see the drop for a 30 AMP cable you may want to consider the 50 AMP for additional safety. The 50 AMP cord will also provide additional longevity for the appliances in the coach. With the voltage drop combined with runing a few appliances at a time will stress the appliances.
__________________
Gary
2005 Newmar KSDP 3910 + GMC ENVOY XUV 37K lbs Moving Down The Road
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
GaryKD is offline   Reply With Quote
Old 05-22-2008, 04:19 PM   #4
Junior Member
 
Join Date: May 2008
Posts: 6
Wow, thanks Gary.

It's a 30 AMP system. The boxes the electrician put on my power pole are 50 amp is all.

This will be a temp fix until I can get a hard line in the ground this summer.

It's in Northern Arizona town called Show Low.

I call it Slow Low because well, it's slow.

Great site, found it today.

Thanks again!
Slow Low is offline   Reply With Quote
Old 05-24-2008, 08:07 AM   #5
Senior Member
 
Workhorse Chassis Owner
Join Date: Jun 2003
Location: Palisade CO
Posts: 3,584
For a 30 amp draw, to keep the voltage drop below the NEC recommended 5% the wire size used should be 04 gauge.
For a 20 amp draw 06 gauge would do.
__________________
Clay WA5NMR - Ex Snowbird - 1 year, Ex Full timer for 11 years - 2004 Winnebago Sightseer 35N Workhorse chassis. Honda Accord toad.
Clay L is offline   Reply With Quote
Old 05-24-2008, 12:20 PM   #6
Administrator in Memoriam
 
Route 66's Avatar


 
Newmar Owners Club
Retired Fire Service RVer's
Spartan Chassis
Join Date: May 2000
Location: Newark, DE
Posts: 25,909
I'm with Clay.

At a 250' distance, 30 amp cord, which is #10 wire, is too small for that distance.
__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, previously 4 years as a fulltimer in a '07 DSDP

Route 66 is offline   Reply With Quote
Old 05-24-2008, 05:39 PM   #7
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 14,840
This wire size calculator and thisvoltage drop calculator are handy to bookmark for future reference.

I think it is much cheaper to buy 3, 250' lengths of #4 copper wire, or #2 aluminum (required to carry 30A-250') than buy one bundled cable that length.
You are commended for asking before jumping in and destroying your RV components with undersized feed wire.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG retired;PPA,Good Sam Life member,FMCA."We the people are the rightful masters of both the Congress and the Courts - not to overthrow the Constitution but to overthrow men who pervert the Constitution. "Abraham Lincoln"
Ray,IN is offline   Reply With Quote
Old 05-25-2008, 09:59 AM   #8
Senior Member
 
Workhorse Chassis Owner
Join Date: Jun 2003
Location: Palisade CO
Posts: 3,584
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by Ray,IN:
This wire size calculator and thisvoltage drop calculator are handy to bookmark for future reference.

I think it is much cheaper to buy 3, 250' lengths of #4 copper wire, or #2 aluminum (required to carry 30A-250') than buy one bundled cable that length.
You are commended for asking before jumping in and destroying your RV components with undersized feed wire. </div></BLOCKQUOTE>

Ray you might want to take a look at THIS SITE for a down loadable program that finds the proper wire size for a given set of conditions.

I really like it - of course that may be because I wrote it.
__________________
Clay WA5NMR - Ex Snowbird - 1 year, Ex Full timer for 11 years - 2004 Winnebago Sightseer 35N Workhorse chassis. Honda Accord toad.
Clay L is offline   Reply With Quote
Old 05-27-2008, 09:10 AM   #9
Senior Member
 
alvinc's Avatar
 
Fleetwood Owners Club
Workhorse Chassis Owner
Join Date: Apr 2002
Location: Beaverton, OR, USA
Posts: 658
Note: it is possible to use 10 awg wire, but you need to limit the current to 9 amps (4.7% voltage drop).

There are two alternatives:

1) Use house type wire in conduit or direct burial to get the service connection closer to the RV.

2) Purchase Multi-conductor portable power cable and create your 250' extension cord.

Since you describe a semi-permanent location for the 5th wheel, I would invest the money to install a pedestal with the full 50 amp capability.

