07-23-2013, 01:04 PM
|
#43
|
Senior Member
Join Date: Jul 2013
Posts: 143
|
Quote:
Originally Posted by clyon51
Ok, doesn't look like you have an EMS. In the below picture, you see my power cable entering a junction box, then the blue conduit that goes to my transfer switch. The 30a outlet above is where I plug my cord and is feed only by the 30a genny circuit. The grey center conduit comes from the genny and is only the 20a circuit. Both the 20 and 30 circuits come back through the lower conduit and runs to the main breaker box in the coach.
Anyway, your ATS should look and operate very similar, the only difference is you don't need to move your cord. Again, most coaches have the ATS in this area, but not all. Yes when everything is operating as it should, you can run both ACs at once with genny running, that's what's nice with a 50a genny in a 30a coach.
Yes, all the ATS does is route the 30a to the coach regardless of where it's coming from. In your coach, I'm just not sure if that ATS handles the 20a circuit at the same time or if it is handled somewhere else. When you find the ATS and the in and outbound wires, that should be apparent.
|
Mine does not look like this for certain.
I did get in touch with Fleetwood and they sent a better wiring diagram. From what I can tell from the print and have heard is the 20a should power the front air, the 30a do the rest of the coach. That is definitely not what I experience.
Jeff
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
07-23-2013, 01:49 PM
|
#44
|
Senior Member
Monaco Owners Club
Join Date: Mar 2012
Location: Angola State Prison - Murder
Posts: 4,230
|
From what Lincolnboy just described with his FW, if you missed seeing or finding that 30a recepticle for the power cord when using genny, that exactly describes the problem you are having. This is also an indication since you are seeing no ATS.
__________________
John & Clare Lyon
2007 43.5' Monaco Dynasty Palace III (All Electric)
Towd: 2011 Chevy Equinox
|
|
|
07-23-2013, 02:00 PM
|
#45
|
Senior Member
Join Date: Jun 2009
Posts: 1,528
|
Question
Based on what I am reading in your Coach's Owners Manual, do you by chance have a Intellitec Climate Control center?
If so then that plays a part in controlling some of this
http://www.flemingsalesoem.com/intel...F/53221301.pdf
Dave
|
|
|
07-23-2013, 04:30 PM
|
#46
|
Senior Member
Join Date: Jul 2013
Posts: 143
|
Quote:
Originally Posted by Dave78Chief
|
Yes. That is mine.
|
|
|
07-25-2013, 05:22 AM
|
#47
|
Senior Member
Join Date: Jul 2013
Posts: 143
|
UPDATE:
I found the problem.
Inside the Onan genset I found the two load wires at the circuit breakers to be reversed. The 20a breaker had the black/yellow wire attached which should have been on the 30a breaker. The black/yellow wire connects to the 10ga coach wire at the 4x4 box in the genset compartment.
Tested and found the front air runs on the 20a breaker, the 30a controls everything else. Just as it was supposed to.
Thanks for all your input everybody, it was a learning experience.
Jeff
|
|
|
07-25-2013, 05:25 AM
|
#48
|
Community Administrator
Join Date: Aug 2009
Posts: 53,540
|
Thanks for the update. Glad you found the problem.
__________________
Cliff,Tallulah and Buddy ( 1999-2012 )
|
|
|
07-25-2013, 07:27 AM
|
#49
|
Senior Member
Texas Boomers Club Fleetwood Owners Club Solo Rvers Club Freightliner Owners Club
Join Date: Jul 2011
Location: Lakin, Ks.
Posts: 3,636
|
Quote:
Originally Posted by Agility57
UPDATE:
I found the problem.
Inside the Onan genset I found the two load wires at the circuit breakers to be reversed. The 20a breaker had the black/yellow wire attached which should have been on the 30a breaker. The black/yellow wire connects to the 10ga coach wire at the 4x4 box in the genset compartment.
Tested and found the front air runs on the 20a breaker, the 30a controls everything else. Just as it was supposed to.
Thanks for all your input everybody, it was a learning experience.
Jeff
|
Then I got my Air Conditioners totally reversed with my prior statement. I thought the back one was on the 20 amp but I know it must be the front one, Jeff.
Sorry, I'm gettin old....and CRS Syndrome.....
__________________
[SIGPIC][/SIGPIC]Kent: 2015 Fleetwood Bounder 35K
With Ferbie (ShihTzu) Lilly (Pekingese) & Daisy (Yorkie) Memoriam: Katie, Spencer, Zoey, Susie, Angie
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
Similar Threads
|
Thread |
Thread Starter |
Forum |
Replies |
Last Post |
30A to 50A Shoreline Upgrade?
|
txquigly |
Class A Motorhome Discussions |
12 |
06-23-2013 03:35 PM |
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|