Old 05-30-2018, 07:32 AM   #1
Senior Member
 
jmck1737's Avatar
 
American Coach Owners Club
Spartan Chassis
Join Date: Aug 2016
Location: Virginia
Posts: 202
Dometic Fridge Cooling questions

I researched and spent hours searching and reading what I could about the issues with RV fridge cooling, especially Dometic, as that is what we have. Ours in in the slide on our 2008 Georgetown and has the upper and lower vents for cooling. I beleive the previous owner also had some problems with cooling as they had a small fan in the lower compartment which I replaced as outlined below. Below is what I have completed to date as far as upgrades to help with cooling.

I have installed 3 new computer brush less fans in bottom of the upper compartment to move air. These are rated at 74 CFM each. On the bottom I have installed an electric fan that moves significant air and is a 3 speed. I can feel air exiting the upper vent with the upper fans only on and more air with both upper and lower fans on.

I am still battling the issue of taking a long time to cool the refrigerator section and having it get to and stay at 34 -37 degrees. if we open the door the temperature will shoot up and take hours to get back down if it does. The freezer works great and will get it down to 0 degrees within 24 hours of startup.

So now to the questions and proposed solutions that I have not found definitive answers to and would like your experiences and advice on which direction we go.

Install another computer fan in the refrigerator section to move air. Was looking at 80mm fan that moves about 34cfm as this is a small area. Not an expensive solution if it doesn't help.

Snip the tip termistor upgrade. More expensive and have seen mixed reviews on line. Some say that it will not give more range than the current termistor.

Of course the ultimate solution would be to go with a residential or new cooling unit and have looked at these solutions. The Amish cooling unit is expensive and a major project and is supposed to be a better unit but still works the same as my current RV fridge. We have the smaller single door Dometic so are limited to a small size residential unit which from my research is hard to find and fit correctly.

Another question I had is can I blow too much air over the coils with my current fan setup thus overcooling the unit?

Any help from those of you who have battled this demon and won would be appreciated. I have enclose a photo of the fridge in the unit if that helps.
Attached Thumbnails
Click image for larger version

Name:	small frig pic.jpg
Views:	89
Size:	268.0 KB
ID:	204864  
__________________
2006 American Coach Eagle 42R
2017 Jeep Cherokee Trailhawk Toad
jmck1737 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-30-2018, 07:55 AM   #2
YC1
Senior Member
 
YC1's Avatar


 
Join Date: Jun 2011
Location: FL
Posts: 11,452
I just love typing out a nice long response and then it goes away.

Check your vent tube/s. If they are cracked this will cause the issue. Be sure they have not been modified or a end lug removed if designed that way.
__________________
Certified Senior Electronic Technician, Telecommunications Engineer, Telecommunications repair Service Center Owner, Original owner HR 2008

.
YC1 is offline   Reply With Quote
Old 05-30-2018, 08:14 AM   #3
Senior Member
 
NHRA225's Avatar
 
American Coach Owners Club
Join Date: Jan 2011
Posts: 2,742
If you google rv refer vent fans you'll find a variety of proposed solutions, at least I did. After all of the reading I Installed 3 x 85 cfm brushless fans in the upper exit of my roof vent. I turn them on when outside temps reach 80 degrees and upward and leave them on All of the time 24/7- Freezer is @ 0 deg and Fridge is 32 deg with my T stat set on 1/2 to 3/4 of a turn up. Now my disclaimer ! All circumstances vary- Temp inside you MH-- Sun Direction on the side of your Coach Ect.
When mine is not in use at anytime during the summer- My A/C is on keeping the inside @ 72 to 74 deg - This significantly helps the Refer keep cool.
__________________
Chuck
Brownsburg Indiana
1992 American Eagle-8.3C-450hp
NHRA225 is offline   Reply With Quote
Old 05-30-2018, 08:27 AM   #4
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 31,500
It may be time to check the clearance , between the back of the fridge ( cooling unit ) and the wall of the RV.
Too much clearance will allow air to go up between the vents , without going across the cooling unit's fins.
Some manufacturers only installed a baffle at the bottom vent , but the max clearance of 1" should be maintained , most of the way up the vent cavity.
Attached Thumbnails
Click image for larger version

Name:	refrigerator-cooling-fan-venting-diagram-1.JPG
Views:	140
Size:	18.6 KB
ID:	204869  
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 05-30-2018, 10:09 AM   #5
Senior Member
 
jmck1737's Avatar
 
American Coach Owners Club
Spartan Chassis
Join Date: Aug 2016
Location: Virginia
Posts: 202
Quote:
Originally Posted by YC1 View Post
I just love typing out a nice long response and then it goes away.

