Adding a Heating Duct and Vent to My Fifth Wheel

This post is about how I added new heating system register and ducting to my 2018 Arctic Fox 29-5T fifth wheel. I was asked in another thread to post this information. Rather than distract from the topic of the other thread I am posing the information here.

I added an additional duct when it became apparent that the ducting in my RV could not expel the hot air from the furnace fast enough. This caused an excessive build-up of hot air in the furnace which in turn caused the burner to short-cycle on-and-off repeatedly which was overworking the high temp limit switch (a safety switch that shuts off the burner when the furnace overheats) and leading to the need for a premature repair. Adding the additional duct allows the furnace to better expel the hot air so that it no longer overheats and no longer short-cycles. A furnace burner should turn on and remain on until the RV reaches the temperature set on the thermostat. If the burner turns on and off repeatedly before the RV comes to the set temp there is a problem. Many RVs have this problem unbeknownst to the owners. It can be caused by a clogged or damaged vent or by the RV manufacturer not providing ample ducting when designing and building the RV (this happens!) or another problem. (Note: a burner can cycle repeatedly while the fan continues to run. If one listens carefully to the furnace it may be possible to hear the burner turn on and off. Placing a quick reading thermometer such as a digital food thermometer over a heating register will show if the burner comes on and off--the temperature will vary maybe 20 to 40 degrees as it cycles on and off.)

My 29-5T has a Suburban SF-35FQ furnace located under the fridge. (This is not a great spot, IMHO, because the fridge above it is trying to keep things cold while the furnace is heating things up from underneath. It would be better to keep refrigerators and furnaces further apart and not placing one above the other especially with the furnace beneath... but I digress.)

The SF-35FQ has seven, 4” circular vent knockouts on its sides to which 4” round, flexible ducting can be attached via a collar which is inserted into the furnace after a knockout is removed. It also has a large rectangular duct on the bottom which is equivalent to four of the 4” round vents.

Suburban requires at least four of the vents be used when installing this furnace. Arctic Fox did that by using the vent on the underside of the furnace, but they also incorporated 90 degree bends into the ducting and these 90 degree bends reduce the airflow and work against the minimum requirement for outlet ducting. Suburban says “Avoid making any sharp turns in the duct system. Sharp turns will increase the static pressure in the plenum area and could cause the furnace to cycle.” That seems to be exactly what was going on in my RV.

I decided the easiest and best fix was to add another duct. In order to do that I removed the grille from in front of the furnace (4 Phillips head screws), then the furnace cover (2 slotted screws). I then pried off one of the knockouts on the left of the furnace using a chisel, small hammer and pliers. For the new vent I cut a hole in the paneling where it was to be placed. For that I covered the area with painter's tape in order to minimize the likelihood of the surface of the wood splintering. Then using a pencil compass I marked a circle on the tape that I would cut out using a rotary tool at 30,000 RPM fitted with a spiral cutting bit designed to cut soft wood. Next, using a 4” hose clamp I attached the collar required to a piece of 4" UL Listed dryer vent ducting good up to 265 degrees and slid the collar with attached ducting into the cabinet housing the furnace, fitting it into the furnace where I had knocked out the vent cover. I attached the vent to the collar before putting the collar in place because I would not have been able to get to the hose clamp with a screwdriver once the collar was inside the cabinet. Then I slid another hose clamp onto the ducting over the free end and slid that end through the hole I had cut into the wood paneling and over the vent. Next, I placed the vent on the paneling, and after drilling pilot holes in the paneling screwed the vent into place after which I slid the hose clamp that was hanging loose on the ducting into position and clamped it down. Finally, I replaced the wood grille.

The addition of the new duct will not only add life to the furnace before requiring repair but because the furnace can now expel the heated air more quickly and the RV heats up much faster.

