50 amp receptacle breaker: 60 amp OK?

I m going to wire a 50 amp receptacle for our motorhome. I have a 60 amp 2 pole breaker for a welder I was thinking of using instead of purchasing a 50 amp, since it is already there.

Will this 60 amp breaker cause any problems? Will the breakers in the MH trip if too many amps are used?

I have a 2002 HR Neptune DP.

Thanks,eh?

Brad
__________________

__________________
Brad and Pat, the Dad and Mom-Dawgs with Kiddo and Dinah-Mite, the Dawter-Dawgs full timin' in our 2002 HR Neptune DP with 2015 Indian Scout Toad
draboo is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-09-2014, 11:20 AM   #2
Senior Member
 
dennis45's Avatar


 
Join Date: Jun 2012
Location: BC
Posts: 7,115
Caution, I am not qualified to explain the difference but I believe a 50A Welder Receptacle is not the same as your RV requirement.
I'm sure one of our Electrical Gurus will chime in shortly.
__________________

__________________
Dennis & Carol
Said so long to our DS for a 2019 Unity LTV CB, pushed by a 2013 Honda CRV, BlueOx Baseplate, Aventa Bar & Patriot Brake
dennis45 is offline   Reply With Quote
Old 09-09-2014, 11:23 AM   #3
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Winnebago Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 32,818
Quote:
Originally Posted by dennis45 View Post
Caution, I am not qualified to explain the difference but I believe a 50A Welder Receptacle is not the same as your RV requirement.
I'm sure one of our Electrical Gurus will chime in shortly.
OP is asking about the breaker, not the receptacle.

OP: I would get the right breaker.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '14 CR-V
Mr_D is offline   Reply With Quote
Old 09-09-2014, 11:28 AM   #4
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
The 60 amp 2 pole breaker is over rated for your 50 amp coach. If you were to have some type of problem, the 60 amp breaker will not trip as soon as a 50 amp breaker would.

Purchase the correct 50 amp 2 pole breaker and you will not only be safe but done with the project instead of having to go back and re-do it later.

Dr4Film ----- Richard
Dr4Film is offline   Reply With Quote
Old 09-09-2014, 12:30 PM   #5
Senior Member
 
wb7auk's Avatar
 
National RV Owners Club
Join Date: Feb 2012
Location: Spokane Valley, Wa
Posts: 1,987
It depends on the transfer panel rating that is used in your motor home and the rating
of the receptacle and wire size being used for the service.
__________________
Art
1999 Trade Winds 7371 Cat 3126B w/current upgrades
1990 D 250 Dodge Ram Cummins Turbo
wb7auk is offline   Reply With Quote
Old 09-09-2014, 12:46 PM   #6
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,022
Well, if you were located in the city known as Lost Wages I would suggest you consult with a odds-maker to discuss the odds of using a 60 amp breaker pair causing a problem,, I suspect, those odds are actually mostly in your favor.

However anywhere else .. The cost of a 50 amp pair is low enough to make the phrase "Cheap insurance" come to mind.

And thus, I shall recommend that course of action.
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 09-09-2014, 08:56 PM   #7
Senior Member
 
Join Date: Nov 2005
Posts: 3,218
Since the 50 amp plug/receptacle can overheat and fail with a long term overdraw especially during a brownout even on a 50 amp breaker is it worth the saving the $30 to $50 on the right sized breaker for the outlet to risk a motor home that still has a retail value of around $35,000? Its one thing to loose a toaster or vacuum cleaner due to the breaker not tripping however you are risking an overheat and fire on everything between the 50 amp receptacle and the 50 amp main breaker in the coach. Yes in the old days people did get away with putting a penny in a fuse socket and screwing a burned fuse down on it or replaced a 20 amp fuse with a 30 to get away with not having to purchase the correct size fuse however a good number also burned their homes down.

How lucky do you feel? When you roll the dice like that there is always the chance of crapping out.

Me I'd purchase the right sized breaker even if money was tight as we are only talking about the same value as a few pizzas or brown bagging lunch for a few days.
__________________
Neil V
2001 Winnebago Adventurer WFG35U
NeilV is offline   Reply With Quote
Old 09-09-2014, 09:17 PM   #8
Senior Member
 
Pds47's Avatar
 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Oct 2012
Location: Tucson AZ
Posts: 261
Blog Entries: 1
lowes has 50 amp breakers about 11 bucks
__________________
Paul & Megan 2007 Neptune XL 36 PDQ REK Bilsteins, KarKaddy,mini cooper, W/ Bear and Sedona
Pds47 is offline   Reply With Quote
Old 09-09-2014, 09:22 PM   #9
Senior Member
 
Join Date: Feb 2010
Posts: 4,534
The breaker is sized to the smallest capacity of the circuit without exception...PERIOD!

