30 amp Surge Guard mounting questions

1) The instructions say it must be installed by a licensed electrician and then go on to provide deailed DYI instructions. Is this a case of them reducing the lawsuit potential, or should I pay an electrician?

2) The unit is marked 110 volts. My darling sweet nephews who were helping me install other new hardware said my A/C unit requires 220 volts and the SG cannot be installed where the shore power line enters the MH. Are they correct?
__________________
Barb (RVM18) with Morkies Lily & Bebe RIP Sena FMCA#F466348
"Homer" ‘11 Shasta Cynara, pulling "Ranger" '97 Ford Ranger toad
The Journey is Our Destination. Full-timer May 2011 - July 2021
[SIGPIC][/SIGPIC]
okmunky is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-11-2011, 05:19 AM   #2
Senior Member
 
az bound's Avatar
 
Workhorse Chassis Owner
Join Date: Dec 2007
Location: Surprise Arizona
Posts: 1,994
Assuming your coach uses 30 amp service, follow the diy instructions and you will be fine.
__________________
Harold & Linda
2009 CT coachworks siena 35V
W22 Workhorse 8.1L. Explorer Sport toad,
az bound is offline   Reply With Quote
Old 05-11-2011, 05:41 AM   #3
Senior Member
 
hardy1000's Avatar
 
Monaco Owners Club
Join Date: Feb 2009
Posts: 1,496
Quote:
Originally Posted by okmunky View Post
1) The instructions say it must be installed by a licensed electrician and then go on to provide deailed DYI instructions. Is this a case of them reducing the lawsuit potential, or should I pay an electrician?

2) The unit is marked 110 volts. My darling sweet nephews who were helping me install other new hardware said my A/C unit requires 220 volts and the SG cannot be installed where the shore power line enters the MH. Are they correct?
I installed mine, just follow the instructions and check your work and all should be good.
Attached Thumbnails
Click image for larger version

Name:	IMG_1589.JPG
Views:	145
Size:	157.2 KB
ID:	10174  
__________________
Del & Lori 2007 Diplomat 40PDQ - 2020 Grand Cherokee TrailHawk Hemi Toad, M&G Brake System, Blue Ox.
hardy1000 is offline   Reply With Quote
Old 05-11-2011, 06:08 AM   #4
Senior Member
 
Luv2go's Avatar
 
Newmar Owners Club
Nor'easters Club
Appalachian Campers
Ford Super Duty Owner
Coastal Campers
Join Date: Dec 2007
Posts: 2,463
Quote:
Originally Posted by okmunky View Post

2) The unit is marked 110 volts. My darling sweet nephews who were helping me install other new hardware said my A/C unit requires 220 volts and the SG cannot be installed where the shore power line enters the MH. Are they correct?
All US RV A/C units that I know of are 120VAC, not 220. All US RV 30A service is 120V. The hard-wired SG can and should be installed where the shore power enters the MH.
__________________
Stewart, Brenda and kids
2008 Newmar Canyon Star 3410, now at a new home
2006 Roadtrek Versatile 210
Luv2go is offline   Reply With Quote
Old 05-11-2011, 06:52 AM   #5
edj
Senior Member
 
edj's Avatar
 
Join Date: Jul 2010
Posts: 416
Quote:
Originally Posted by okmunky View Post
1) The instructions say it must be installed by a licensed electrician and then go on to provide deailed DYI instructions. Is this a case of them reducing the lawsuit potential, or should I pay an electrician?

2) The unit is marked 110 volts. My darling sweet nephews who were helping me install other new hardware said my A/C unit requires 220 volts and the SG cannot be installed where the shore power line enters the MH. Are they correct?
I have installed both the 30 amp and 50 amp versions in my trailers. Unless you know absolutely nothing about electrical systems/wiring, it is usually an easy install. The most difficult part I had was finding the location to put the Surge Protector and cutting the 50 amp cable (had to use a hacksaw). Be sure to measure the cable slack/routing at least 3 times before cutting the cable.... Mount the Surge Protector box and attach the cable conductors. The end that comes from the RV power plug goes into the Surge Protector input and the end from the CB box goes to the Surge Protector output.

The surge protector does not have to be installed right where the external power comes into the rig. It should be installed between the incoming power connection and the RV AC circuit breaker box at a convenient location. You want to find a location where you have some room to work and the box will be protected from stuff you store.

