If the unit runs fine in A/C mode, but doesn't in Heat Pump, it may be the circuit board. If it doesn't run in either, my first guess would be the start capacitor(s). If you remove the panel covering the condenser coil you will see the electrical compartment to the left. There are 4 capacitors in total. The two black shorter ones are the start capacitors one for each compressor, and the two taller gray ones are the run capacitors again one for each compressor. Disconnect any 120v shore line power source and turn off your house batteries. Carefully remove the wires to one of the start capacitors, then take an insulated screwdriver and short across the two terminals. This will remove any residual electrical charge that may still be built up in the capacitor. Using a volt/ohm meter set to check continuity, adjust it to give a full scale reading (or full needle deflection if an analog meter) with the probes shorted together. Then connect one probe to one terminal of the capacitor, and watch the meter as you touch the second probe to the other terminal. If there is a quick needle (or reading) fluctuation from zero to say 1/4 of full scale deflection then back to zero, the capacitor is good. It has charged and discharged from the battery power in the volt meter. If there was no deflection, the capacitor is "open" and if the needle deflected to full scale and stayed there, the capacitor is "shorted". If that test is to be repeated, the capacitor terminals must first be shorted again to remove any residual charge. Either of the last two scenarios would require replacement.