Hi all
I want to run a 50 amp service to one side of my house so i can plug in my MH. Is there a special way to do it. I have the wire, 6/3 with ground ( 4 wires ) and i have the 4 prong outlet. Not sure about the neutral and the ground. I think i will need also two single 50 amp breakers and not a 240 volt double 50 amp breaker. Any advice will help.

__________________
Al & Katie
2005 Excursion 39L
Retired 33 years NOFD and survived Katrina
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-06-2011, 01:44 AM   #2
Dunner is online now
Senior Member
Dunner's Avatar
Join Date: Jun 2011
Location: Phx, Arid~zona
Posts: 4,538
I did the same thing and used a double 50 amp breaker. If one leg trips, it will be for a reason and will also trip the other leg.

Go here and click on the 50 amp service on the left.

RV Electric

__________________
2004 32' F53 National Sea Breeze 1311 - Segway X2 - Sadie, Co-Pilot & Best Friend
1800 lb, 400 HP, Corvette LS1 Powered Mid-Engine Sandrail
1997 Dodge Ram 2500 CTD - 1994 Dodge Ram Stepside 1500
  Reply With Quote
   
Old 11-06-2011, 01:55 AM   #3
RV Wizard is offline
Community Moderator
RV Wizard's Avatar


Gulf Streamers Club
Country Coach Owners Club
Appalachian Campers
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 8,263
Al, you will indeed need a two pole 50 amp circuit breaker. Look on the compartment door for a label which indicates the coach power supply is 120/240 volts AC, 50 Amps, 60 Htz single phase. In the cable there should be a Black, red, white and green conductor. The red and black will go to the double pole circuit breaker and to the two flat terminals on opposite sides of each other on the receptacle. At the distribution panel of the house the green conductor is attached to the equipment ground bar (you will see a lot of bare copper wires attached here). The half round terminal of the receptacle is the equipment ground and the green conductor attaches here. The flat terminal opposite from the equipment ground is the neutral terminal on the receptacle. The white conductor attaches here and to the neutral bar in the distribution panel. You will see other white conductors attached to this neutral bar. If you need a picture, you can go http://www.wylersonwheels.com/docume...calHookups.pdf for the receptacle side of things. If you are not comfortable with electrical wiring, get an electrician to wire it exactly like a 50 amp 4 wire range circuit and you will be good to go.
__________________

Mike, Certified Master RV Technician
Amy, RV Merchandiser; Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser w/ Banks & 2 toads
  Reply With Quote
   
Thumbs up
Old 11-06-2011, 05:39 AM   #4
ajm12 is offline
Member
ajm12's Avatar


Fleetwood Owners Club
Join Date: Apr 2011
Posts: 78
Quote:
Originally Posted by Dunner View Post
I did the same thing and used a double 50 amp breaker. If one leg trips, it will be for a reason and will also trip the other leg.

Go here and click on the 50 amp service on the left.

RV Electric
Thanks great info. You confirmed what i though. Was told that you could not connect the ground and neutral to the same bar in the panel. Which they have a neutral bar and a ground bar and they tie together so was just a little confused.
__________________
Al & Katie
2005 Excursion 39L
Retired 33 years NOFD and survived Katrina
  Reply With Quote
   
Old 11-06-2011, 05:46 AM   #5
ajm12 is offline
Member
ajm12's Avatar


Fleetwood Owners Club
Join Date: Apr 2011
Posts: 78
Quote:
Originally Posted by RV Wizard View Post
Al, you will indeed need a two pole 50 amp circuit breaker. Look on the compartment door for a label which indicates the coach power supply is 120/240 volts AC, 50 Amps, 60 Htz single phase. In the cable there should be a Black, red, white and green conductor. The red and black will go to the double pole circuit breaker and to the two flat terminals on opposite sides of each other on the receptacle. At the distribution panel of the house the green conductor is attached to the equipment ground bar (you will see a lot of bare copper wires attached here). The half round terminal of the receptacle is the equipment ground and the green conductor attaches here. The flat terminal opposite from the equipment ground is the neutral terminal on the receptacle. The white conductor attaches here and to the neutral bar in the distribution panel. You will see other white conductors attached to this neutral bar. If you need a picture, you can go http://www.wylersonwheels.com/docume...calHookups.pdf for the receptacle side of things. If you are not comfortable with electrical wiring, get an electrician to wire it exactly like a 50 amp 4 wire range circuit and you will be good to go.
Thanks Mike good info. Very familiar with wiring homes. I was told that RV Wiring was different then home wiring. So was a little confused for a moment. Now i know what that person was talking about the neutral and ground being separate until it reaches the main panel.
__________________
Al & Katie
2005 Excursion 39L
Retired 33 years NOFD and survived Katrina
  Reply With Quote
   
