Dryer receptacle adapter
Old 12-24-2011, 09:21 AM   #1
M2HB is offline
Member
M2HB's Avatar
Join Date: Oct 2011
Posts: 56
I have a spare NEMA 10-30 receptacle in our new house. As I understand it this is two 30 amp 120 volt lines combined into one 240 volt circuit. Is this correct? Is it safe or feasible to fabricate an adapter to split this into two 120 volt circuits and connect to the two 120 volt legs of an RV 50 amp circuit? I am having an electrician install the proper 50 amp outlet at the new house next week so I will not actually be using such an adapter but I wonder if it would be useful if I found myself in a situation where I needed more power than a normal household 15 or 20 amp plug could provide.

__________________
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-24-2011, 09:32 AM   #2
mahon1993 is offline
Senior Member
mahon1993's Avatar
Join Date: Mar 2010
Location: Fowlerville, Mich.
Posts: 368
Do not plug anything with any kind of adaptor into that outlet unless you are sure of what you got. Chances are it is a 240 volt dryer / welder outlet. Plugging a RV into it means instant expensive smoke. Have an electrican install the proper 50 amp rv plug for you.
Greg

__________________
2000 Monaco Diplomat 40PBD
2002 Grand Chrokee Overland
2006 FXD35 & Three spoiled Great Danes
  Reply With Quote
   
Old 12-24-2011, 11:24 AM   #3
wa8yxm is offline
Senior Member


Workhorse Chassis Owner
Damon Owners Club
Join Date: Mar 2009
Posts: 8,078
IS it feasible: Non sufficient data.. (I will explain)

Is it reasonable and proper: NO. in most cases.

Do I recommend it: NO.

Do I know how to do it.. Well, if it is possible (And I'm not saying it is)

Danger: There is still a company, present in every city or township or county, that makes house calls.. it's called Company __ of the Fire Department. And the danger is they may come a calling if you make an adapter.. Which is why I'm not going to tell you how to do it.

The problem: To run a proper 30 amp circuit you need fairly heavy wire, like 6 or 8 ga for any length of run, minimum 10ga for short runs. The problem is that the cable to that outlet is 3 wire.. (As you can deduce from the fact there are 3 slots in the outlet) now the two HOT leads, will be the right size, but the 3rd wire (Neutral) may be considerably smaller, since it is designed to carry current for only a brief period (Just long enough to make the breaker go CLICK)

Or to carry far less current.

If you plug in an RV with an adapter. You can easily overload this neutral wire unless your loads are properly balanced.

Second.. You will only be able to connect 3 wires, This leaves the safety ground floating, Normally one would think this is not a problem.. HOWEVER I can all but guarantee you will end up with the chassis at considerable voltage above ground unless you address this.

THUS.. I do not recommend trying it.

IF you pull a proper 4-wire cable, you could use a 50 amp RV outlet and without changing the breakers slap a label (Brother P-Touch is great for this) "30 amp limit"

That... Would be safe, IT would be better, You would run no danger of a neutral overload, and the safety ground would be there... The only danger is Eva Gabor syndrom (Turning 40 amps of stuff on a 30 amp leg and getting the CLICK of darkness,,, From the TV show Green Acres)
__________________
Home is where I park it!
  Reply With Quote
   
Old 12-24-2011, 11:44 AM   #4
bluepill is offline
Senior Member
bluepill's Avatar


Join Date: Jan 2011
Location: NY & FL
Posts: 841
Lack of a proper and sufficient ground with the NEMA 10 30 configuration is the killer. Pun Intended.
__________________
2008 Itasca Meridian 37H
2011 & 2012 Len & Pat's "One lap of America"
14K miles so far - Woo Woo!
  Reply With Quote
   
Old 12-24-2011, 02:11 PM   #5
GaryKD is offline
Senior Member
GaryKD's Avatar


Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 6,933
Hi M2HB,
The technical explanation is already posted. For me, I wouldn't touch this. If you want an outlet for the coach, do it correctly from the beginning. None of the parts are expensive.
__________________
Gary
2005 Newmar KSDP 3910,
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
  Reply With Quote
   
Old 12-27-2011, 08:23 AM   #6
GWinger is offline
Member
Join Date: Dec 2011
Posts: 54
Quote:
Originally Posted by wa8yxm View Post
IS it feasible: Non sufficient data.. (I will explain)

Is it reasonable and proper: NO. in most cases.

Do I recommend it: NO.

Do I know how to do it.. Well, if it is possible (And I'm not saying it is)

Danger: There is still a company, present in every city or township or county, that makes house calls.. it's called Company __ of the Fire Department. And the danger is they may come a calling if you make an adapter.. Which is why I'm not going to tell you how to do it.