Check your vent tube/s. If they are cracked this will cause the issue. Be sure they have not been modified or a end lug removed if designed that way.
Thanks for the responses. I went back out and looked and did not see any cracks. No large amount of yellow powder either. Just turned it to Gas only to see if that would help. Electric got it down to 49 degrees running over night with temps in the low 70's but high humidity. AC on in the coach around 76 degrees.
__________________
2006 American Coach Eagle 42R
2017 Jeep Cherokee Trailhawk Toad
jmck1737 is offline   Reply With Quote
Old 05-31-2018, 08:18 AM   #6
YC1
Senior Member
 
YC1's Avatar


 
Join Date: Jun 2011
Location: FL
Posts: 11,452
Pull the top vent out of the side and look down to perhaps find a couple of fans installed there. Use your phone to take pictures or a mirror.

If you find a fan or two and they are not running you need to chase the wires to the device that turns them on and off. It might have tabs on it and could be clamped to the cooling unit some place. Finding that device check to see if it has 12 volts on each side. If not, just jump across it and the fans should run if not defective.

If the fans are defective you can get to them by pulling the refer out several inches versus pulling it all the way out. That can be a trick finding hidden screws covered in dust in the back.

If you find the fans are bad be sure to install new vent tubing at the same time. The stuff they install becomes very brittle.
__________________
Certified Senior Electronic Technician, Telecommunications Engineer, Telecommunications repair Service Center Owner, Original owner HR 2008

.
YC1 is offline   Reply With Quote
Old 05-31-2018, 12:44 PM   #7
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,848
OP Stated:
I am still battling the issue of taking a long time to cool the refrigerator section and having it get to and stay at 34 -37 degrees. if we open the door the temperature will shoot up and take hours to get back down if it does.

The freezer works great and will get it down to 0 degrees within 24 hours of startup.



Classic example of obstruction/blockage in cooling unit between LOW temp evap (freezer) and HIGH temp evap (food compartment)
Hot ammonia vapor is being condensed into cool Liquid ammonia in Condenser section (finned section at top of fridge).
That requires sufficient airflow/draft....which you have


The condensed liquid ammonia gets very cold when it mixes with the hydrogen gas.......it then absorbs heat from freezer via the LOW temp evap.

Then is has to absorb heat from food compartment (HIGH temp evap)
Until freezer section gets down to 10*F or lower the cold liquid ammonia can not absorb much heat from food compartment due to all the heat it had to absorb from freezer.
Your freezer is getting very cold (good) but food compartment temps take long time to cool down/recover .....


To test if 'cooling unit' is problem or if thermistor is you need to force cool the fridge
Unplug the thermistor leads from P2 connector on lower circuit board
Run fridge on electric for at least 12 hrs. W/O thermistor the fridge will 'cool' continuously (not turn electric elements off)
Temp in food compartment should get very cold ---possibly even freeze items


If it does.......replace thermistor (Snip-The-Tip is a convenient way but not a clue all)


If it doesn't then cooling unit has blockage which will only gets worst over time
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 05-31-2018, 02:08 PM   #8
Senior Member
 
jmck1737's Avatar
 
American Coach Owners Club
Spartan Chassis
Join Date: Aug 2016
Location: Virginia
Posts: 202
Quote:
Originally Posted by Old-Biscuit View Post
OP Stated:
I am still battling the issue of taking a long time to cool the refrigerator section and having it get to and stay at 34 -37 degrees. if we open the door the temperature will shoot up and take hours to get back down if it does.

The freezer works great and will get it down to 0 degrees within 24 hours of startup.



Classic example of obstruction/blockage in cooling unit between LOW temp evap (freezer) and HIGH temp evap (food compartment)
Hot ammonia vapor is being condensed into cool Liquid ammonia in Condenser section (finned section at top of fridge).
That requires sufficient airflow/draft....which you have


The condensed liquid ammonia gets very cold when it mixes with the hydrogen gas.......it then absorbs heat from freezer via the LOW temp evap.

Then is has to absorb heat from food compartment (HIGH temp evap)
Until freezer section gets down to 10*F or lower the cold liquid ammonia can not absorb much heat from food compartment due to all the heat it had to absorb from freezer.
Your freezer is getting very cold (good) but food compartment temps take long time to cool down/recover .....


To test if 'cooling unit' is problem or if thermistor is you need to force cool the fridge
Unplug the thermistor leads from P2 connector on lower circuit board
Run fridge on electric for at least 12 hrs. W/O thermistor the fridge will 'cool' continuously (not turn electric elements off)
Temp in food compartment should get very cold ---possibly even freeze items


If it does.......replace thermistor (Snip-The-Tip is a convenient way but not a clue all)


If it doesn't then cooling unit has blockage which will only gets worst over time
Old Biscuit,

That is excellent info and I appreciate it. I definitely learned something. I will do that and test the thermistor. I had no idea how to test the unit other than what I have already done with voltage, fire, etc.

If it passes I would assume the blockage issue means new cooling unit or would the burp test (taking unit out and rolling it upside down and back a few times) I have seen on the web a possibility? I ran over night last night and only got down to around 43 degrees. We have a camping trip planned for this weekend so I may use that as a test.
__________________
2006 American Coach Eagle 42R
2017 Jeep Cherokee Trailhawk Toad
jmck1737 is offline   Reply With Quote
Old 05-31-2018, 02:12 PM   #9
Senior Member
 
jmck1737's Avatar
 
American Coach Owners Club
Spartan Chassis
Join Date: Aug 2016
Location: Virginia
Posts: 202
Quote:
Originally Posted by YC1 View Post
Pull the top vent out of the side and look down to perhaps find a couple of fans installed there. Use your phone to take pictures or a mirror.