Parts List:
Suburban 050715 4" Duct Collar
Deflecto Supurr-Flex Aluminum Dryer Vent Duct, Flexible, Fire-Resistant, 4 Inches Dia. x 8 Feet, Silver (F0408B/4)
4" Hose Clamps
Valterra A10-3353VP Rotating/Dampered Heating and A/C Register-4″ ID x 5-3/8″ OD
Painter's tape

Tool List:
1/8" spiral cutting bit for soft wood
Rotary tool (like Black & Decker RTX, Roto Zip or Dremel)
Flat and #2 Phillips bit screwdriver
Pliers
Chisel (may not be necessary)
Small hammer (may not be necessary
Attached Thumbnails
Click image for larger version

Name:	Suburban RV Furnace.jpg
Views:	94
Size:	81.9 KB
ID:	268152   Click image for larger version

Name:	Vent Collar.jpg
Views:	69
Size:	119.7 KB
ID:	268153  

Click image for larger version

Name:	Valterra Vent.jpg
Views:	63
Size:	120.6 KB
ID:	268154   Click image for larger version

Name:	Deflecto Duct 1000.jpg
Views:	78
Size:	158.4 KB
ID:	268155  

Click image for larger version

Name:	thermometer IMG_9493.jpg
Views:	102
Size:	141.4 KB
ID:	268156   Click image for larger version

Name:	Furnace IMG_9784_1200-02.jpg
Views:	99
Size:	156.7 KB
ID:	268157  

Click image for larger version

Name:	collar in place IMG_9774_1024.jpg
Views:	89
Size:	126.5 KB
ID:	268158  
RussOnTheRoad is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-28-2019, 07:28 PM   #2
Senior Member
 
Outdoors RV Owners Club
Join Date: Dec 2017
Location: wasaga beach ont
Posts: 166
Very interesting. Great job and lots of information thanks for sharing. May try to add one in front off my closet in bedroom.
benderdog is offline   Reply With Quote
Old 11-28-2019, 09:17 PM   #3
Senior Member
 
RussOnTheRoad's Avatar
 
Join Date: Oct 2013
Posts: 859
Quote:
Originally Posted by benderdog View Post
Very interesting. Great job and lots of information thanks for sharing. May try to add one in front off my closet in bedroom.
This isn't rocket science but there are things that can be done wrong so I think it's a good idea to consult the literature from the furnace mfr. I did not include such info in my post, for example, vent ducts must be a certain distance from the furnace intake in order to avoid the furnace taking in heated air which can cause it to overheat.

There may be additional helpful info on YouTube and other forum posts, perhaps some of it unintentionally showing how not to do something like this.
RussOnTheRoad is offline   Reply With Quote
Old 12-02-2019, 03:02 PM   #4
Senior Member
 
Outdoors RV Owners Club
Join Date: Oct 2017
Posts: 149
Thank you for the detailed information. The furnace in my rig is right under my fridge also, however I have not noticed the fluctuations.


Regards


//KMac
__________________
2020 GMC 3500HD Denali SRW CC Duramax
2017 ORV Timber Ridge Titanium 26RLS
2020 Alliance Paradigm 310RL, Richland, WA
kmac7800 is offline   Reply With Quote
Old 12-02-2019, 03:09 PM   #5
Senior Member
 
RussOnTheRoad's Avatar
 
Join Date: Oct 2013
Posts: 859
Quote:
Originally Posted by kmac7800 View Post
Thank you for the detailed information. The furnace in my rig is right under my fridge also, however I have not noticed the fluctuations.


Regards


//KMac
I did not mean to suggest that the repeated on-off-on-off cycling of the furnace in my unit (or anybody else's) would be related to the relative position of the fridge and furnace. I only mentioned that my fridge was above my furnace as an unrelated observation about a design that didn't seem the best idea.

