Im running a Honda EU3000 in the bed of my truck to supply power to the fifth wheel when dry docking.
The Honda will start the AC unit fine, but after about 20-30 minutes (variable) the breaker on the generator kicks out the power to the trailer. I always make sure the fridge is set to Gas Only when I do this, and don't use the microwave unless I turn off the AC first.
Theres something else causing an occassional load on the AC circuits to draw enough power to overload the Honda. Any ideas what it is and how to easily disable it for a few hours? Or even how to isolate what it is?
The fiver has a Coleman Mach 15 AC pulling 16.1Amps at full load under extreme conditon 115F outside.
Honda EU3000 rated at 23.3Amps continuous and 25Amps max.
This problem is not at startup...as I know you need to wait 5 minutes for the pressure to drop on the AC unit before starting it back up. The AC and Honda just kick off while the AC is running.
Any and all suggestions and experiences appreciated.
Thanx,
Joe
__________________
2004 Dodge Ram 5.9L Cummins HO, Auto QC 4WD SRW LWB....2004 HitchHiker II LS, 30.5 RLBG, Dbl Slide....2005 Sandpiper Sport 19ft T21 toyhauler
|
|
|
|
| |
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
06-12-2006, 04:03 PM
|
#2
|
|
Senior Member
Join Date: Mar 2003
Posts: 136
|
Im running a Honda EU3000 in the bed of my truck to supply power to the fifth wheel when dry docking.
The Honda will start the AC unit fine, but after about 20-30 minutes (variable) the breaker on the generator kicks out the power to the trailer. I always make sure the fridge is set to Gas Only when I do this, and don't use the microwave unless I turn off the AC first.
Theres something else causing an occassional load on the AC circuits to draw enough power to overload the Honda. Any ideas what it is and how to easily disable it for a few hours? Or even how to isolate what it is?
The fiver has a Coleman Mach 15 AC pulling 16.1Amps at full load under extreme conditon 115F outside.
Honda EU3000 rated at 23.3Amps continuous and 25Amps max.
This problem is not at startup...as I know you need to wait 5 minutes for the pressure to drop on the AC unit before starting it back up. The AC and Honda just kick off while the AC is running.
Any and all suggestions and experiences appreciated.
Thanx,
Joe
__________________
2004 Dodge Ram 5.9L Cummins HO, Auto QC 4WD SRW LWB....2004 HitchHiker II LS, 30.5 RLBG, Dbl Slide....2005 Sandpiper Sport 19ft T21 toyhauler
|
|
|
|
| |
|
06-12-2006, 05:30 PM
|
#3
|
|
Senior Member
Appalachian Campers Pond Piggies Club Winnebago Owners Club Mid Atlantic Campers
Join Date: Dec 2002
Location: Sarver, PA/Crystal River, FL/Hawthorne, PA
Posts: 3,762
|
How long is your extension cord and is it the proper gauge???
__________________
Sarver, PA/Crystal River, FL/Hawthorne, PA · FMCA 335149 · Mystic Knights of the Sea
2005 Suncruiser 38R · W24 chassis, no chassis mods needed · 2003 Honda Civic EX · 2008 Honda Odyssey EX-L
|
|
|
|
| |
|
06-12-2006, 06:03 PM
|
#4
|
|
Senior Member
Join Date: Mar 2003
Posts: 136
|
The cord running from the gen set to the trailer power center is about 40 ft long and is 3 conductor #8 cu. I intentionally oversized it to avoid voltage drop. At the panel box end a 3ft std 30amp cord pigtail connects to the gen set cord. My recollection of past performance was that there was no significant voltage difference when on the gen set (115v) vs shore power (120v)
I do get a ground fault alarm whenever I start the Honda gen set up though. Still trying to figure out why that is, since all grounds are connected in the wiring system.
Thanx for any help.
Joe
__________________
2004 Dodge Ram 5.9L Cummins HO, Auto QC 4WD SRW LWB....2004 HitchHiker II LS, 30.5 RLBG, Dbl Slide....2005 Sandpiper Sport 19ft T21 toyhauler
|
|
|
|
| |
|
06-13-2006, 01:12 AM
|
#5
|
|
Community Moderator
Gulf Streamers Club Country Coach Owners Club Appalachian Campers
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 7,952
|
Check the condition of your batteries; if they require the converter /charger to put out a lot of amp this could be a problem for the 3000 watt generator.
__________________

