EMS not Sheding Load?

We're at a site with 50 amp service. It's very hot and all 3 ACs are cranking. We have electric water heater, a clothes dryer and my wife is drying her hair. I start to notice it's getting warm in the coach, the ACs have shut down. I go up and look at the EMS panel and see there is no power service. I go outside and the breaker has tripped. I reset the breaker and turn the dryer off, the hot water off and she starts with the hair dryer again. All 3 ACs are on and the outside breaker pops again.

So now I have a few hours to my self (the wife and daughter are out shopping) so I start mapping what appliances go to what leg of my EMS. I then start turning things on looking to see when the system starts to shed loads (I've previously seen the system work, so I know it worked at one time). I put all 3 ACs on, turn the dryer on and check the EMS. I'm at 42 Amps total between both legs. I then put the hairdryer on full power (EMS says its drawing 14 amps) and the total draw goes to 54 Amps, 4 amps beyond where I would think it should start shedding something. I let it run for a few minutes and then decide to shut the overloads down and think about what to check next.

Any ideas? I have a Precision Circuits EMS in my 2015 Discovery 40G. Not sure exactly which model it is, it looks like this Power Control System Central Monitor Panel Remote Display | Precision Circuits Inc.
__________________
2023 Winnebago Travato
2023 Airstream Flying Cloud BH 30'
jondrew55 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-29-2016, 02:05 PM   #2
Community Administrator
 
CLIFFTALL's Avatar


 
Join Date: Aug 2009
Posts: 53,560
Blog Entries: 1
EMS not Sheding Load?

My EMS didn't show amps while on 50 amp hookup. You may have lost a leg at the pole which may cause this and therefore you're not getting the 50 on each side. My Bounder had a different EMS , so my thoughts here may not be applicable however they may be .
__________________


Cliff,Tallulah and Buddy ( 1999-2012 )
CLIFFTALL is offline   Reply With Quote
Old 05-29-2016, 02:20 PM   #3
YC1
Senior Member
 
YC1's Avatar


 
Join Date: Jun 2011
Location: FL
Posts: 11,452
My EMS panel does not shed while on 50 amps. As suggested you may have lost one leg of the 50 amp at the post.
__________________
Certified Senior Electronic Technician, Telecommunications Engineer, Telecommunications repair Service Center Owner, Original owner HR 2008

.
YC1 is online now   Reply With Quote
Old 05-29-2016, 02:41 PM   #4
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
A 50 amp RV Shore Power supply is really 100 amps total.

120 VAC (Leg#1) x 50 amps = 6000 watts

120 VAC (Leg #2) x 50 amps = 6000 watts.

100 amps x 120 VAC = 12,000 watts

That's a total of 12,000 watts of power to be used for the entire coach.

Sounds like you have a coach with 3 rooftop A/C's if your coach is like others you most likely have an Intellitec relay that will choose either the third A/C or the washer/dryer as you don't have enough power to run everything all at the same time on that same Leg.

Dr4Film ----- Richard
Dr4Film is offline   Reply With Quote
Reply

Tags
ems



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Intellitec EMS 800 Load Management Issue dmastroluca Monaco Owner's Forum 23 11-20-2015 11:15 AM
Load shedding EMS Hooky Entegra Owner's Forum 12 06-26-2014 07:47 PM
Load range F vs. Load range G Txcirclem Class A Motorhome Discussions 18 06-17-2013 04:03 AM
Load Range D vs Load Range E royjeri 5th Wheel Discussion 29 07-29-2011 04:30 AM
EMS-PT30C vs. EMS-PT50C surge/voltage protector Peacekeeper6 Class A Motorhome Discussions 9 04-14-2011 09:18 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 07:08 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.