The furnace burner cycling was caused by my furnace not being able to sufficiently expel the hot air it makes which caused the burner to overheat and the high temperature limit switch to activate.
RussOnTheRoad is offline   Reply With Quote
Old 12-06-2019, 11:44 AM   #6
Member
 
Join Date: Apr 2018
Posts: 74
Can't say that I have noticed this up to now. I will check this though. Seems like this could be problematic if not addressed.
__________________
Truck: 2018 Ram Laramie Longhorn Limited Edition 3500 SRW 4x4.
Trailer: 2018 Arctic Fox 29.5T.
Ryqster is offline   Reply With Quote
Old 12-06-2019, 11:50 AM   #7
Senior Member
 
RussOnTheRoad's Avatar
 
Join Date: Oct 2013
Posts: 859
Quote:
Originally Posted by Ryqster View Post
Can't say that I have noticed this up to now. I will check this though. Seems like this could be problematic if not addressed.
I have heard from an owner of a 2018 Arctic Fox 32.5M that he is seeing the problem. I have also heard from an owner of an Arctic Fox 29-5T that he hadn't noticed it, but I asked him to take a careful look. I don't mean to single out Arctic Fox because I expect this may be a more widespread issue.

I do hope you will check your 5T and report back whether or not you are seeing the temp swings at the register and notice excessive burner cycling or not.

BTW, your signature file indicates you have a 28-5T. I'm guessing that's a typo... I never heard of a 28-5T. You must have meant 29-5T, no?
RussOnTheRoad is offline   Reply With Quote
Old 12-06-2019, 12:10 PM   #8
Member
 
Join Date: Apr 2018
Posts: 74
Typo...oops
__________________
Truck: 2018 Ram Laramie Longhorn Limited Edition 3500 SRW 4x4.
Trailer: 2018 Arctic Fox 29.5T.
Ryqster is offline   Reply With Quote
Old 12-13-2019, 07:04 AM   #9
Member
 
grantrekker's Avatar
 
Join Date: Jun 2019
Location: Maple Valley, WA
Posts: 68
Great info and timely for my purposes, AND I hope this reply is not viewed as too much of a digression that it needs it's own thread. It seems what you have done is applicable to what I intend to undertake. History: In my 2014 AF 29.5K, the heat unit (appears to be identical to the picture you posted) is under the kitchen sink cabinetry. I noticed that the entire cabinet was warming up so I pulled some drawers and panels and discovered that one of the large knockouts on the top was dislodged and had fallen down into the plenum (?) which seems to surround heat tubes (I now believe you are aware of my lack of education with respect to HVAC). Since this "cabinet warming" happened suddenly on the Alcan Highway and the large knockout was just laying on the tubes in the plenum, I assumed this knockout was intended to remain intact. Now, RV shops in Seward, AK do not exist so I went to the well stocked local hardware store and bought some of the silver ducting tape and some tin and tinsnips and cut a sheet which I superimposed over the open area where the failed knockout was removed from. Problem solved I hope. ??? Now to the issue at present. My observation is that the only heat duct exiting from the plenum originates from the bottom of the plenum area (I think I have that term right) and enters a duct that feeds four vents, two in the lower cabin and two in the upper bedroom cabin and whatever else is shuttled to heat the water and waste tanks. We leave two heat register vents in the upper cabin shut permanently as we enjoy cold sleeping and can tolerate a chilly bathroom and shower area or can open the connecting door to the upper area and the warm "downstairs" air heats the upper room very well. In the process of this on the road repair, I noticed that there are two 4" knockouts that face into the living area (floor level) and thought that I would take one of these out and introduce warm air into the main lower cabin through the cabinet wall which is approx. 1-1/2" from the knockout. This is intended to 1) allow for additional warm air introduction into the lower cabin hopefully resulting in quicker warm-up time, and 2) provide a airflow offset to the heat registers that we keep closed in the upper cabin in the event that there is some back pressure issue created by only using two of the four cabin register outlets in the factory design. First question: Am I on track with this so far? Your post states "...Suburban requires at least four of the vents be used when installing this furnace. Arctic Fox did that by using the vent on the underside of the furnace." Assuming this to be the case for my heating unit and observing that the only exit vent used is the large rectangular down vent that effectively services only two active cabin registers and whatever flow that is directed down into the holding tank areas, I question whether the required outflow is being met after adding the to be installed 4" vent. If all is good to this point, on to the next question.