If you find the fans are bad be sure to install new vent tubing at the same time. The stuff they install becomes very brittle.
YC1

Thanks for the replay and info. I have already changed the 2 DC fans I had in the top to 2 DC fans that moved almost twice the air as the old ones. I also have a fan in the bottom blowing up onto the coils.

I think Old Biscuit may have provided my next logical step. I am learning a lot about evaporative refrigeration whether I wanted to or not.
__________________
2006 American Coach Eagle 42R
2017 Jeep Cherokee Trailhawk Toad
jmck1737 is offline   Reply With Quote
Old 05-31-2018, 03:06 PM   #10
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,848
Quote:
Originally Posted by jmck1737 View Post
Old Biscuit,

That is excellent info and I appreciate it. I definitely learned something. I will do that and test the thermistor. I had no idea how to test the unit other than what I have already done with voltage, fire, etc.

If it passes I would assume the blockage issue means new cooling unit or would the burp test (taking unit out and rolling it upside down and back a few times) I have seen on the web a possibility? I ran over night last night and only got down to around 43 degrees. We have a camping trip planned for this weekend so I may use that as a test.





Burping/flip-flopping fridge is a band-aid attempt at best


The sodium chromate in the cooling solution (anti-rust inhibitor) crystallizes from being overheated.......lack of coolant flow/off level operation, inadequate airflow/draft etc.
The crystals plate out on inside of tubing 9section between the two evap coolers) or in perk tube (boiler section)
The plating out is permanent....crystals will not go back into solution.

Burping/flipping etc might dislodge some of the crystals but they will just cause an obstruction elsewhere.


Force cool and determine if cooling unit or thermistor.
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 05-31-2018, 03:30 PM   #11
Senior Member
 
jmck1737's Avatar
 
American Coach Owners Club
Spartan Chassis
Join Date: Aug 2016
Location: Virginia
Posts: 202
Ok. couldn't wait to try Old Biscuits thermisor test. So out to the MH, shut down AC and DC power, unhook the P2 connector, power back on, and frig running on AC power. We shall see in the morning if this works and my fingers are crossed as the snip a tip is a much easier and less expensive fix.
__________________
2006 American Coach Eagle 42R
2017 Jeep Cherokee Trailhawk Toad
jmck1737 is offline   Reply With Quote
Old 05-31-2018, 03:32 PM   #12
Senior Member
 
jmck1737's Avatar
 
American Coach Owners Club
Spartan Chassis
Join Date: Aug 2016
Location: Virginia
Posts: 202
Quote:
Originally Posted by Old-Biscuit View Post
Burping/flip-flopping fridge is a band-aid attempt at best
Burping/flipping etc might dislodge some of the crystals but they will just cause an obstruction elsewhere.

Force cool and determine if cooling unit or thermistor.
Thanks for the helpful info. Doing the thermistor test now so should know something tomorrow morning. will post results.
__________________
2006 American Coach Eagle 42R
2017 Jeep Cherokee Trailhawk Toad
jmck1737 is offline   Reply With Quote
Old 05-31-2018, 04:08 PM   #13
Senior Member
 
Forest River Owners Club
Ford Super Duty Owner
Join Date: Dec 2014
Posts: 1,024
Dometic Fridge Cooling questions

Dealer told me the best these do is 38*F or so. Today was a cool day. This morning it was 34*. Now 37* - opened it a few times to prepare dinner.
AbdRahim is offline   Reply With Quote
Old 06-01-2018, 04:14 AM   #14
Senior Member
 
jmck1737's Avatar
 
American Coach Owners Club
Spartan Chassis
Join Date: Aug 2016
Location: Virginia
Posts: 202
I guess I did not get lucky with the problem being the easier to repair thermistor. Went out to check and it was 50 degrees in fridge and 13 in freezer after running 12 hours with thermistor disconnected. Guess I order a cooling unit today. I could live with 34-38 degrees but not 40's and 50.
__________________
2006 American Coach Eagle 42R
2017 Jeep Cherokee Trailhawk Toad
jmck1737 is offline   Reply With Quote
Reply

Tags
cooling, dometic, fridge



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dometic Fridge not cooling on gas aaronpapemh RV Systems & Appliances 15 05-04-2021 09:03 AM
OLD Dometic fridge over cooling.. urbex RV Systems & Appliances 2 10-07-2016 05:19 PM
Dometic RM 1350 Fridge cooling question racer26 MH-General Discussions & Problems 5 03-01-2016 01:27 AM
Dometic RM1350 Fridge Cooling Problem BarbandBob RV Systems & Appliances 2 01-13-2015 01:43 PM
1984 pace arrow dometic fridge not cooling aaron81182 Fleetwood Owner's Forum 8 04-30-2013 05:35 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 01:38 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.