Old 03-20-2014, 02:50 PM   #15
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
Quote:
Originally Posted by njs42 View Post
You need to get this right. I'm not an electrician but I just had a box installed. This explanation is correct;

http://www.myrv.us/Imgs/PDF/50-amp%20Service.pdf
Yes .. just do as linked and everyone will be happy.
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-21-2014, 05:27 PM   #16
Senior Member
 
Ray,IN's Avatar
 
Join Date: Aug 2001
Location: North America somewhere
Posts: 30,982
Quote:
Originally Posted by FlyingDiver View Post
Just FYI - the pedestal needs to be wired as a true 240V circuit (two hot leads out of phase). If it's not, it's broken and should not be used.

Also, SOME RVs are actually wired with a real 240V subpanel and support 240V appliances (like our dryer). Not all are wired with two independent 120V legs.
You are exactly correct!
__________________
2000 Winnebago Ultimate Freedom USQ40JD, ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;Good Sam Life member,FMCA." My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
Ray,IN is offline   Reply With Quote
Old 03-21-2014, 05:45 PM   #17
Senior Member
 
PushedAround's Avatar
 
Tiffin Owners Club
Join Date: Sep 2012
Location: Ambler, PA
Posts: 2,853
Blog Entries: 7
Quote:
Originally Posted by TQ60 View Post
With the two 120 vac example and ac say 15 amps the neutral is carrying 30.

You were good till you got to this point. Because the A leg is 180 degrees out of phase with the B leg, if you have exactly 15 amps on both legs, you will have 0 volts on the neutral. The neutral leg is necessary here to keep the potential voltage at 120v. Neutrals burn up typically because someone has accidentally tied two A legs (or 2 B legs) on the same neutral.

BTW I did not sleep at a Inn Express but I am a licensed commercial electrical contractor.
__________________
Larry & Cheryl Oscar, Louie, Ranger & Henry (our Springers)
PushedAround is offline   Reply With Quote
Old 03-21-2014, 05:54 PM   #18
Senior Member
 
Join Date: Feb 2010
Posts: 4,654
You miss understood...

If there are two 120 vac legs on same source they are not 180 out and an issue.

Correct is to be 180 out but sub panel may not be wired that way.

I used both bad and good examples to direct the point.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 03-21-2014, 05:54 PM   #19
Senior Member
 
Join Date: Feb 2014
Location: Bamber Lake
Posts: 500
WOW!!! A man has to know his limitations, and electric is mine.
RayJr is offline   Reply With Quote
Old 03-21-2014, 05:57 PM   #20
Senior Member
 
PushedAround's Avatar
 
Tiffin Owners Club
Join Date: Sep 2012
Location: Ambler, PA
Posts: 2,853
Blog Entries: 7
Quote:
Originally Posted by TQ60 View Post
You miss understood... If there are two 120 vac legs on same source they are not 180 out and an issue. Correct is to be 180 out but sub panel may not be wired that way. I used both bad and good examples to direct the point.
Yes, you are correct here, but I guess that I did not read your initial post as meaning that. My bad.
__________________
Larry & Cheryl Oscar, Louie, Ranger & Henry (our Springers)
PushedAround is offline   Reply With Quote
Old 03-21-2014, 09:31 PM   #21
Senior Member
 
Join Date: Feb 2010
Posts: 4,654
Just checking to see if you were paying attention....you passed...
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 03-22-2014, 08:37 AM   #22
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,024
50 amps is 50 amps at 120/240 volts (50 amps at 240 volts divided).

The three flat blades are

|<-120=>|<-120->|
|<-=-=-240 Volt - -|

All the electrical stuff in your RV is 120 volt.. So why do they do it this way.

Well, let's say you are 1,000 feet from the power source (Transformer) and the voltage drop in the wires is 5 volts per thousand feet at your current power consumption level

If you were sucking 110 volt only.. You'd have 1000 feet (5 volt) from the transformer to your RV and 1000 feet (Another 5 volt) back so 120 volt becomes 110 volt

But by using 240 volt and BALANCING the loads (Example of balance Front AC on Leg 1 Rear on Leg 2 Microwave on 1 Water heater on 2

you now have 1000 feet out (five volt drop) and the neutral is carying nothing, the other thousand feet is the other leg

So the effective voltage drop is five volts instead of 10 in the first example.

Footnote: All figures in this post are examples the odds that I got the voltage drop per thousand feet exact are right next to the odds of a snowball surviving 10 minutes inside an operating blast furnace. (In short zero).
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 03-22-2014, 09:00 AM   #23
Member
 
markroblee's Avatar
 
Join Date: Mar 2014
Posts: 68
Quote:
Originally Posted by wa8yxm View Post
50 amps is 50 amps at 120/240 volts (50 amps at 240 volts divided). The three flat blades are |<-120=>|<-120->| |<-=-=-240 Volt - -| All the electrical stuff in your RV is 120 volt.. So why do they do it this way. Well, let's say you are 1,000 feet from the power source (Transformer) and the voltage drop in the wires is 5 volts per thousand feet at your current power consumption level If you were sucking 110 volt only.. You'd have 1000 feet (5 volt) from the transformer to your RV and 1000 feet (Another 5 volt) back so 120 volt becomes 110 volt But by using 240 volt and BALANCING the loads (Example of balance Front AC on Leg 1 Rear on Leg 2 Microwave on 1 Water heater on 2 you now have 1000 feet out (five volt drop) and the neutral is carying nothing, the other thousand feet is the other leg So the effective voltage drop is five volts instead of 10 in the first example. Footnote: All figures in this post are examples the odds that I got the voltage drop per thousand feet exact are right next to the odds of a snowball surviving 10 minutes inside an operating blast furnace. (In short zero).

