I made some progress. Following the troubleshooting flow and the note about the flashing green LED.
AC present on outside PCB across Test Point 1 and 5.
Bypassed both thermisters (Indoor coil and Outdoor coil) no change.
This indicates the yellow Exclusion Relay is bad (or the whole PCB) - see picture below
https://drive.google.com/file/d/0B1n...it?usp=sharing
I was poking at the relay with a pointed piece of plastic and pressed a little too hard. I actually poked a hole into the relay and my outdoor fan and compressor came on. See stabbed relay below
https://drive.google.com/file/d/0B1n...it?usp=sharing
The temperature quickly started to drop and when 1 degree below setpoint AC automatically kicked off. Once it warmed up again it still worked.
So I isolated it to the Exclusion Relay and stabbed it to temporarily fix the problem (not recommended). It's less than $10 for the part, solders to the PCB with 8 leads. I will replace it before our next vacation in February.
Thanks again for all the help!