Regarding installation of the new 4" vent. It appears as though the now removed 4" side vent can easily exit through a 1/8" wood cabinet base (much like the picture you show only my heat unit is under the kitchen cabinet complex and NOT the refer) into the lower cabin area just 1-1/2" away with just the addition of a collar and a vent cover, with maybe some ducting tape. Seems fairly simple. What am I missing? Would using both of the 4" side exits be better instead of just one?

Your observations of and answers to the above are greatly appreciated.
grantrekker is offline   Reply With Quote
Old 12-13-2019, 08:40 AM   #10
Senior Member
 
RussOnTheRoad's Avatar
 
Join Date: Oct 2013
Posts: 859
Quote:
Originally Posted by grantrekker View Post
Great info and timely for my purposes, AND I hope this reply is not viewed as too much of a digression that it needs it's own thread. It seems what you have done is applicable to what I intend to undertake. History: In my 2014 AF 29.5K, the heat unit (appears to be identical to the picture you posted) is under the kitchen sink cabinetry. I noticed that the entire cabinet was warming up so I pulled some drawers and panels and discovered that one of the large knockouts on the top was dislodged and had fallen down into the plenum (?) which seems to surround heat tubes (I now believe you are aware of my lack of education with respect to HVAC). Since this "cabinet warming" happened suddenly on the Alcan Highway and the large knockout was just laying on the tubes in the plenum, I assumed this knockout was intended to remain intact. Now, RV shops in Seward, AK do not exist so I went to the well stocked local hardware store and bought some of the silver ducting tape and some tin and tinsnips and cut a sheet which I superimposed over the open area where the failed knockout was removed from. Problem solved I hope. ??? Now to the issue at present. My observation is that the only heat duct exiting from the plenum originates from the bottom of the plenum area (I think I have that term right) and enters a duct that feeds four vents, two in the lower cabin and two in the upper bedroom cabin and whatever else is shuttled to heat the water and waste tanks. We leave two heat register vents in the upper cabin shut permanently as we enjoy cold sleeping and can tolerate a chilly bathroom and shower area or can open the connecting door to the upper area and the warm "downstairs" air heats the upper room very well. In the process of this on the road repair, I noticed that there are two 4" knockouts that face into the living area (floor level) and thought that I would take one of these out and introduce warm air into the main lower cabin through the cabinet wall which is approx. 1-1/2" from the knockout. This is intended to 1) allow for additional warm air introduction into the lower cabin hopefully resulting in quicker warm-up time, and 2) provide a airflow offset to the heat registers that we keep closed in the upper cabin in the event that there is some back pressure issue created by only using two of the four cabin register outlets in the factory design. First question: Am I on track with this so far? Your post states "...Suburban requires at least four of the vents be used when installing this furnace. Arctic Fox did that by using the vent on the underside of the furnace." Assuming this to be the case for my heating unit and observing that the only exit vent used is the large rectangular down vent that effectively services only two active cabin registers and whatever flow that is directed down into the holding tank areas, I question whether the required outflow is being met after adding the to be installed 4" vent. If all is good to this point, on to the next question.

Regarding installation of the new 4" vent. It appears as though the now removed 4" side vent can easily exit through a 1/8" wood cabinet base (much like the picture you show only my heat unit is under the kitchen cabinet complex and NOT the refer) into the lower cabin area just 1-1/2" away with just the addition of a collar and a vent cover, with maybe some ducting tape. Seems fairly simple. What am I missing? Would using both of the 4" side exits be better instead of just one?

Your observations of and answers to the above are greatly appreciated.
It sounds like you taped some tin on the furnace to cover the knockout that fell out. It may be more likely that the knockout was removed and left inside the furnace by a workman. That's the kind of thing I have come to expect from RV manufacturers. I believe they make duct cover plates for the purpose of covering knockouts that you can use instead of tin and tape. This might be the item:
https://www.rvautoparts.com/050733-S...iABEgI_W_D_BwE

You refer to a knockout on the "top" of the furnace. Did you mean "side"? I'm not sure there are any knockouts on top. Furnaces do differ from one to the next, I'm sure.

