Looking at the specs on that unit, I'm curious?
Mod.59516, 15K BTU, compressor = 12.9 amps & Fan motor 2.9 amps. = 15.8 A. @115 V. Either device could be over amp. both may have run capacitors.
Although four hours is a fare amount of time to run with a defective part...
"AC circuit protection (user supplied) 20 amp ACAR circuit breaker or time delayed fuse."?
You checked your amperage, what was your voltage? Campground infrastructure (pedestals, etc.) can have loose connections. Shore power cords and connecters can overheat and cause resistance also. Voltage droop could be happening also. Low voltage = increased amperage.
Like BFlinn181 suggested, be sure the condenser coil is absolutely clean of dust and debris. The fan which is equipped to run at 3 speeds should be running at high speed in that environment and temp. The blade should be tidy also. Excessive head pressure = increased amperage.
When it is running in the night or early morning in that four hr. period the suction line back to the compressor should be cool to the touch.
Units are rated for 100+ but efficiency decreases as well as discharge air temp inside will rise.
If the compressor is bucking the breaker or the thermal overload frequently, with no apparent cause it's days could be numbered.
Sorry you're having troubles.