Did anyone happen to notice the topic in the tech section of this month's Trailer Life dealing with the individual who has rigged a pigtail to plug his RV into one phase of a dryer outlet at his house? The magazine guru gave this arrangement his blessing.
I don't recall the dryer plug having a separate terminal for ground - it uses a grounded neutral if I recall correctly. I wonder what the individual is doing with his RV ground lead? Without knowing, this sounds like a pretty good way to light up one's eyeballs!
Rusty
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
06-17-2005, 10:49 AM
|
#2
|
Senior Member
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
|
Did anyone happen to notice the topic in the tech section of this month's Trailer Life dealing with the individual who has rigged a pigtail to plug his RV into one phase of a dryer outlet at his house? The magazine guru gave this arrangement his blessing.
I don't recall the dryer plug having a separate terminal for ground - it uses a grounded neutral if I recall correctly. I wonder what the individual is doing with his RV ground lead? Without knowing, this sounds like a pretty good way to light up one's eyeballs!
Rusty
|
|
|
06-17-2005, 11:03 AM
|
#3
|
Senior Member
Join Date: Jul 2001
Location: Tucson AZ
Posts: 393
|
I think there are two kinds of dryer outlets. One has 3 prongs (H, H, G) and the other has 4 prongs (H, H, C, G). Assuming that you have a 4 prong outlet, and connect between one of the hot legs and common, there should be no problem. I did this exact thing at the townhouse I lived in since I had a gas dryer.
|
|
|
06-17-2005, 11:10 AM
|
#4
|
Senior Member
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
|
Now that I think about it, you're probably right. We recently bought a new washer & dryer at Lowe's and they asked us if the dryer had a 3 or 4 prong outlet. Since our house is more than 5 years old, it had a 3 prong - that's what I was thinking of. The difference, of course, is that an RV uses an isolated ground where our 3-prong dryer outlet doesn't.
I guess all you folks with new houses don't have a problem. I'm not sure I would want to try this with the 3-prong outlet with the grounded neutral, though!!
Rusty
|
|
|
06-18-2005, 10:42 PM
|
#5
|
Moderator Emeritus
Country Coach Owners Club Appalachian Campers Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,060
|
I will again recommend that all owners invest in a Surge Guard for the service of their rigs. I cannot remember the numbers of rigs that have lost almos all electronics from plugging into a dryer outlet. If it is a four prong receptacle and the adapter and receptacle are wired properly, there should not be a problem but if not; with out an overvoltage protection device you will fry the rigs electrical systems.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
|
|
|
06-20-2005, 10:37 AM
|
#6
|
Member
Join Date: Jul 2000
Location: Oxnard, CA, USA
Posts: 48
|
The difference between the three prong and four prong 240V plug is the additional "common" wire (as described above). The reason why the common wire is added is to allow for 120 volt operation for the device as well.
Some dryers (or other 240 volt appliances) have controllers or other such stuff that require 120 volts, whereas the main heater/whatever requires 240. Actually the 240 is done by having two 120 hot lines exactly out of phase with each other, so the cummulative effect is 240 volts.
The bottom line is yes, if you do have a four prong 240 plug (with the common wire), then one hot lead and the common wire will supply 120 volts. Be sure to use the common wire, not the ground!
If you have any questions on this at all, then I recomend getting a qualified electrician to assist you.
Dave
|
|
|
06-29-2005, 07:47 PM
|
#7
|
Junior Member
Join Date: Jun 2005
Location: Fair Oaks, CA
Posts: 13
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by RV Wizard:
I will again recommend that all owners invest in a Surge Guard for the service of their rigs. I cannot remember the numbers of rigs that have lost almos all electronics from plugging into a dryer outlet. If it is a four prong receptacle and the adapter and receptacle are wired properly, there should not be a problem but if not; with out an overvoltage protection device you will fry the rigs electrical systems. </div></BLOCKQUOTE>
Mike--
I agree wholeheartedly! Probably one of the best investments you can make in the long term health of your RV. I just installed a 50A hard-wired Surge Guard in my 5th wheel this past weekend. The hardest part of the whole operation was figuring out where to hang it! The installation itself was a snap.
