Quote:
Originally Posted by RV Wizard
How about in the open forum?
|
skeptical of the "you did what" or "hey that is not a direct drop in"
and some one will get offended by "my" path to a repair.
but since i have no feelings........
stand by for heavy rolls.
i used a different motor, it has a built on cap.
Remember the movie "A space odyssey 2001" where HAL failed an antenna and made the crew go out side the spaceship to replace said device and then only to find later it wasn't failed at all, so they reinstalled and it worked fine and HAL then killed them all.
Well lets call my roof a/c HAL
after much searching and measuring i found a replacement motor at grainger supply, including taking back the first one and settling on the last one as a "BEST FIT"
its a model number 4UU28. Its by no means a drop in and go replacement, but it does meet the speed and up's the hp a bit. Plus its not made in Korea or China. It is shorter in the overall length for the motor body and has a built on capacitor so you will not need to lug it into the currently installed capacitor. The shaft ends, like all motors will need to be trimmed in length and are easy to cut with a powered hacksaw or by hand.
So here is the down and dirty
secure all POWER to the roof a/c
remove the plenum screws for the condenser fan cover and the rear cover of the heat exchanger.
remove the rear fan first.
then pop the clamps to hold the motor and use a 10 mm wrench to remove the cold air fan
then lay the motor aside.
I then took careful measures of the shaft height and relationship to the the plenums and then removed the factory motor mount
i acquired some alum channel and made new supports for the new motor to bolt in place on the existing mounting bracket
then mounted the new motor to it and went back up top to check the measures
and scribe exact shaft lengths needed ( this will not be the same as the old motor, so measure a few times before you commit). The shaft lengths are pretty flexible as well, take your time and "blue print" the install. get it as close to tolerance as possible for a smoother run.
then adjust as required for center and put on your fans.
then its a matter of plugging in the wires for the speeds and your golden.
now back to my HAL
the motor was squeaking but functional
so i removed it again and soaked the sleeve bearing with synthetic motor oil and ran it by hand to ensure it was lubed well
this actually dropped my running amp load by 2 amps.
and the motor spins very free now if you spin it by hand.
so i boxed up the replacement motor and mounting adapters and have it in the basement, for a quick change out if it acts up again or it cools off enough i can change it out without the risk of heat stroke.
www.http://bryantrv.com/docs.html
the above web site has the downloadable service manual for the unit and is pretty easy to follow
I also opened up the rear ac and lubed its sleeves bearings as well
the front one i found some rust on the bearing to shaft interface and I believe was the cause of the squeak and bind. funny thing is that area is exposed to COLD air from the a/c unit and it simply had condensate building up when cold air hit the hot motor sleeve bearing...duh
hope it helps
re-lubed motor has been running now almost non-stop for three weeks no squeaks