If the outlet is specified as 60 amp @ 240 VAC and you only had #10 wire then you would use a 30 amp breaker due to tge wire limiting the ampacity.

The outlet is rated 50 amp so that limits breaker to 50 as long as correct wire is used.

Larger breaker would mean big trouble if you had a fire.

Plus if you have a welder outlet it is likely only 3 wire....L1. L2 and safety ground and you would need a neutral to be good.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 09-09-2014, 10:14 PM   #10
Senior Member
 
draboo's Avatar
 
Holiday Rambler Owners Club
Join Date: May 2013
Location: North Myrtle Beach, SC
Posts: 284
Affording the breakers isn't an issue. If I could safely use the 60A breaker, I would. Since I cannot, I will purchase the proper one.

Thanks for everyones input! I m off to Lowes on the morrow.

Brad
__________________
Brad and Pat, the Dad and Mom-Dawgs with Kiddo and Dinah-Mite, the Dawter-Dawgs full timin' in our 2002 HR Neptune DP with 2015 Indian Scout Toad
draboo is offline   Reply With Quote
Old 09-10-2014, 03:31 AM   #11
Senior Member
 
Join Date: Nov 2005
Posts: 3,218
Quote:
Originally Posted by Pds47 View Post
lowes has 50 amp breakers about 11 bucks
Home Depot has some for $8.25 however those only fit a Synder Square D panel. Range is from $8.25 to $177 depending on the panel you have and if per local code you need GFI protection on an outlet used for a device that is located outdoors.
__________________
Neil V
2001 Winnebago Adventurer WFG35U
NeilV is offline   Reply With Quote
Old 09-10-2014, 08:32 AM   #12
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 3,391
Were you planning on using the existing receptacle and wiring? If it is wired to provide 240 volts with a neutral and ground to a four position receptacle you are fine. The motor home has 50 amps breakers and will not draw more than 50 amps before tripping in the motor home entrance panel. If every thing is rated for 60 amps on your side you are actually safer. I have yet to see a motor home ever coming close to 50 amps per leg.

This is the right receptacle NEMA 5-50R

50 amp 120/240 volt 3 pole with ground

If the receptacle is wrong you could make an adapter.

__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C Handicap Equipped
F53/V10
1999 Jeep Cherokee & 1991 Jeep Wrangler Renegade
John Hilley is offline   Reply With Quote
Old 09-10-2014, 09:37 AM   #13
Senior Member
 
draboo's Avatar
 
Holiday Rambler Owners Club
Join Date: May 2013
Location: North Myrtle Beach, SC
Posts: 284
I'm going to run about 25 feet of #8 3 wire with ground from the subpanel to the outside outlet.

The 60A 2 pole breaker is very,very old. I'm going to replace it with a fresh one.

I ll report back on the progress. Might not get to it for a few days. We are in the middle of moving out of our house and into our MH full time. We are parking for the winter at a friends home and are in need of a 50A service outlet there.

A large moving sale is planned for a week from this Saturday. Anyone in the Roseburg,OR area is welcome!
__________________
Brad and Pat, the Dad and Mom-Dawgs with Kiddo and Dinah-Mite, the Dawter-Dawgs full timin' in our 2002 HR Neptune DP with 2015 Indian Scout Toad
draboo is offline   Reply With Quote
Old 09-10-2014, 09:44 AM   #14
Senior Member
 
OLYLEN's Avatar
 
Monaco Owners Club
Join Date: Jan 2008
Location: Olympia, Wa
Posts: 2,680
Perhaps the experts can tell me why your panel at the S/B has a 200 amp main that ends at 15 amp breakers and it's OK. And a 30 amp RV can use a 50amp post with a cheater and it's OK, but not use a 60amp to a 50 amp.

LEN
__________________

__________________
2004 Clss C 31' Winnebgo
OLYLEN is online now   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
50 AMP Breaker keeps popping karencollins iRV2.com General Discussion 30 09-06-2014 06:52 PM
30 amp main breaker tripping woodworker414 RV Systems & Appliances 8 06-29-2014 01:32 PM
30 Amp Receptacle Replacement campnfool 5th Wheel Discussion 17 04-20-2014 10:49 AM
troubleshooting no power to receptacle gemini5362 Class A Motorhome Discussions 12 04-19-2014 08:35 AM
Heart Freedom 458 inverter excessive idle amp draw jm80129 RV Systems & Appliances 9 06-10-2013 03:45 AM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 09:58 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.