05-29-2014, 05:25 PM
|
#1
|
Senior Member
Fleetwood Owners Club Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
|
Generator was running fine, stopped, will not start...
Generator running fine for about three hours. Then just quit. When trying to restart, it turns over, appears to try to start, then quits. Blinking code 32 (not cranking fast enough...).
On an 5500 Gold, 789 hours.
Oil level is full.
Gas tank is 3/4 full.
Battery connections are tight (code 32 suggestion), and cranking speed appears good and it tries to start...
Oil, oil and air filters maybe 6 months and a few dozen hours ago. Don't know if fuel filter has ever been changed.
Suggestion?
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
05-29-2014, 05:56 PM
|
#2
|
Senior Member
Join Date: Oct 2011
Posts: 1,136
|
Check the ground at the gen also. Onan is notorious for loose ground due to vibration
|
|
|
05-29-2014, 08:22 PM
|
#3
|
Senior Member
Outdoors RV Owners Club
Join Date: Oct 2009
Location: Manitoba,Canada
Posts: 2,789
|
Same thing happened to our 6.5kw Onan generator. Turned out the engine control board had failed.
Got a new one from:
A.S.A.P.
Then it started and ran again.
Jim
__________________
2016 Creekside 23RKS
2012 Ram 2500 Laramie 4X4 Cummins 6.7L
Canada, eh?
|
|
|
05-29-2014, 08:53 PM
|
#4
|
Senior Member
Fleetwood Owners Club Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
|
Quote:
Originally Posted by trackman
Check the ground at the gen also. Onan is notorious for loose ground due to vibration
|
Checked grounds. Removed, buffed, and replaced. No joy.
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
|
|
|
05-29-2014, 08:57 PM
|
#5
|
Senior Member
Fleetwood Owners Club Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
|
Quote:
Originally Posted by Papa_Jim
Same thing happened to our 6.5kw Onan generator. Turned out the engine control board had failed.
Got a new one from:
A.S.A.P.
Then it started and ran again.
Jim
|
Reading and thinking the same. The generator actually does start, runs for a couple seconds, stops.
Pulled the cover off the box with the start switch and circuit breakers, thinking the control board was there, but it's not. Can't find it or a picture online showing where it's located...
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
|
|
|
05-30-2014, 05:01 AM
|
#6
|
Senior Member
Join Date: Nov 2009
Posts: 2,043
|
Post your exact model number. It is highly doubtful the control board is the problem on a 32 error. Speed sense faults can be tricky and can be a result of many different things. If yours is an HG series, in most cases a 32 error is either a drive belt failure or the drive belt tensioner which has become oxidized/corroded and can no longer maintain tension on the drive belt. I can guide you to inspecting the drive assembly, brush assembly/slip rings and windings, all of which can be done, depending upon model, without removing the genset from the coach. Repairing any of the above with exception of the brushes/slip rings would require removal of the genset to repair.
__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
|
|
|
05-30-2014, 07:34 AM
|
#7
|
Senior Member
Damon Owners Club Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,024
|
Same thing happened to my next site neighbor in 2007 in Quartsite,,, Generator needed to be refurbished (Brushes bad) in their case.. ONAN generators are like Yogi, smarter than the average bear.. They have the ability to check for output, and if the generator is not working, why waste gas running the engine? So they shut off, and flash 32. (They assume the reason for no output is not running fast enough) alas, they are not all that smart.
Bottom line: There are many conditions that can flash a 32
Thankfully for the folks beside me... They were parked next to the only 30 amp outlets in that part of the desert.. ... Yup.. I have 30 amp daisy chain outlets on my rig. Part of my house upgade from back in the S&B days. (I put in 3 30 amp outlets, (one 4 wire, two TT-30)
__________________
Home is where I park it!
|
|
|
05-30-2014, 11:22 AM
|
#8
|
Senior Member
Winnebago Owners Club
Join Date: Aug 2013
Posts: 1,636
|
Starts, runs a couple of seconds then dies, I'd change the fuel filter, sounds like fuel starvation. Fuel filters probable the cheapest and easiest try 1st.
__________________
2012 Journey 40U (Our Incredible Journey)
2008 Dodge Dakota(TOAD) 2005 Honda Shadow in TOAD
AF-1 braking system
|
|
|
07-05-2014, 07:43 PM
|
#9
|
Senior Member
Fleetwood Owners Club Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
|
Finally getting around to revisiting this. Pulled the fuel line loose at the engine. When pushing switch to prime has a strong flow. Removed the 2nd of two filters at the engine (other is down below next to the fuel pump) and put on the loose end of the fuel line. Still a strong flow. When pushing the switch to start, the flow is good for a few seconds, then stops - appears the logic is telling it to shut off.
Methinks next is to go to a shop for service. Thoughts on going to a RV repair shop vs. Onan service center?
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
|
|
|
07-06-2014, 06:34 AM
|
#10
|
Senior Member
Texas Boomers Club
Join Date: Dec 2003
Location: Mo/Texas
Posts: 3,555
|
Quote:
Originally Posted by vsheetz
Finally getting around to revisiting this. Pulled the fuel line loose at the engine. When pushing switch to prime has a strong flow. Removed the 2nd of two filters at the engine (other is down below next to the fuel pump) and put on the loose end of the fuel line. Still a strong flow. When pushing the switch to start, the flow is good for a few seconds, then stops - appears the logic is telling it to shut off.
Methinks next is to go to a shop for service. Thoughts on going to a RV repair shop vs. Onan service center?
|
Onan service center for genie. Hrly cost should be close and that's what there for.
|
|
|
07-06-2014, 06:39 AM
|
#11
|
Senior Member
Join Date: Nov 2009
Posts: 2,043
|
In post #6 above I had asked for your model number... :-)
You mention when pushing START the flow from the fuel pump is good for a few seconds then stops.. but is the engine cranking? There is no logic built-in on any model that will stop the fuel pump while you're still cranking.. your model # is a must to help any further :-)
__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
|
|
|
07-06-2014, 10:29 AM
|
#12
|
Senior Member
Fleetwood Owners Club Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
|
Yes, The cranking and the fuel flow stop at the same time.
Model number below
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
|
|
|
07-06-2014, 10:59 AM
|
#13
|
Member
Join Date: May 2013
Posts: 74
|
I took mine to cummings/onan Rocky Mountain in Salt Lake City. They have centers all over the west. They have techs that work on generators all day every day and they usually have parts in stock. Their not cheap but they know what their doing.
|
|
|
07-06-2014, 12:04 PM
|
#14
|
Senior Member
Join Date: Nov 2009
Posts: 2,043
|
Ok, HGJAB ... look at the bell end of the generator housing- you should be able to see part of the rotor. While you're cranking is the center section of the generator turning exactly in speed/rotation with the engine while cranking? Pay careful attention that it does not move at all after the engine stops cranking. This model is notorious for either a broken or slipped drive belt and/or belt tensioner that galls up and allows the belt to slip. A 32 error on these units are either a faulty drive system as mentioned above OR brushes/slip ring issues.
__________________
94-Newmar Kountry Star 40-KSDP
Spartan/Cummins 8.3C-300HP/Allison 3060 WTEC-II/25yr RV Tech RVIA Certified/Onan-Cummins Certified
|
|
|
|
|