After you have it all hooked up, go to the CB box and switch OFF all the circuit breakers. Triple check the wire color codes going in and out the Surge Protector and then do the "smoke test". If all is OK, as it is most likely to be, switch back on the circuit breakers.
__________________
Ed J - Summer->Vestal, NY Winter->Melbourne, FL
1999 Dodge 2500 diesel, 6-spd manual
2007 HitchHiker Discover America 329RSB
edj is offline   Reply With Quote
Old 05-11-2011, 09:11 PM   #6
Member
 
ptysonjr's Avatar
 
Join Date: Apr 2011
Location: Melissa, TX.
Posts: 32
Do NOT connect 220 V service to your unit!!!!!

This is a simple installation and yes this is the manufacturer covering their tail end.
__________________
U.S. Air Force Veteran - 2015 Ford F350 DRW CC Air Bags - 2017 DRV Mobile Suites 41RSSB4 - B&W Companion Hitch

ptysonjr is offline   Reply With Quote
Old 05-11-2011, 09:14 PM   #7
Member
 
ptysonjr's Avatar
 
Join Date: Apr 2011
Location: Melissa, TX.
Posts: 32
Quote:
Originally Posted by ptysonjr
Do NOT connect 220 V service to your unit!!!!!

This is a simple installation and yes this is the manufacturer covering their tail end.
Sorry, I did not read thoroughly. A/C unit does not run on 220. Entire system us 120v
__________________
U.S. Air Force Veteran - 2015 Ford F350 DRW CC Air Bags - 2017 DRV Mobile Suites 41RSSB4 - B&W Companion Hitch

ptysonjr is offline   Reply With Quote
Old 05-11-2011, 09:35 PM   #8
Senior Member
 
AFChap's Avatar
 
Forest River Owners Club
Join Date: Aug 2002
Location: ...East Texas
Posts: 5,325
Wiring a 30a RV receptical for 220v is a very common mistake by experienced electricians because 30a 220v is "normal" in their world ...but a 30a RV is ALWAYS a 30a 120v connection, and the outlet (assuming you have the CORRECT one) is normally marked as such right on it. ...and my SurgeGuard is installed in the power compartment where the shore power line enters the system.
__________________
Paul (KE5LXU) ...was fulltimin', now parttimin'
2022 Coachmen Leprechaun 319MB
towing 2017 Jeep Grand Cherokee Limited
AFChap is offline   Reply With Quote
Old 05-15-2011, 12:44 AM   #9
Senior Member
 
okmunky's Avatar
 
Solo Rvers Club
iRV2 No Limits Club
Join Date: Feb 2011
Location: Yuma County, AZ
Posts: 10,869
Thanks Y'all!!! Your help is greatly appreciated. The knowledge base and experience level of this group is an invalueable resource.
__________________
Barb (RVM18) with Morkies Lily & Bebe RIP Sena FMCA#F466348
"Homer" ‘11 Shasta Cynara, pulling "Ranger" '97 Ford Ranger toad
The Journey is Our Destination. Full-timer May 2011 - July 2021
[SIGPIC][/SIGPIC]
okmunky is offline   Reply With Quote
Old 05-21-2011, 01:03 PM   #10
Senior Member
 
gpearston's Avatar
 
Join Date: Jan 2011
Location: Pidemont, SD
Posts: 101
As many have already said - 30a is 120v. The SG is easy to install and well worth the effort.

Good luck and enjoy
__________________
Glenn
KD0NSG
Live your life and forget your age
gpearston is offline   Reply With Quote
Old 07-17-2011, 12:20 AM   #11
Senior Member
 
clarkgriswold's Avatar
 
Holiday Rambler Owners Club
Join Date: Jul 2009
Location: Dublin, VA
Posts: 391
Just as a note, the 3 wire, 220v prong configuration is purposely different than the 3 wire, 120v, 30a RV plug. ...and that's the reason, so electricians not familar with RVs take note and don't make the mistake. Fact is, the actual 30a connection is electrically the same as a 'standard' residential plug - except for the breaker and conductor size. There both still hot-neutral-ground.
__________________
Mike & Cindy, (of course with Lucy the Miniature Schnauzer & Eddie the Yorkie) Dublin, VA / Fun Finder TT / X215WSK
clarkgriswold is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30 Amp Surge Guard Installed; It buzzes? FDchief Winnebago Industries Owner's Forum 5 08-06-2009 04:22 PM
finished my surge guard re-install powerboatr Damon 0 04-30-2009 05:00 PM
50 amp surge protector issue CWIL 5th Wheel Discussion 3 08-26-2008 03:18 PM
Will a 50 amp surge protector work with a 30 amp system CWIL 5th Wheel Discussion 5 08-21-2008 02:34 PM
Autoformer vs Surge Guard or both? MA4529 RV Systems & Appliances 11 10-14-2007 03:12 AM