The problem: To run a proper 30 amp circuit you need fairly heavy wire, like 6 or 8 ga for any length of run, minimum 10ga for short runs. The problem is that the cable to that outlet is 3 wire.. (As you can deduce from the fact there are 3 slots in the outlet) now the two HOT leads, will be the right size, but the 3rd wire (Neutral) may be considerably smaller, since it is designed to carry current for only a brief period (Just long enough to make the breaker go CLICK)

Or to carry far less current.

If you plug in an RV with an adapter. You can easily overload this neutral wire unless your loads are properly balanced.

Second.. You will only be able to connect 3 wires, This leaves the safety ground floating, Normally one would think this is not a problem.. HOWEVER I can all but guarantee you will end up with the chassis at considerable voltage above ground unless you address this.

THUS.. I do not recommend trying it.

IF you pull a proper 4-wire cable, you could use a 50 amp RV outlet and without changing the breakers slap a label (Brother P-Touch is great for this) "30 amp limit"

That... Would be safe, IT would be better, You would run no danger of a neutral overload, and the safety ground would be there... The only danger is Eva Gabor syndrom (Turning 40 amps of stuff on a 30 amp leg and getting the CLICK of darkness,,, From the TV show Green Acres)
wa8xym,
Not to dispute anything you said, but to clarify, your paragraph beginning with, "The Problem,..."
The NEC says 10 gauge copper wiring is SAFE for a 30 amp circuit. The only reason to increase it to 6 or 8 would be for a very long run. It helps to prevent voltage drop along the longer runs. As far as the neutral being smaller (#10) that isn't a problem a when the voltage between the other two legs is 240vac, the neutral carries only the 'unbalance' current.
Meaning if your pulling say 12 amps on one leg and 10amps on the other, the neutral is carrying only 2amps. On a circuit protected with a 30amp circuit breaker, the current on the neutral is never more than 30 amps, and most often, less. The danger in tapping off a three-wire circuit is that while you have a neutral, you have no Ground. The neutral normally carries current. The Ground is designed to carry only Fault current, which normally would occur when something shorts out.

The power for a 50amp circuit to an RV should NEVER originate from the same 120volt power phase. Which can happen when someone who doesn't understand electricity trys to adapt a circuit to an RV from a dryer or range home outlet.
GWinger
__________________
  Reply With Quote
   
Old 12-27-2011, 09:49 AM   #7
Tallyrver is offline
Senior Member
Tallyrver's Avatar
Winnebago Owners Club
Join Date: Mar 2010
Posts: 608
I had a 50 amp installed at my driveway , a friend was going to do it .He thought it was the same plug as a drier...I did a little research. There could have been a visit from the big red truck if he had done it the way he wanted. I did the labor and had another electrician check it for me.

This link has some great information ,for you and the person that is doing the work .

Wayne

RV Electric
__________________
Wayne and Debbie
2011 Winnebago Journey 40U
Tallahassee ,Florida
  Reply With Quote
   
Old 12-27-2011, 10:50 AM   #8
wa8yxm is offline
Senior Member


Workhorse Chassis Owner
Damon Owners Club
Join Date: Mar 2009
Posts: 8,078
I fully agree Winger.. I like to use oversize wire, (Safer, lower voltage drop, etc) in case you wonder.

I did say without a ground I can virtually guarantee a hot chassis (Voltage present) didn't I.. Thought I did.

In short don't do it.
__________________
Home is where I park it!
  Reply With Quote
   
Old 12-27-2011, 11:30 AM   #9
vermilye is offline
Senior Member
vermilye's Avatar


Join Date: Nov 2006
Location: Oswego, NY
Posts: 188
Send a message via Skype™ to vermilye
Although the neutral does carry the difference between the hots, in the case of RVs & some other types of loads, there is a good possibility that the load will not be balanced. Because of this it is important (and required by NEC) that the neutral be full sized.

I agree that even if there was a full sized neutral, because a 3 pole dryer receptacle combines the ground & neutral, there is no way it can be safely used to power a RV. At a minimum, you will be putting the neutral voltage on the frame of the RV. At the worst, you will annoy plumbers working on copper piping in the house & set up a condition that might result in a shock from a stream of water.

  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Haldex Air Dryer Rebuild quikduk Spartan Motorhome Chassis Forum 6 09-03-2011 04:14 AM
Receptacle Tester RJEV RV Systems & Appliances 2 04-10-2011 04:26 PM
Help with finding WiFi antenna & Adapter RustyTools Technology: Internet, TV, Satellite, Cell Phones, etc. 23 12-24-2010 11:06 AM
GFI Receptacle - Ice Maker liralen Monaco Owner's Forum 7 08-12-2010 03:50 PM
Ouch - Air Dryer Rebuild teofff Monaco Owner's Forum 12 04-20-2010 06:06 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 05:27 AM.