Ken
__________________
Ken & Cricket
2019 Arctic Fox Silver Edition 28-5C
2006 Dodge Ram 3500 Dually, 5.9L Cummins Diesel
|
|
|
06-30-2005, 05:48 AM
|
#8
|
Senior Member
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by aa6vh:
The difference between the three prong and four prong 240V plug is the additional "common" wire (as described above). The reason why the common wire is added is to allow for 120 volt operation for the device as well. </div></BLOCKQUOTE>Dave,
With all respect, what was added in the 4-prong plug was an isolated ground. The 3-prong plug has L1, L2 and N with neutral (N) normally being grounded at the breaker box. In the 3-prong plug, L1-L2 will provide 240VAC, and either L1-N or L2-N will provide 120VAC. As you state, L1 and L2 are 180* out of phase.
Rusty
|
|
|
06-30-2005, 10:50 AM
|
#9
|
Member
Join Date: Jul 2000
Location: Oxnard, CA, USA
Posts: 48
|
Rusty,
We both could be right, so to speak. I have seen 240 volt circuits (my house A/C for example) where there is no neutral wire, just two hots and a ground. I suspect there are other, espcially older circuits that do not have the ground, and the third wire is neutral.
According to current electrical codes, you must have a separate ground wire (at least in my area).
With respect,
Dave
|
|
|
06-30-2005, 11:05 AM
|
#10
|
Senior Member
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by aa6vh:
According to current electrical codes, you must have a separate ground wire (at least in my area).
With respect,
Dave </div></BLOCKQUOTE>Yep, that's why newer homes (built within, say, the last 5 years) here in the Houston area went to the 4 prong plug - it added the isolated ground wire instead of relying on a grounded neutral that could be grounded at the breaker box 100' or more from the appliance.
Rusty
|
|
|
07-11-2005, 06:43 AM
|
#11
|
Member
Texas Boomers Club
Join Date: Jun 2002
Location: Waco Texas
Posts: 46
|
So what do we have when when plugging in a 30amp adapter on the end of our 50amp RV cord. It doesnt have the 4th wire so is it H,H,G?
Or is it H,C,G. I suspect it would be the first configuration or some of the RVs electrical would be non functioning due to load splitting in the main RV panel. If this is correct how does it function without the 4th common wire.
Good topic as I am making a extra 50amp cord from a unused welding extension cord that is only 3 wire.
John
__________________
97 Dodge 2500 CC,5spd, Cummins, minor eng mods. AKA Deezul 1
2006 Montana 3400RL Quad Slide full timing July 06 <a href="https://www.wunderground.com/US/TX/Waco.html">
|
|
|
07-11-2005, 06:52 AM
|
#12
|
Senior Member
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
|
John,
The 30 amp "dogbone" is L1, N, G. It internally jumpers the 2 hot legs of the RV's 50 amp service together so that they are both powered, but are no longer 180* out of phase. Using the 30 amp adapter, a 50 amp RV only has 30% of the theoretical ampacity that is has on 50 amp service where it has 50 amps x 2 legs = 100 amps.
One thing to consider when using these dogbones is that the 2 each 50A main breakers in the RV distribution box are no longer protecting the RV (actually, the dogbone adapter) in the sense that they're overrated for the available power supply - you're relying on the 30A breaker on the shore power pole for overcurrent protection.
Rusty
|
|
|
07-11-2005, 11:29 AM
|
#13
|
Member
Texas Boomers Club
Join Date: Jun 2002
Location: Waco Texas
Posts: 46
|
Good to know how the 30amp adapter works, hated to cut one apart to find out.
For many years I have done many different types of wiring jobs and almost all main panels (residential and commercial) combine the neutral wire and the ground wire on the same buss bar. Many old houses didnt have a ground circuit at all. I was told by an electrician working for the power company that the neutral is the ground supplied by the power company and the panel ground is supplied by the individual installation.
I hope I havnt hijacked this thread with these questions but there is a need for this knowledge here I believe.
Thanks
John
__________________
97 Dodge 2500 CC,5spd, Cummins, minor eng mods. AKA Deezul 1
2006 Montana 3400RL Quad Slide full timing July 06 <a href="https://www.wunderground.com/US/TX/Waco.html">
|
|
|
07-11-2005, 12:07 PM
|
#14
|
Senior Member
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
|
For those that may be wondering, one reason that it's so essential that the RV have a separate, isolated ground (typically, a ground rod at the shore power box) is that it's sitting on rubber tires. Now, if I have my jack pads on plastic Lynx levelers, this local, isolated ground is grounding the RV chassis through the power cord, thus preventing any stray current from knocking one flat if they were to, say, step onto the metal steps barefoot with one foot still on the ground!
Rusty
|
|
|
|
|