I would suggest you determine which furnace you have so that you can be certain of its requirements both in terms of servicing and parts. Manuals may be hard to find because Suburban doesn't seem to like the idea of regular Joes like us getting our hands on them but they can be found if not on the Suburban web site. Try this page/site:
https://techsupport.pdxrvwholesale.c...urban-sf-35fq/

The airflow requirements for ducting are in the installation instructions and are provided in terms of square inches and number of ducts required to be used... at least that's what I recall. I did say that Arctic Fox (more properly Northwood) met the venting requirements in my RV by using the bottom vent but I also said they put 90° bends in the ducting that works against that. Said another way I think they failed to meet the minimum venting requirements.

Registers need to be placed a minimum of 18" from the return air opening. From the installation instructions for the Suburban SF-20FQ • SF-25FQ • SF-30FQ • SF-35FQ • SF-42FQ: "No outlet register is to be placed within 18” of the return air opening. Any register installed at 18” should never be adjusted to blow the outlet air toward the return air opening. If a register is installed on a wwall [sic] 90 degrees to the return air, it can be less than the 18”. They don't want hot air coming back into the furnace because this can cause it to overheat. You can get a copy of the instructions at the page/site I mentioned above.

I found all the parts I used on Amazon. BTW, the vent register I used protrudes several inches on the rear to allow for attaching 4" flexible ducting. I don't think you could use it if the furnace is only 1.5" from the wall on which you plan to mount the register. You may need to use a knockout on another side of the furnace with some flexible ducting.

HTH.
RussOnTheRoad is offline   Reply With Quote
Old 12-13-2019, 10:16 AM   #11
Member
 
grantrekker's Avatar
 
Join Date: Jun 2019
Location: Maple Valley, WA
Posts: 68
Quote:
Originally Posted by RussOnTheRoad View Post
It sounds like you taped some tin on the furnace to cover the knockout that fell out. It may be more likely that the knockout was removed and left inside the furnace by a workman. That's the kind of thing I have come to expect from RV manufacturers. I believe they make duct cover plates for the purpose of covering knockouts that you can use instead of tin and tape. This might be the item:
https://www.rvautoparts.com/050733-S...iABEgI_W_D_BwE

You refer to a knockout on the "top" of the furnace. Did you mean "side"? I'm not sure there are any knockouts on top. Furnaces do differ from one to the next, I'm sure.

I would suggest you determine which furnace you have so that you can be certain of its requirements both in terms of servicing and parts. Manuals may be hard to find because Suburban doesn't seem to like the idea of regular Joes like us getting our hands on them but they can be found if not on the Suburban web site. Try this page/site:
https://techsupport.pdxrvwholesale.c...urban-sf-35fq/

The airflow requirements for ducting are in the installation instructions and are provided in terms of square inches and number of ducts required to be used... at least that's what I recall. I did say that Arctic Fox (more properly Northwood) met the venting requirements in my RV by using the bottom vent but I also said they put 90° bends in the ducting that works against that. Said another way I think they failed to meet the minimum venting requirements.

Registers need to be placed a minimum of 18" from the return air opening. From the installation instructions for the Suburban SF-20FQ • SF-25FQ • SF-30FQ • SF-35FQ • SF-42FQ: "No outlet register is to be placed within 18” of the return air opening. Any register installed at 18” should never be adjusted to blow the outlet air toward the return air opening. If a register is installed on a wwall [sic] 90 degrees to the return air, it can be less than the 18”. They don't want hot air coming back into the furnace because this can cause it to overheat. You can get a copy of the instructions at the page/site I mentioned above.

I found all the parts I used on Amazon. BTW, the vent register I used protrudes several inches on the rear to allow for attaching 4" flexible ducting. I don't think you could use it if the furnace is only 1.5" from the wall on which you plan to mount the register. You may need to use a knockout on another side of the furnace with some flexible ducting.

