Electrical...the more I try to understand it, the more confused I become

I have what appears to be a 30 amp electrical outlet on the side of my home that I want to use to keep my RV charged up.

Looking at my home's breaker box, every 30 amp breaker I have is 2 pole. When I put a meter on the outlet's black and ground, I get a reading of 125v. Black and white also reads 125v. White and ground reads zero.

I was told by an electrician I know that the above readings indicate a single pole breaker. Then I go to this page RV Electric under the link to "outlet testing". According to this, my readings indicate 2 pole, and is considered "RV friendly".

RV 30 amp service is supposed to be single pole, no?

Someone or something I'm reading is incorrect. What can y'all add to this state of confusion I appear to be in?
__________________

__________________
2005 Newmar KSDP 3910
ISC on a Spartan
USMCRET is online now   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-03-2011, 06:00 PM   #2
Administrator in Memoriam
 
Route 66's Avatar


 
Newmar Owners Club
Retired Fire Service RVer's
Spartan Chassis
Join Date: May 2000
Location: Newark, DE
Posts: 25,909
30A service is 120v with a single pole breaker as there is only one hot line.

A 2 pole breaker is used for 240v service.

Do both terminals of the 30A two pole breaker have wires connected to them?

You need to verify what is actually wired.
__________________

__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, previously 4 years as a fulltimer in a '07 DSDP

Route 66 is offline   Reply With Quote
Old 11-03-2011, 06:07 PM   #3
Senior Member
 
jackrobinryan's Avatar
 
Workhorse Chassis Owner
Join Date: Oct 2006
Location: wherever
Posts: 432
Good to ask before proceeding.....if you go to the section on 30A service, you'll see it specifies a single 30A breaker. And the explanation for how both ends of the connection are wired, if you plan on checking. I would.

Note: If you do not feel completely comfortable opening up and working in a hot breaker panel. Don't. Find someone who does.

Find the breaker assocaiated with the this outlet and mark it. I'd keep it switched Off when not in use since it is outside.

I usually check anything I personally have not installed for correct wiring and tightness of terminations. Loose connections can heat up and cause problems.

be safe
jack
__________________
2007 Adventurer 38T w/
sway & trac bars, Koni FSDs and SafeT+
2006 Jeep Liberty toad
jackrobinryan is offline   Reply With Quote
Old 11-03-2011, 06:14 PM   #4
Senior Member
 
Join Date: Aug 2000
Location: Walnut Creek Ca USA
Posts: 662
There is 30 amp 220 outlet, and there is 30 amp 110 outlet they are not the same configuration. A dryer outlet is a 30 amp 220. An RV uses a 30 amp 110. That means a hot lead going to one phase of your house hold 2 phase power and a single breaker. In 30 amp 110 volt rv recepticle there is 1 hot lead typically black, one neutral should be white, and one ground either green or a bare. All is the same on 220 except you also have a red wire oposite phaze from the black and a 2 pole breaker.
Check the wire size at the outlet. Is it 10 gauge wire or 6 gauge wire and how many conductiors do you have? You may have to trace out the wires to find out what's happening. I've seen some really goofy electrical stuff in my years as a custom home builder.
Paul R. Haller
Paul R. Haller is offline   Reply With Quote
Old 11-03-2011, 06:55 PM   #5
Senior Member
 
FlyingDiver's Avatar
 
Newmar Owners Club
Join Date: May 2007
Location: Somewhere....
Posts: 3,934
I think the wording on that website is confusing. He's referring to 30 amp (one hot lead) as 2-pole, and he refers to 50 amp (two hot leads) as three pole.

So, normally, a 30 amp RV wired socket would only have one single pole breaker. If you don't have any single pole 30 amp breakers, it's possible that used to be a 240v AC outlet and the wiring has been changed (but not the breaker). Start turning off breakers until you figure out which one is feeding that outlet, then see if you can figure out where the other half of the breaker is going to. You might even want to open up the outlet box (with the breaker off) and see if there's an extra wire in there not going to anything. Or take the cover off the breaker box and see if that extra wire is going to the neutral bar.

joe
__________________
2008 King Aire 4562, Spartan K3(GT) w/ Cummins ISX 600
2014 Jeep Grand Cherokee Overland 5.7L V8 Hemi w/ Blue Ox Aventa LX Tow Bar and baseplate, SMI Air Force One brake
FlyingDiver is online now   Reply With Quote
Old 11-03-2011, 07:14 PM   #6
Moderator Emeritus
 
TXiceman's Avatar


 
Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Full Time, TX Home Base
Posts: 17,183
Blog Entries: 21
If it is a 2 pole breaker, it is 240 volts. You will read, 120 v on either side to the ground, but hot to hot is 240 v.

