5500 onan generator quits

I have read of others having the same problem but no resolutions. why????

My generator quits. It seems to be getting worse, It used to restart but today it wont restart, and for now it is too hot to work on. I will pull the filter after it cools.

meanwhile I would like to know why I cannot find any text showing a parts breakdown for this unit. I have been told to check the oil level sensor but can,t find out where it is located, I want and need a maintenance and parts manual do you know where I can get one?

It is mounted in my 1999 Fleetwood pace arrow (onan marquis 5500 BGM)

Thanks....................Donny
donnyman is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-22-2012, 03:48 PM   #2
Senior Member
 
jdoc's Avatar
 
Texas Boomers Club
Fleetwood Owners Club
Freightliner Owners Club
Join Date: Jul 2001
Location: Big Spring, Texas
Posts: 776
Send a message via Yahoo to jdoc
Have you tried calling Cummins-Onan? They may be able to help you.

Jerry
__________________
Jerry and Janell
Navy by record, Marine by choice. 2020 Thor Chateau 31 W towing a 2019 Jeep Grand Cherokee Limited
jdoc is offline   Reply With Quote
Old 05-22-2012, 03:48 PM   #3
Community Administrator
 
CLIFFTALL's Avatar


 
Join Date: Aug 2009
Posts: 53,379
Blog Entries: 1
Donny. I googled 1999 Onan 5500 manual and got it. I can't seem to post it here but can email it to you if you pm your address to me or you can google it.On page #22 there is a troubleshooting section. Good luck.
__________________


Cliff,Tallulah and Buddy ( 1999-2012 )
CLIFFTALL is offline   Reply With Quote
Old 05-22-2012, 03:49 PM   #4
Senior Member
 
The General's Avatar
 
Forest River Owners Club
Freightliner Owners Club
Join Date: Sep 2007
Location: Rancho Cordova, California
Posts: 1,038
Send a message via Yahoo to The General
Quote:
Originally Posted by donnyman View Post
I have read of others having the same problem but no resolutions. why????

My generator quits. It seems to be getting worse, It used to restart but today it wont restart, and for now it is too hot to work on. I will pull the filter after it cools.

meanwhile I would like to know why I cannot find any text showing a parts breakdown for this unit. I have been told to check the oil level sensor but can,t find out where it is located, I want and need a maintenance and parts manual do you know where I can get one?

It is mounted in my 1999 Fleetwood pace arrow (onan marquis 5500 BGM)

Thanks....................Donny
Hi Donny,

Easy first: Top of the gen. crankcase oil.
http://www.cumminsonan.com/www/html/...dbook-2010.pdf

Page 17
Cranks But
Won’t Start
1. Fuel below generator pickup level in tank. 1. Add fuel.
2. Fuel supply shutoff valve closed. 2. Fully open fuel supply valve.
3. Carbon deposits on spark plug(s). 3. Remove spark plug(s) and replace.

4. Low oil level. 4. Add oil.

The next thing I would do is check if you are getting fuel to the carb:
If not the rubber fuel hose from gen into gas tank may be cracked and may suck air into carb.
Big job to drop gas tank and replace 13 year old fuel hose.

Let us know what happens AND

__________________
Steve Bernard
2009 Sportscoach Legend 40QS
425HP Cummins ISL/Allison3000/Freightliner XC-R
2007 Saturn Vue RedLine
The General is offline   Reply With Quote
Old 05-22-2012, 05:49 PM   #5
Senior Member
 
donnyman's Avatar
 
Fleetwood Owners Club
Join Date: Feb 2011
Posts: 151
Blog Entries: 4
gen.

Hello all!
My generator is running as I type this. It cranked up immediately after cooling and I intend to let it run for at least four hours with both ac's running at max settings I have two hours to go.

Thanks for your responses the only one not tried (but will be) is to call Cummings - Onan. I checked, My filter was clean As I had done a complete tune up on the gen. not to long ago. I have the operator and install pamphlets, not much help!

The owners manual says do not over fill the oil and I thought I did real good with this but not really, it was a little over the fill mark, that is until it heated up then it was way over the fill mark. so I drained it down to the normal range. that's all and it is running smoothly now, I don't really believe this but we will see. I truly feel something is heating up and failing, only time will tell. I will return if something happens.
donnyman is offline   Reply With Quote
Old 05-22-2012, 05:52 PM   #6
Community Administrator
 
CLIFFTALL's Avatar


 
Join Date: Aug 2009
Posts: 53,379
Blog Entries: 1
Great. Thanks for the update.
__________________


Cliff,Tallulah and Buddy ( 1999-2012 )
CLIFFTALL is offline   Reply With Quote
Old 05-22-2012, 09:44 PM   #7
Senior Member
 
The General's Avatar
 
Forest River Owners Club
Freightliner Owners Club
Join Date: Sep 2007
Location: Rancho Cordova, California
Posts: 1,038
Send a message via Yahoo to The General
Quote:
Originally Posted by donnyman View Post
Hello all!
My generator is running as I type this. It cranked up immediately after cooling and I intend to let it run for at least four hours with both ac's running at max settings I have two hours to go.

Thanks for your responses the only one not tried (but will be) is to call Cummings - Onan. I checked, My filter was clean As I had done a complete tune up on the gen. not to long ago. I have the operator and install pamphlets, not much help!

The owners manual says do not over fill the oil and I thought I did real good with this but not really, it was a little over the fill mark, that is until it heated up then it was way over the fill mark. so I drained it down to the normal range. that's all and it is running smoothly now, I don't really believe this but we will see. I truly feel something is heating up and failing, only time will tell. I will return if something happens.

Donny,

Fingers Xd
__________________
Steve Bernard
2009 Sportscoach Legend 40QS
425HP Cummins ISL/Allison3000/Freightliner XC-R
2007 Saturn Vue RedLine
The General is offline   Reply With Quote
Old 05-23-2012, 06:37 AM   #8
Senior Member
 
donnyman's Avatar
 
Fleetwood Owners Club
Join Date: Feb 2011
Posts: 151
Blog Entries: 4
Just want to say thanks to all!

It helps me a lot to have input from others as it fires my brain up and I am inspired to keep going to solve the problem. this site and it's members have saved me time and a lot of money!!!!!!
again thank you.........................Donny
donnyman is offline   Reply With Quote
Old 07-19-2012, 11:29 AM   #9
Senior Member
 
donnyman's Avatar
 
Fleetwood Owners Club
Join Date: Feb 2011
Posts: 151
Blog Entries: 4
Smile generator up date

I just replied to a person with the same problem I had,...... no reply yet.

But the overfill was the problem with mine I have run the unit all day without so much as a burble. accurate filling is a must!

Donny
donnyman is offline   Reply With Quote
Reply

Tags
generator, onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:53 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.