HTH.
Thnak you RussOnTheRoad for your most informative and timely reply. I will reply to your comments:

1) there was a large retangular knockout on the top of the unit and is in the same place that your picture shows the indented area or what I assumed to be a knock out as it was still hanging down into the plenum by a shred of a tab

2) I will measure the now large opening on the top and order the cover you suggested, That is a much more elegant covering than my tin & tape on-the-road solution

3) I do need to find the model number on this unit. Am afraid it is on the top and if so would entail destruction of the cabinet to some degree to view.

4) Airflow requirement as you state "...for ducting are in the installation instructions and are provided in terms of square inches and number of ducts required to be used.... As best as I can determine, the only outlet from the plenum that was used was what I assume to be downward and into the basement area. Further it seems to be a pretty straight shot for the ducting without any severe bends. However, if the manual describes the airflow requirements in terms of output from the plenum, this would be simply one large downward knockout into the main lateral vent line with the four cabin registers and whatever holding tank exits exist. Wouldn't covering/shutting 2 of the factory cabin registers then restrict the airflow at the end distribution point to the same effect as shutting it down at the plenum (except considering the downflow directed to the holding tank areas)? I have effectively closed down 32s.i. of flow so reasoned that opening up one 4" hole withing 1-1/2" of the plenum would be replacing the outflow by only about 12.6s.i. So I might be shy by quite a bit for a one to one replacement of the closed vents if that is to be considered.
5) Regarding placement of the new 4" outlet, it is in a "wall", can be directed with the register cover and will be about 30" from the air return at the end of the bar area. Will have to check the manual when I find the model etc, and confirm this works.
6) Thanks to your research and part numbers, I have ordered the parts on Amazon and I read the collar depth as 1.1" although am not sure as it gives product dimensions as 4 x 1.1 x 5 inches and I'm not sure how to interpret this. Will see when it arrives tomorrow and may need to get the snips out.

What am I missing???
__________________
Home in western Washington State from where wife and I travel all seasons in our 2018 Arctic Fox 29.5K fifth wheel, outfitted with solar and a few Li batteries, and usually weighing in at around 14K. Pulled by 2019 F450 stock King Ranch 6.7L diesel.
grantrekker is offline   Reply With Quote
Old 12-13-2019, 10:37 AM   #12
Member
 
grantrekker's Avatar
 
Join Date: Jun 2019
Location: Maple Valley, WA
Posts: 68
Regarding response 6) above, Isee that I am in error as you mentioned the cover, not the collar. Well, both will be here tomorrow so I may have some reduction to do on the collar
__________________
Home in western Washington State from where wife and I travel all seasons in our 2018 Arctic Fox 29.5K fifth wheel, outfitted with solar and a few Li batteries, and usually weighing in at around 14K. Pulled by 2019 F450 stock King Ranch 6.7L diesel.
grantrekker is offline   Reply With Quote
Old 12-13-2019, 12:14 PM   #13
Senior Member
 
RussOnTheRoad's Avatar
 
Join Date: Oct 2013
Posts: 859
Quote:
Originally Posted by grantrekker View Post
Thnak you RussOnTheRoad for your most informative and timely reply. I will reply to your comments:

1) there was a large retangular knockout on the top of the unit and is in the same place that your picture shows the indented area or what I assumed to be a knock out as it was still hanging down into the plenum by a shred of a tab

2) I will measure the now large opening on the top and order the cover you suggested, That is a much more elegant covering than my tin & tape on-the-road solution

3) I do need to find the model number on this unit. Am afraid it is on the top and if so would entail destruction of the cabinet to some degree to view.