Ken
__________________
Amateur Radio Operator (KE5DFR)|Full-Time! - 2012 6.7L Ford Crew Cab Dually -2013 HitchHiker Champagne 38RLRSB - Travel with one Standard Schnauzer and one small Timneh African Gray Parrot
TXiceman is offline   Reply With Quote
Old 11-03-2011, 07:39 PM   #7
Senior Member
 
Ramblin's Avatar
 
National RV Owners Club
Workhorse Chassis Owner
Ford Super Duty Owner
Carolina Campers
Join Date: Aug 2011
Posts: 2,253
Your readings indicate a single pole circuit. It may be wired to a 15 or 20 amp breaker. As the other folks have said, I'd first figure out which breaker it's on, and turn it off. Then you can find out if there is anything else on the circuit, and you can open up the outlet and see what size wire was used. If the wire size is sufficient, and its the only outlet on the circuit, you can check the connections, and replace the 15A or 20A with a single phase 30A one for your RV.
Ramblin is offline   Reply With Quote
Old 11-03-2011, 07:52 PM   #8
Senior Member
 
wa8yxm's Avatar
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,022
Something you are reading is indeed incorrect... however The voltage readings you are seeing do indicate "RV SAFE"

Recommendation.. Open the main breaker box inside the RV, turn off ALL breakers, epically the mains.

now plug in to that outlet.. Measure the voltage between the Main breaker's screw (IT WILL BE HOT) and the white wire bus. Should be in the 120-125 range plus or minus a bit
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 11-03-2011, 08:37 PM   #9
Senior Member
 
Dave78Chief's Avatar
 
Join Date: Jun 2009
Posts: 1,525
You are trying to convert a older (pre-1996) appliance outlet to RV operation.
Read the Appliance Service section of his site which addresses part of this confusion. He actually is using the corrrect context and you will see this in other documentation also.
Nema Plug and Receptacle configurations
NEMA Plug & Receptacle Configurations Reference Chart (Straight Blade)
It's the reference point that is creating the confusion. "2 Pole" in the NEMA context relates to North-South (Hot & Nuetral) pole windings at the generating source.

From his Appliance section:

Converting the OLD APPLIANCE (10-30 or 10-50) service to a 30-amp 120-volt 2 pole 3 wire RV service is simple. Remove the Double pole breaker and replace it with a Single pole 30-amp breaker. This service requires 3 wires 1 Black (Hot lead) 1 White (Neutral) and 1 Ground. One of the hot wires will have to be made into a Ground wire. Remove the insulation or use green tape to identify it for future reference. Install a TT-30R receptacle and its ready to go.

Dave
__________________
Dave in Virginia
1978 Winnebago Chieftain
Dodge M400 - 440-3
Classic Winnebago Site: http://www.classicwinnebagos.com/forum/index.php
Dave78Chief is offline   Reply With Quote
Old 11-04-2011, 04:45 AM   #10
1977-2006
 
USMCRET's Avatar


 
Newmar Owners Club
Join Date: Jul 2011
Posts: 1,607
Super info in these replies. Thanks so much! We are headed out for the weekend, but I will get back on this next week.
__________________

__________________
2005 Newmar KSDP 3910
ISC on a Spartan
USMCRET is online now   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30 amp to 50 amp Electrical Upgrade mikwallace Winnebago Industries Owner's Forum 17 11-30-2009 11:17 AM
Installation of a New Open Grill Partition in the Electrical Compartment SteveG Winnebago Industries Owner's Forum 0 10-14-2009 07:46 PM
Provide Cooling Air to 2004 Journey 36G Electrical Compartment SteveG Winnebago Industries Owner's Forum 15 12-23-2008 02:04 PM
I fixed my DC Electrical Panel/Block in a 1979 Dodge Motorhome niki123 RV Systems & Appliances 5 05-28-2006 06:31 PM