The basics here are very very correct. If you want a major math test you can check for exact numbers but IMHO it is not needed. What it comes down to is the big new rigs have more bells and whistles than the older "standard" 30amp does not have the needed capacity to make everything work so manufacturers have had to change to keep everyone happy.

These larger loads is also why at older campgrounds you need to keep an eye on available voltage at your pedestal. Lots of AC, electric water heaters, microwaves, etc. etc. can REALLY stress these systems and cause real problems with the RV equipment.
markroblee is offline   Reply With Quote
Old 03-22-2014, 09:09 AM   #24
Senior Member
 
wb7auk's Avatar
 
National RV Owners Club
Join Date: Feb 2012
Location: Spokane Valley, Wa
Posts: 1,987
And then install the ground rods required and the voltage drop on the neutral lessens.
__________________
Art
1999 Trade Winds 7371 Cat 3126B w/current upgrades
1990 D 250 Dodge Ram Cummins Turbo
wb7auk is offline   Reply With Quote
Old 03-22-2014, 10:06 AM   #25
Senior Member
 
njs42's Avatar
 
National RV Owners Club
Workhorse Chassis Owner
Join Date: Apr 2011
Location: Federal Way, Wa.
Posts: 2,901
A thousand words

Click image for larger version

Name:	50_Amp_240V_metered.JPG
Views:	112
Size:	35.3 KB
ID:	58876
__________________
I do all my own stunts
03 Dolphin LX 6355, Workhorse W22, 8.1 vortec, 04 CR-V, Blue Ox, Brake Pro----Norm, Barb and
Doc(He's a PhD)
njs42 is offline   Reply With Quote
Old 03-22-2014, 10:13 AM   #26
Senior Member
 
FlyingDiver's Avatar
 
Newmar Owners Club
Join Date: May 2007
Location: Somewhere....
Posts: 4,054
Quote:
Originally Posted by wa8yxm View Post
All the electrical stuff in your RV is 120 volt.. So why do they do it this way.
Not in my RV it's not. Nor many other high-end rigs.
__________________
2008 King Aire 4562, Spartan K3(GT) w/ Cummins ISX 600
2014 Jeep Grand Cherokee Overland 5.7L V8 Hemi w/ Blue Ox Aventa LX Tow Bar and baseplate, SMI Air Force One brake
FlyingDiver is offline   Reply With Quote
Old 03-22-2014, 10:15 AM   #27
Senior Member
 
FlyingDiver's Avatar
 
Newmar Owners Club
Join Date: May 2007
Location: Somewhere....
Posts: 4,054
Quote:
Originally Posted by wb7auk View Post
And then install the ground rods required and the voltage drop on the neutral lessens.
Install where? Per NEC, the pedestal and panel combo in the RV are sub-panels and neutral/ground must be isolated. So how is adding a ground rod going to help with the voltage drop caused by resistance in the wires over the distance from the transformer?
__________________
2008 King Aire 4562, Spartan K3(GT) w/ Cummins ISX 600
2014 Jeep Grand Cherokee Overland 5.7L V8 Hemi w/ Blue Ox Aventa LX Tow Bar and baseplate, SMI Air Force One brake
FlyingDiver is offline   Reply With Quote
Old 03-22-2014, 10:20 AM   #28
Senior Member
 
wb7auk's Avatar
 
National RV Owners Club
Join Date: Feb 2012
Location: Spokane Valley, Wa
Posts: 1,987
Quote:
Originally Posted by FlyingDiver View Post
Install where? Per NEC, the pedestal and panel combo in the RV are sub-panels and neutral/ground must be isolated. So how is adding a ground rod going to help with the voltage drop caused by resistance in the wires over the distance from the transformer?
The neutral and earth ground at the meter as well as at the main panel.
__________________
Art
1999 Trade Winds 7371 Cat 3126B w/current upgrades
1990 D 250 Dodge Ram Cummins Turbo
wb7auk is offline   Reply With Quote
Reply

Tags
fuse



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Confused about light replacement harleychief Newmar Owner's Forum 8 01-12-2014 01:55 PM
30A or 50A to garage mothgrey Class A Motorhome Discussions 31 11-21-2013 04:14 PM
30A to 50A Adapter Causes MH Fire Pusherman Class A Motorhome Discussions 173 09-02-2013 04:33 PM
50A RV to 50A Welder dogbone Ramblin iRV2.com General Discussion 17 08-04-2013 12:05 PM
Bounder: 30A to 50A converting Sonnydale Fleetwood Owner's Forum 20 06-11-2013 09:08 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 11:03 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.