Mike, Certified Master RV Technician
Amy, RV Merchandiser; Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser & 2 toads
|
|
|
|
| |
|
06-13-2006, 05:49 AM
|
#6
|
|
Senior Member
Join Date: Feb 2001
Location: Texas hillcountry USA
Posts: 499
|
I also think the converter is asking for power and tripping the breaker when it does.
__________________
Robert & Nancy with "Murphy the EOG"
KE5NWT
02 Holiday Rambler 32SKS fiver, 02 F350
|
|
|
|
| |
|
06-13-2006, 06:28 AM
|
#7
|
|
Senior Member
Join Date: Mar 2003
Posts: 136
|
Converter/charger.........
That's what I was thinking would cause an intermittant load that might put a big enough load on the 120v system to put me over the load limit for the Honda while running my AC.
Is there some way I could shut down the 'converter/charger only' while Im on gen power, without turning off the 12v lights, refer igniter, water pump etc?
Thanx,
Joe
__________________
2004 Dodge Ram 5.9L Cummins HO, Auto QC 4WD SRW LWB....2004 HitchHiker II LS, 30.5 RLBG, Dbl Slide....2005 Sandpiper Sport 19ft T21 toyhauler
|
|
|
|
| |
|
06-13-2006, 06:39 AM
|
#8
|
|
Senior Member
Join Date: Feb 2001
Location: Texas hillcountry USA
Posts: 499
|
You could find the "110v power-in" to the converter and turn it off (maybe have to install a switch/breaker or unplug converter). With converter off, use your batteries to power all 12 volt.
__________________
Robert & Nancy with "Murphy the EOG"
KE5NWT
02 Holiday Rambler 32SKS fiver, 02 F350
|
|
|
|
| |
|
06-13-2006, 07:13 AM
|
#9
|
|
Senior Member
Join Date: Mar 2006
Location: Mead, WA
Posts: 187
|
The converter/charger may have it's own breaker. If so you can trip it before you run the generator.
__________________
2004 Chevy Silverado 2500HD - Duramax/Allison
1997 Sandpiper 25FLS
|
|
|
|
| |
|
06-13-2006, 08:47 AM
|
#10
|
|
Senior Member
Join Date: May 2005
Location: South Carolina
Posts: 249
|
I do not have an answer for you but just wanted to let you know that I had a 3000i and used it on my fiver. I had it mounted on the back so no extension cord but mine ran the air along with lights, tv, and so on. Not the microwave with air running.
Have you tried it without the extension cord?
__________________
2005 Damon Challenger 371
|
|
|
|
| |
|
06-13-2006, 04:26 PM
|
#11
|
|
Senior Member
Join Date: Mar 2003
Posts: 136
|
All good ideas guys.....I will try them all and by process of elimination determine the best fix.
As of now I've found the 110V 15A breaker that feeds the converter and I can turn it off when using the Honda, allowing the batteries to power the 12V system.
Will post here my testing results in a few days.
Regards,
Joe
__________________
2004 Dodge Ram 5.9L Cummins HO, Auto QC 4WD SRW LWB....2004 HitchHiker II LS, 30.5 RLBG, Dbl Slide....2005 Sandpiper Sport 19ft T21 toyhauler
|
|
|
|
| |
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|

»
Recent Discussions

»
Upcoming Rallies
No events scheduled in the next 365 days.
|
»
iRV2 on facebook
|