Old 05-31-2007, 04:02 PM   #1
Member
 
Join Date: May 2007
Location: Maryland
Posts: 48
Any suggestions for an air conditioner that freezes up? It ran fine until the 90 degree heat hit - then it froze up. I defrosted it with a blow dryer and it ran fine again, but the next day it froze up again. Is there anyone out there with HVAC experience that could give me an idea of what would cause the unit to freeze up? It literally had ice covering the coils and that is what caused it to shut down. Thanks.
__________________

__________________
The White Family (including our dog Jack)

1999 Damon Intruder
Darrell & Mel is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-31-2007, 04:02 PM   #2
Member
 
Join Date: May 2007
Location: Maryland
Posts: 48
Any suggestions for an air conditioner that freezes up? It ran fine until the 90 degree heat hit - then it froze up. I defrosted it with a blow dryer and it ran fine again, but the next day it froze up again. Is there anyone out there with HVAC experience that could give me an idea of what would cause the unit to freeze up? It literally had ice covering the coils and that is what caused it to shut down. Thanks.
__________________

__________________
The White Family (including our dog Jack)

1999 Damon Intruder
Darrell & Mel is offline   Reply With Quote
Old 05-31-2007, 04:38 PM   #3
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 7,897
Low refrigerant is the likely cause. Oddly enough, my heat pumps will freeze up in the 30's, but the A/C side works fine.
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA 1SG, retired, Good Sam Life member.
The Constitution is not neutral. It was designed to take the government off the backs of people. Supreme Court Justice Douglas
Ray,IN is online now   Reply With Quote
Old 05-31-2007, 04:51 PM   #4
Moderator Emeritus
 
TXiceman's Avatar


 
Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Full Time, TX Home Base
Posts: 16,707
Blog Entries: 20
Most likely the problem is not low refrigerant. The units are sealed (hermetic) and seldom loose refrigerant unless you have a pin hole leak from vibration or corrosion.

The usual problem with freezing up is low air flow across the evaporator. Do you clean the filter regularly and check to see if the coil is clean? Don't run the fan on low speed as it is more likely to freeze due to low air flow.

A simple check to see if the unit is cooling Ok is to start the unit and run it on high fro about 10 minutes. Check the temperature of the air entering the unit and then the air leaving a duct near the unit. The leaving air should be 15 to 20 dF lower than the entering air. If it is more, you may have reduced air flow or possible low on refrigerant.

Ken
__________________
Amateur Radio Operator (KE5DFR)|Full-Time! - 2012 6.7L Ford Crew Cab Dually -2013 HitchHiker Champagne 38RLRSB - Travel with one Miniature Schnauzer, one Standard Schnauzer and one small Timneh African Gray Parrot
TXiceman is online now   Reply With Quote
Old 05-31-2007, 11:49 PM   #5
Community Moderator
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 10,194
We often find that the unit are short cycling the discharge air back into the return air allowing the evaporator temperature to subcool and freeze up. CHeck to be sure the return area of the ceiling pacakge is well seperated (use metal foil tape) to seal off this area from the dischage side of the ceiling package. Make sure coil is clean, if ducted not vents are closed, run fan on high and try to keep humidity down. GOod luck and keep us posted as to the outcome. as best possible
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 350 ISC w/ Banks = 450Hp & 1330# torque
06 Saturn Vue & 06 Chevy Z71 4x4 toads
RV Wizard is online now   Reply With Quote
Old 06-22-2007, 05:21 PM   #6
Member
 
Join Date: May 2007
Location: Maryland
Posts: 48
Mike,
I have a question for you. When I look up into the AC unit, there are two sides to the unit. Is one of them the discharge side and the other side the return side? If that is the case, I also see a piece of foam covered with metal foil. It is about 5" by 8" and is about 1" thick. What is the purpose of this foam piece? Also, I am not sure where that foam piece should be positioned in the unit. Thanks for your help!
__________________
The White Family (including our dog Jack)

1999 Damon Intruder
Darrell & Mel is offline   Reply With Quote
Old 06-22-2007, 07:36 PM   #7
Moderator Emeritus
 
TXiceman's Avatar


 
Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Full Time, TX Home Base
Posts: 16,707
Blog Entries: 20
You should be able to flow the air from the fan outlet into a duct in the ceiling. The baffle should seal this area from the inlet air side (filter side).

Ken
__________________
Amateur Radio Operator (KE5DFR)|Full-Time! - 2012 6.7L Ford Crew Cab Dually -2013 HitchHiker Champagne 38RLRSB - Travel with one Miniature Schnauzer, one Standard Schnauzer and one small Timneh African Gray Parrot
TXiceman is online now   Reply With Quote
Old 06-28-2007, 12:48 PM   #8
Member
 
Join Date: May 2007
Location: Maryland
Posts: 48
Thanks Ken! I will check the position of the baffle, reposition it if necessary, then try running the AC and check to see if it freezes up again.