General Wire sells power cable like you would need, see their catalog and contact a local electric supply house for a price or something similar. Multi-conductor portable cord Note that 3 conductor, 4 awg wire is 920 lbs per 1000 ft.
__________________
Alvin/KB7VHI
2002 35R Southwind, W22 8.1L Vortec UltraPower, 19.5' wheels
Toad: Wrangler, lifted and on 35" tires
alvinc is offline   Reply With Quote
Old 05-27-2008, 12:02 PM   #10
Junior Member
 
Join Date: May 2008
Posts: 6
Hmmmmmmm.

The 30 AMP cords I bought worked just fine. They never got hot, ran a vacuum cleaner and the microwave ( not at the same time).

I will over do it with the big gauge wire when I run it proper in a few weeks.
Slow Low is offline   Reply With Quote
Old 05-29-2008, 10:32 AM   #11
Senior Member
 
alvinc's Avatar
 
Fleetwood Owners Club
Workhorse Chassis Owner
Join Date: Apr 2002
Location: Beaverton, OR, USA
Posts: 658
The 30 amp cord would not get hot, the effect would be reduced voltage and more stress on the appliances. Motors will heat up a bit when presented with low voltage. A vacuum cleaner should work just fine even on 100 volts, just a little slower.

I would worry more about the microwave, it will not like low voltages and will cook slower.

In my earlier mail I stated that a 10awg 250 ft cord can handle up to 9 amps with no more than 5% voltage drop. Since the nominal voltage is 115 VAC, this would translate to 109 VAC at the end of the cord.

If we allow 100 VAC at the cord end (13%), you could draw up to 25 amps. For 105 VAC (8.8%) you could draw 16 amps.

This means that the 10 awg could be used if you limit your current draw. Note, to make sure you meet this limit, you could install a different breaker in your house panel, use a 15 amp breaker rather than a 30 amp breaker.

Remember the breakers can do two things;
1) they are sized to limit the current to less than the ampacity of the wire. This is where the rule of thumb for 15 amps with 14 awg, 20 amps with 12 awg, and 30 amps with 10 awg.

2) breakers can also be used to limit voltage drop, even though they are current devices. What we do is calculate the acceptable voltage drop and choose a breaker rating that will limit the voltage drop. This is why a 15 amp breaker would help limit the current draw at the end of the 250 ft 30 awg cord.
__________________
Alvin/KB7VHI
2002 35R Southwind, W22 8.1L Vortec UltraPower, 19.5' wheels
Toad: Wrangler, lifted and on 35" tires
alvinc is offline   Reply With Quote
Old 05-30-2008, 11:41 AM   #12
Senior Member
 
alvinc's Avatar
 
Fleetwood Owners Club
Workhorse Chassis Owner
Join Date: Apr 2002
Location: Beaverton, OR, USA
Posts: 658
Let me clarify why the 30 amp cord (10 awg) would not get hot when using it for a 15 amp load.

The capacity of 10 awg wire is designated as 60 amps, even for a 1 foot length. This means that if you exceed 60 amps on a 10 awg wire, it is considered a fire hazard.

If you draw no more than 30 amps over 75 ft a 10 awg wire is a good choice. If you draw no more than 9 amps over 250 ft a 10 awg wire is a good choice.

Why 75 ft.....most RV cords are 25 ft, and you can buy a 50 ft extension cord. Just don't use more than one.
__________________

__________________
Alvin/KB7VHI
2002 35R Southwind, W22 8.1L Vortec UltraPower, 19.5' wheels
Toad: Wrangler, lifted and on 35" tires
alvinc is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wondering if I can use a 50 amp converter cord with my 30 amp service? luke_vardanian Travel Trailer Discussion 12 11-10-2008 04:34 AM
50 amp extension cord? LIKENIT 5th Wheel Discussion 7 04-19-2007 04:07 PM
50 amp electric cord bthomforde Winnebago Industries Owner's Forum 4 10-18-2005 02:07 PM
30 amp RV cord to Generator Calvin RV Systems & Appliances 6 09-09-2005 10:21 AM
Length of 50 amp cord The Shadow Winnebago Industries Owner's Forum 22 07-31-2005 03:55 PM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:30 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.