Old 11-06-2011, 07:37 AM   #6
Dunner is online now
Senior Member
Dunner's Avatar
Join Date: Jun 2011
Location: Phx, Arid~zona
Posts: 4,538
That's still confusing to me. Looking at them, they appear to be the same at the service panel.
__________________
2004 32' F53 National Sea Breeze 1311 - Segway X2 - Sadie, Co-Pilot & Best Friend
1800 lb, 400 HP, Corvette LS1 Powered Mid-Engine Sandrail
1997 Dodge Ram 2500 CTD - 1994 Dodge Ram Stepside 1500
  Reply With Quote
   
Old 11-06-2011, 07:56 AM   #7
ajm12 is offline
Member
ajm12's Avatar


Fleetwood Owners Club
Join Date: Apr 2011
Posts: 78
Quote:
Originally Posted by Dunner View Post
That's still confusing to me. Looking at them, they appear to be the same at the service panel.
Yes i know what you mean. Had everything ready to go then when i was told that i stopped dead in my tracks and then started scratching my head. Thanks again
__________________
Al & Katie
2005 Excursion 39L
Retired 33 years NOFD and survived Katrina
  Reply With Quote
   
Old 11-06-2011, 08:08 AM   #8
Dunner is online now
Senior Member
Dunner's Avatar
Join Date: Jun 2011
Location: Phx, Arid~zona
Posts: 4,538
Just like an amp meter shunt, there could be a minute amount of voltage difference. Don't know if it matters though.
__________________
2004 32' F53 National Sea Breeze 1311 - Segway X2 - Sadie, Co-Pilot & Best Friend
1800 lb, 400 HP, Corvette LS1 Powered Mid-Engine Sandrail
1997 Dodge Ram 2500 CTD - 1994 Dodge Ram Stepside 1500
  Reply With Quote
   
Old 11-06-2011, 09:42 AM   #9
vermilye is offline
Senior Member
vermilye's Avatar


Join Date: Nov 2006
Location: Oswego, NY
Posts: 188
Send a message via Skype™ to vermilye
Quote:
Originally Posted by Dunner View Post
That's still confusing to me. Looking at them, they appear to be the same at the service panel.
The service entrance panel is the only place the neutral ties to the ground. All additional panels (called sub panels) require a separate neutral from the ground. An RV is treated as a "sub panel" ie it must have both a neutral buss & a ground buss.

The reason for this is to prevent the neutral current from being carried by the ground system. If a sub panel (or RV) has the neutral & ground tied together, the neutral current would be split between the ground & neutral wires. Because most of the metal in a home is tied to the ground, it would be likely that the plumbing, ductwork, etc in the home would be carrying current. A shock hazard would exist for plumbers, even a homeowner running water from a faucet.

Again, a sub panel or RV should have a ground buss tied to the chassis of the RV & an insulated neutral buss that is not connected to the chassis or ground wiring.
  Reply With Quote
   
Old 11-06-2011, 09:58 AM   #10
Full.Monte is offline
Senior Member
Join Date: Jul 2011
Posts: 275
If you really want to understand wiring, go to Home Depot and buy a copy of Wiring Simplified by Richter. You should find it in the electrical dept. on a hook. I've read it three times, and there is nothing I can't do on house or RV wiring because of it.

__________________
2004 Tiffin Allegro 27.5 ft. P32 18,000 lb GVW. 8.1 liter engine on Workhorse chassis. 12,000 miles. Acquired 7/11. 19.5 inch wheels.
  Reply With Quote
   
Reply

Tags
power


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
House Power by RV Generator... poppatello RV Systems & Appliances 22 08-31-2011 10:40 AM
House battery power cuts off jrcwen Winnebago Industries Owner's Forum 5 07-20-2009 02:43 PM
RV genset to power house during power outage McDanie1 Newmar Owner's Forum 8 07-16-2009 08:54 AM
No 12 volt house power GKM Winnebago Industries Owner's Forum 8 02-07-2009 12:43 PM
house battery power loss Jack_Va MH-General Discussions & Problems 5 07-11-2005 10:00 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 06:29 AM.