4) Airflow requirement as you state "...for ducting are in the installation instructions and are provided in terms of square inches and number of ducts required to be used.... As best as I can determine, the only outlet from the plenum that was used was what I assume to be downward and into the basement area. Further it seems to be a pretty straight shot for the ducting without any severe bends. However, if the manual describes the airflow requirements in terms of output from the plenum, this would be simply one large downward knockout into the main lateral vent line with the four cabin registers and whatever holding tank exits exist. Wouldn't covering/shutting 2 of the factory cabin registers then restrict the airflow at the end distribution point to the same effect as shutting it down at the plenum (except considering the downflow directed to the holding tank areas)? I have effectively closed down 32s.i. of flow so reasoned that opening up one 4" hole withing 1-1/2" of the plenum would be replacing the outflow by only about 12.6s.i. So I might be shy by quite a bit for a one to one replacement of the closed vents if that is to be considered.
5) Regarding placement of the new 4" outlet, it is in a "wall", can be directed with the register cover and will be about 30" from the air return at the end of the bar area. Will have to check the manual when I find the model etc, and confirm this works.
6) Thanks to your research and part numbers, I have ordered the parts on Amazon and I read the collar depth as 1.1" although am not sure as it gives product dimensions as 4 x 1.1 x 5 inches and I'm not sure how to interpret this. Will see when it arrives tomorrow and may need to get the snips out.

What am I missing???
I have wondered about the rectangular piece on top of the furnace as to whether or not it's intended to be used as a vent. The Suburban rep I spoke to did not mention that as being a vent nor the other way around. He did say the unit has 11 vents counting 7 on the sides and the one on bottom as 4. He may have missed the vent on top if that's what it is. The installation manual does seem to indicate it is a vent if I read it right.

Re: your #2: The knockout cover I referenced was for the 4" round vents on the furnace, not the rectangular one on top or bottom.

Re: #3: The model number for my furnace was found under the front cover where the high temp limit sensor is located. You could call Northwood and ask or possibly query other owners at nroa2003.com. Either would be easier than pulling the unit or cutting it into pieces.

Re: # 4: It seems you may be missing the fact that there is one 90° bend in the ducting at the furnace where either the top or bottom rectangular vent is located if the hot air is redirected from the vertical plane to the horizontal which it is, and another 90° bend where the ducting turns upward through the floor where the in-floor registers are, if you have those. If you have 4 in-floor registers you have at least 5 90° bends assuming your furnace vents through the bottom. Suburban told me that using just the bottom vent met the bare minimum requirements for the SF-35FQ and using more was better. Also that 90° bends in the ducting work against that minimum requirement. Do you think then that Northwood has satisfied the minimum venting requirements where it may use just the bottom vent for that furnace and incorporate 90° bends in the ducting? Also, the manual specifies vents into sealed areas such as holding tank areas do not count and in my unit that vent comes off the ducting anyway and not the furnace itself. It does not add venting capacity. Please refer to the installation instructions yourself so I don't have to do it for you repeatedly. Closing dampers on registers acts against the minimum requirements as to venting. So, where you have the minimum requirements being met, or less than those, installing damped registers is, IMHO, irresponsible.
RussOnTheRoad is offline   Reply With Quote
Old 12-13-2019, 01:01 PM   #14
Member
 
grantrekker's Avatar
 
Join Date: Jun 2019
Location: Maple Valley, WA
Posts: 68
Thanks RussOnTheRoad, your help has been most valuable.
__________________
Home in western Washington State from where wife and I travel all seasons in our 2018 Arctic Fox 29.5K fifth wheel, outfitted with solar and a few Li batteries, and usually weighing in at around 14K. Pulled by 2019 F450 stock King Ranch 6.7L diesel.
grantrekker is offline   Reply With Quote
Reply

Tags
fifth wheel, vent, heating, heat



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Downsizing from 35 ft fifth wheel to shorter fifth wheel or trailer campinsharz 5th Wheel Discussion 31 03-02-2018 04:54 PM
Adding additional heating vent on furnace mr. seaview National RV Owner's Forum 1 02-04-2016 02:41 PM
Installing vent fan in Fifth Wheel LR vent SkiSmuggs iRV2.com General Discussion 1 03-30-2015 08:12 AM
Carriage 37cksls bedroom AC 2 duct or not 2 duct Tumble Weed 5th Wheel Discussion 2 07-22-2013 06:14 PM
AC Vent and Duct cleaning lthrnk Winnebago Industries Owner's Forum 7 09-01-2008 05:01 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:50 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.