09-15-2014, 09:59 AM
|
#29
|
Junior Member
Join Date: Sep 2014
Posts: 19
|
The function of the main breaker is to protect the wire feeding the panel and the rating of the panel. A 200amp main would most likely have a minimum size 2/0 cu which 2/0 cu is suitable for 200 amps. The panel would then contain multiple breakers 15,20,30 amp and so on. Some single pole and some double pole. The reason you don't exceed the rating of the wire on eithere the service entrance conductors or the lower amp branch circuits by simply installing a larger breaker is to avoid thermal breakdown of the insulation on the wire. For example: pulling anything above 50 amps thru a wire rated at 50 amps, will cause melting of the insulation on the wire resulting in short circuit and or fire. Speed at which the the insulation melts down is relative to the level of current above the rating of the wire and, heat generated. Also, the combined load, not the numbers of breakers on a 200 amp main, exceed the 200 amp main, the main should trip. Notice I said should trip. They are man made electro mechanical devices subject to a failure of correct operation. Doesn't happen often on the overload, more likely to start having a premature trip. Hope that helps.
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
09-15-2014, 10:52 AM
|
#30
|
Junior Member
Join Date: Sep 2014
Posts: 19
|
I didn't answer part of your question. It is not ok, by use of a cheater as you indicated, to connect a 30 amp rv to a 50 amp receptical. What you have is a 30 amp circuit protected by a 50 amp breaker. Again, thermal breakdown of the insulation causing a short or fire. I know fully it's done all the time across the USA. Doesn't make it right or more importantly safe for you and your family. If the 50 amp receptical is protected with a 30 amp breaker, I would then say it's ok, not ideal but the most likely failure point would be the cheater not melting down the insulation.
|
|
|
09-15-2014, 11:38 AM
|
#31
|
Senior Member
Join Date: Sep 2012
Posts: 8,055
|
Quote:
Originally Posted by NormDunn
The function of the main breaker is to protect the wire feeding the panel and the rating of the panel. A 200amp main would most likely have a minimum size 2/0 cu which 2/0 cu is suitable for 200 amps. The panel would then contain multiple breakers 15,20,30 amp and so on. Some single pole and some double pole. The reason you don't exceed the rating of the wire on eithere the service entrance conductors or the lower amp branch circuits by simply installing a larger breaker is to avoid thermal breakdown of the insulation on the wire. For example: pulling anything above 50 amps thru a wire rated at 50 amps, will cause melting of the insulation on the wire resulting in short circuit and or fire. Speed at which the the insulation melts down is relative to the level of current above the rating of the wire and, heat generated. Also, the combined load, not the numbers of breakers on a 200 amp main, exceed the 200 amp main, the main should trip. Notice I said should trip. They are man made electro mechanical devices subject to a failure of correct operation. Doesn't happen often on the overload, more likely to start having a premature trip. Hope that helps.
|
Make that "may" instead of "will" cause a fire and you have the point. It will cause a slightly higher than desired temperature rise in the overloaded conductor. As a fraction of overload it is less of an overload than replacing a 15 A breaker with a 20 A breaker in a 15 A circuit. That is a fairly common practice. Anyone worried might find this discussion interesting:
14 AWG allowable ampacity - Electrician Talk - Professional Electrical Contractors Forum
Given that the current ratings are purposely conservative for wire in a bundle in a conduit sitting in the Texas sun on a hot day the only place I get worried is where the wire is running through an enclosed pipe. I will give you that a 3 or 4 wire insulated cable will get warm laying in the sun but it is well below the rated maximum temperature for the cable.
It also assumes the power cord will dissipate an extra 10 A somewhere between the receptacle and the 50A breaker at the input of the Motor Home. If you have 10 A of leakage current you already have a bad power cord and probably a fire despite the breaker size.
All that assumes the MH will draw 50A on either leg under normal usage.
Altogether too many assumptions for me to get worried about putting a 50A receptacle on a 60 A protected circuit.
|
|
|
09-15-2014, 01:49 PM
|
#32
|
Junior Member
Join Date: Sep 2014
Posts: 19
|
Thanks, I looked at and liked the link. Upon reading it I quickly noticed they were talking about a/c circuits and motor load circuits and not a multipurpose circuit. Personally, I don't believe and it has not been my experience that any electrical inspector has, would, will allow a 20A breaker on a comercial, residential or rv circuit that is not specifically dealing with a dedicated ac or motor circuit. Again, that's just been my experience.
I like to think of any code book as the absolute worst job you can do and still get a green tag.
|
|
|
09-15-2014, 09:17 PM
|
#33
|
Senior Member
Join Date: Nov 2005
Posts: 4,063
|
Doesn't really matter what we are personally worried about it is what code enforcement requires balanced against what your insurance companies inspector will allow to be covered when an incident has occurred with local conditions taken into account that may require a step up in specs. Too late then to say well Dan/Bob/Bill/Sue at IRV2 said electricians in other jurisdictions feel that the code is too strict and that I could get away with it.....
You do it to exceed code. As was mentioned Code is many times not best practice but just good enough to get by and still get paid for the job.
Where I live we have long running low voltage events that will increase amperage and heat well above design specs. A good local electrician and local electrical engineer will keep that in mind and exceed code due to local conditions and not take liberties in their designs. A good local electrical inspector may also on inspection take exception to special circumstances that he notes and require components be upgraded.
