Jim,
Hopefully your furnace is working by now.
If not, here is some information for you concerning your 7900-II: (this information came from an original Hydroflame 7900 manual - Atwood bought Hydroflame some time ago.)
What the manual doesn't tell you:
The fan runs first to "purge" the combustion chamber. When the gas valve opens, you should hear a single "snap" sound. Next, you should hear the rapid "ticking" of the ignitor. These sounds occur in immediate sequence: "snap" then "ticking" (and they
are different). The rapid "ticking" will last for about six seconds then stop. The fan will contine to run to purge the unlit propane from the chamber, then the board will try to cause ignition again. After three unsuccessful tries to ignite, all the furnace functions stop completely. It's a safety item referred to as board "lock-out". You
must turn the t-stat "OFF" completely, then "ON" again to reboot the board and restart the sequence.
Have you heard the two sounds described? (You may have to get close to the furnace to hear them.) If you have NOT, the board is not getting the necessary 12 volts to function - check the t-stat and 12 vdc power supply. If you HAVE, you now have two other possibilities - gas flow and ignitor function. Check both.
Hope this helps.