V/r,
Darrell
__________________
The White Family (including our dog Jack)

1999 Damon Intruder
Darrell & Mel is offline   Reply With Quote
Old 06-28-2007, 04:31 PM   #9
Senior Member
 
Join Date: Apr 2000
Location: Lake Almanor, CA USA
Posts: 419
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by Darrell & Mel:
Any suggestions for an air conditioner that freezes up? It ran fine until the 90 degree heat hit - then it froze up. </div></BLOCKQUOTE>
Our experience, when our AC froze up (non-ducted, roof mount), was to back off the temperature control a little. Rather than putting it in the most extreme "cold" position, we run it with about 1/8" from that post. This gives the compressor time to cycle off & on, giving it time to "de-ice" if necessary. It has never iced up in the past 4 years since we started this procedure.

We are in humid Branson, MO right now, and inside the trailer it is 72 degrees, 60% humidity. Outside it is 80 degrees, 85% humidity. It was warmer during the day and is cooling off now because of some showers, but the AC continues to keep the trailer consistently cool.
__________________
Paul <?)))>< Lake Almanor, CA

2002 Thor Tahoe 23FBGL TT, 28'
Paul Heuvelhorst is offline   Reply With Quote
Old 06-29-2007, 02:27 AM   #10
Senior Member
 
mrschwarz's Avatar
 
Winnebago Owners Club
Texas Boomers Club
Freightliner Owners Club
Join Date: Jul 2006
Posts: 829
Send a message via Skype™ to mrschwarz
Freezes up regularly is a symptom of a system low on refrigerant charge. If it happens occasionally on a humid day, others advice makes sense.
__________________
Michael
2010 Winnebago Tour 42AD, Cummins ISL 400, Allison 3000, Progressive EMS, Aventa II, Air Force One, Tire Safeguard TPMS, Blue Ox Tru Center (maybe), Lotsa LEDs
mrschwarz is offline   Reply With Quote
Old 06-29-2007, 05:19 AM   #11
Moderator Emeritus
 
TXiceman's Avatar


 
Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Full Time, TX Home Base
Posts: 16,707
Blog Entries: 20
9 out of 10 RV A/C freeze ups are low air flow, and seldom low refrigerant. Look first at low air flow due to restricted filters, low fan speed, dirty evaporator coil or bypassing air between the inlet and out let of the unit.

The units are factory sealed (hermetic) and are not easily checked or repaired by the normal shade tree mechanic. People will use the short cut of a saddle clamp and add some refrigerant. Problem is the saddle clamps are bad leakers. you have to use one to access the system and clear the refrigerant. then you have to solder in two Schrader valves with low pressure N2 flowing in the lines to prevent oxidization inside due to the heat. Next you use a vacuum pump and pull the system into a deep vacuum to get the moisture and air. Then you finally recharge the system with refrigerant.

The easiest thing to do is check for low air flow. When operating correctly, there should be about a 20 dF difference between inlet air and outlet air on the unit.


Ken
__________________
Amateur Radio Operator (KE5DFR)|Full-Time! - 2012 6.7L Ford Crew Cab Dually -2013 HitchHiker Champagne 38RLRSB - Travel with one Miniature Schnauzer, one Standard Schnauzer and one small Timneh African Gray Parrot
TXiceman is online now   Reply With Quote
Old 06-30-2007, 02:57 PM   #12
Member
 
Join Date: May 2007
Location: Maryland
Posts: 48
Thanks for the information. What I found today as I was working on various things on my coash is that the flow divider (or baffle) that is supposed to separate the inlet from the outlet was not positioned properly, and was allowing air flow to go directly from the outlet (ducted side) to the inlet (or return side). So I repositioned the flow divider and ran the unit for two hours today with no freezing up. Now I am looking forward to running the unit during a hot summer day for several hours, but I think the flow divider was the culprit.
__________________
The White Family (including our dog Jack)

1999 Damon Intruder
Darrell & Mel is offline   Reply With Quote
Old 06-30-2007, 04:32 PM   #13
Senior Member
 
machman72's Avatar
 
Appalachian Campers
Join Date: Mar 2005
Location: La Grange, North Carolina
Posts: 327
This is what I love about this site. All the good knowledge here. My AC froze up twice last summer while I was in Florida. I "assumed" it was low on refrigerant myself, and knowing it is a sealed unit, wondered who or how to fill it. Before going to that extreme though, I removed top and bottom covers, blew everything out good, cleaned the filter, tightened up the floppy air deflectors, and carefully put everything back together. I have not had a problem since. Had to be an airflow problem that was fixed with the cleaning.
__________________

__________________
Your never too old to have a happy childhood.
machman72 is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
air conditioner ljelinger Winnebago Industries Owner's Forum 9 05-25-2008 05:47 PM
Air Conditioner gunny Winnebago Industries Owner's Forum 17 09-05-2007 11:15 AM
Manual for True Air Air Conditioner? #2 Compressor Inop? FlyingW Winnebago Industries Owner's Forum 32 09-05-2007 09:05 AM
Loss of Air - Basement Air Conditioner Ducts j griff Winnebago Industries Owner's Forum 8 07-14-2007 09:18 AM
Air Conditioner sawtooth Travel Trailer Discussion 4 03-31-2005 01:38 AM

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 08:19 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2014, vBulletin Solutions, Inc.