__________________
Neil V
2001 Winnebago Adventurer WFG35U
|
|
|
09-15-2014, 09:22 PM
|
#34
|
Senior Member
Forest River Owners Club Ford Super Duty Owner
Join Date: Aug 2010
Location: S florida now Cocoa
Posts: 286
|
most all rv have a inside main breaker 50a can only draw that much ,so all that is fused at 60 is the cord
__________________
Rick & Barbara
"98" 30 'Coachmen C Santara FL (front lounge) V 10
TST tpms, ScanGauge 2 cats Tyler,Lucy
|
|
|
09-15-2014, 10:18 PM
|
#35
|
Senior Member
Holiday Rambler Owners Club
Join Date: May 2013
Location: North Myrtle Beach, SC
Posts: 365
|
Quote:
Originally Posted by Santara
most all rv have a inside main breaker 50a can only draw that much ,so all that is fused at 60 is the cord
|
I had a electrician look at what I wanted to do and he said the same thing. The coach won't draw any more than a max of 50A. The cord and wiring between the coach and the breaker will be protected for 60A.
I m going to be doing this in a few days and will post a few pics for y'alls amusement!
__________________
Brad and Pat, the Dad and Mom-Dawgs with Kiddo and Dinah-Mite, the Dawter-Dawgs full timin' in our 2002 HR Neptune DP with 2017 Grand Caravan toad
|
|
|
09-15-2014, 11:28 PM
|
#36
|
Senior Member
Join Date: Feb 2010
Posts: 4,654
|
NEC is just that...national code.
The breaker is rated for wire and all parts of the circuit up to and including the outlet.
Breaker is not designed to protect the wiring past that point thus smaller loads like wall wart used in a 15 amp ckt.
A 30 amp cord will trip a 50 amp breaker...
If there was a fire and the inspector found the 60 amp breaker on conductors or outlet rated for less than breaker then sn insurance adjuster can deny claim.
I believe op stated they were going to use correct size so it should be done to NEC or local code.
__________________
Tony & Lori
1989 Country Coach Savannah SE
|
|
|
09-16-2014, 12:28 PM
|
#37
|
Senior Member
Forest River Owners Club Ford Super Duty Owner
Join Date: Aug 2010
Location: S florida now Cocoa
Posts: 286
|
Quote:
Originally Posted by draboo
I had a electrician look at what I wanted to do and he said the same thing. The coach won't draw any more than a max of 50A. The cord and wiring between the coach and the breaker will be protected for 60A.
I m going to be doing this in a few days and will post a few pics for y'alls amusement!
|
that was my racket also
__________________
Rick & Barbara
"98" 30 'Coachmen C Santara FL (front lounge) V 10
TST tpms, ScanGauge 2 cats Tyler,Lucy
|
|
|
09-18-2014, 09:30 PM
|
#38
|
Senior Member
Join Date: Aug 2013
Posts: 893
|
Make sure your power inverter can handle the extra power. Otherwise I would recommend upgrading to a higher power, power inverter.
|
|
|
09-19-2014, 06:49 AM
|
#39
|
Senior Member
Join Date: Sep 2012
Posts: 8,055
|
Quote:
Originally Posted by cimplexsound
Make sure your power inverter can handle the extra power. Otherwise I would recommend upgrading to a higher power, power inverter.
|
What does your power inverter have to do with the coach service wiring?
|
|
|
09-19-2014, 07:14 AM
|
#40
|
Senior Member
Monaco Owners Club Texas Boomers Club
Join Date: Jan 2009
Posts: 2,529
|
Quote:
Originally Posted by hdossett
That said, match the breaker to the wire, i.e. #8 wire (3/wG), no more than 40 amp DP breaker.
|
Not all the time! A #8 THWN or THHN wire is rated at 55 amps...
__________________
Hal & Ginny Miller '04 Beaver Santiam PRT40
'04 Saturn Vue - US Gear Brake - Blue Ox tow
3"girls" (2 Irish Setters - 1 Retriever) - RIP Annie & Emily (12/26/2017)
|
|
|
09-19-2014, 08:26 AM
|
#41
|
Senior Member
Join Date: Aug 2013
Posts: 893
|
50 amp receptacle breaker: 60 amp OK?
All your electrical house wiring is serviced by your power inverter. You could say your power inverter is the central nervous system or brain of your RV's electrical system. If you cause it an overload, your in trouble. Meaning lights out? Just saying it's better to be safe than sorry.
|
|
|
09-19-2014, 08:39 AM
|
#42
|
Senior Member
Join Date: Apr 2014
Location: No. Central Texas
Posts: 580
|
Thanks, OLYLEN, I think you answered a question I was about to ask. We are about to add electrical to a new barn for our 30amp service RV. I want to go ahead and wire for 50amp service now, so when the DW decides we need to upgrade we'll probably need it - and we'll have it without having to upgrade the electrical service as well (which will probably cost more than the original install). Of course we'll get a 30amp-to-50amp adapter for our current RV for now.
__________________
Butch and Peggy
2000 Itasca Suncruiser 32V;Workhorse P-32;7.4L Vortec;Complete Banks Pwr Sys/Air Flow;UltraPower ECM;Steer Safe;Springs/Airbags front;Timbren rear Susp.kit;30amp;Onan 5K Emerald
|
|
|
|
|