Which fan motor are you having trouble with? I would take that it might be the condenser fan motor since it was probably pulled for the coil repair. Suggest you start at the motor and see if you have voltage when unit is turned on, engine is running and compressor pumping. If no voltage you should check for blown fuse. If fuse is good It probably has a Bosh type relay; check to be sure this is getting power and signal. There may also be a pressure switch in the condenser circuit to increase the fan speed when pressure is high. Most likely it will be something simple to diagnose if you know where these components are located on the coach. Good luck and keep us posted.