Coleman 13,500 rooftop ac circa 1999. Getting 10 degree temperature differential between intake and exhaust. Pulls about 7 amps at 95 degree ambient temperature. Evaporator and condenser are both clean. Iíve read that these ac are charged to an amp draw at a certain temperature and not a low side/high side pressure range like automotive acís. Before I chunk this ac in the trash I would like to confirm that itís low (too low current draw?) and if so, possibly install one of those piercing ports on the low side and add a smidge of R22. Looking at this data plate, would the amp draw be the
Fan Motor FLA of 2.9 plus the
Compressor BCSC of 8.7 which would equal 11.6?

Or would it be the RLA of 7.6 plus the fan FLA of 2.9 equaling 10.5?

Or neither.

If so, at what temperature is that at? 90? And is it 1 amp change per 10 degrees of temperature rise/fall?

Thanks.
Attached Thumbnails
Click image for larger version

Name:	A972C381-8968-4DC0-802A-766D4A794D09.jpg
Views:	14
Size:	322.0 KB
ID:	257861  
__________________

Fugitive861 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-24-2019, 05:25 PM   #2
Member
 
Join Date: Apr 2018
Location: North Florida
Posts: 51
too much mumbo jumbo..its old an worn out.. change it out. R22 is hard to find and would cost a fortune to put a Shrader valve on it and charge the unit.. It probably has a leak in the evaporator and not worth fixing.
__________________

tanman32225 is offline   Reply With Quote
Old 08-24-2019, 05:40 PM   #3
Senior Member
 
Join Date: Sep 2015
Location: Houston, TX
Posts: 181
Quote:
Originally Posted by tanman32225 View Post
too much mumbo jumbo..its old an worn out.. change it out. R22 is hard to find and would cost a fortune to put a Shrader valve on it and charge the unit.. It probably has a leak in the evaporator and not worth fixing.
Thank you for your insightful information.
Fugitive861 is offline   Reply With Quote
Old 08-24-2019, 05:59 PM   #4
Senior Member
 
Join Date: Aug 2017
Posts: 1,347
Quite possibly the compressor is worn out or you have a leak. You would have to install ports on the hi & low pressure sides to properly test it. Your looking at a few hundred just to find out what the problem is , then there is the cost to repair it, and you still have an old unit.
__________________
1993 Tiffin Allegro Bay 32'
Soppy is offline   Reply With Quote
Old 08-24-2019, 06:28 PM   #5
Senior Member
 
Stan&Jacquie's Avatar
 
Monaco Owners Club
Join Date: Mar 2012
Location: Allentown, PA
Posts: 749
20 years out of a rooftop AC unit is darn good. This puppy doesn't owe you anything and should be laid to rest. The gentlemen above hit this nail on its head. Easy for us to say "Go buy a new one" with your wallet but any money put into your unit will be money lost.
__________________
Stan & Jacquie
2007 Monaco Knight DFT 40'
2012 Equinox w/Air Force I, Blue Ox Alpha & Base, 600 Watts Solar.
Stan&Jacquie is offline   Reply With Quote
Old 08-24-2019, 06:35 PM   #6
Senior Member
 
Join Date: Nov 2015
Posts: 10,366
LRA-----Locked Rotor Amps (max current to the motor when it is in a locked)

RLA-----Rated Load Amps (calculate the max overcurrent protection permitted)

FLA-----Full Load Amps ( motor's rated-current at rated-load and rated-voltage)


BCSC---Branch-Circuit Selection Current (determines ratings of motor branch-circuit conductors--always higher or at least equal to RLA)


Compressor RLA PLUS Fan Motor FLA-----7.6A +2.9A =====10.5A
Those figures give you an indication of how close unit is running to specs
BUT not good for figuring IF it is cooling properly


AS noted above.......
R22 plus shrader valve (which leak) plus time/labor IF you have the proper gauges might be 'fun experiment' but hardly worth it for that old of an RV a/c unit (20+ yrs old)
Got your monies worth !
__________________
Is it time for YOUR Medication or Mine?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
Old-Biscuit is online now   Reply With Quote
Old 08-24-2019, 07:05 PM   #7
Senior Member
 
Join Date: Sep 2015
Location: Houston, TX
Posts: 181
Quote:
Originally Posted by Old-Biscuit View Post
LRA-----Locked Rotor Amps (max current to the motor when it is in a locked)

RLA-----Rated Load Amps (calculate the max overcurrent protection permitted)

FLA-----Full Load Amps ( motor's rated-current at rated-load and rated-voltage)


BCSC---Branch-Circuit Selection Current (determines ratings of motor branch-circuit conductors--always higher or at least equal to RLA)


Compressor RLA PLUS Fan Motor FLA-----7.6A +2.9A =====10.5A
Those figures give you an indication of how close unit is running to specs
BUT not good for figuring IF it is cooling properly


AS noted above.......
R22 plus shrader valve (which leak) plus time/labor IF you have the proper gauges might be 'fun experiment' but hardly worth it for that old of an RV a/c unit (20+ yrs old)
Got your monies worth !


Thank your for your information. I can check amperage for free, add a shrader valve for $8 and I already have the R22. Even if it doesnít work itís no big deal.
Fugitive861 is offline   Reply With Quote
Old 08-24-2019, 07:15 PM   #8
Moderator Emeritus
 
TXiceman's Avatar


 
Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Full Time, TX Home Base
Posts: 17,430
Blog Entries: 21
First off the saddle clamp valve are prone to leaking. i do not use them except for a temporary fix. Next, the easiest way to check unit performance is to run the unit on high fan and check the temperature difference between inlet air and outlet air temperature. The outlet should be 20 degF (+/- 2 degF) lower than the inlet. Both readings should be taken as close to the unit as possible.

Use a real liquid filled or temperature sensor thermometer to get your readings. The infra red temp guns do not read actual air temperature/ They only read the temperature of the surrounding surface.

And a 20 year old A/C unit really is not worth repairing. And I charge by pressure reading at the compressor suction and discharge while watching amps. For the manufacturers, the charge is put in by weight.

Ken
__________________
Amateur Radio Operator (KE5DFR)|Full-Time! - 2012 6.7L Ford Crew Cab Dually -2013 HitchHiker Champagne 38RLRSB - Travel with one Standard Schnauzer and one small Timneh African Gray Parrot
TXiceman is offline   Reply With Quote
Old 08-24-2019, 08:36 PM   #9
Senior Member
 
Join Date: Sep 2015
Location: Houston, TX
Posts: 181
https://www.airxcel.com/docs/default...e.pdf?sfvrsn=5
Fugitive861 is offline   Reply With Quote
Old 08-24-2019, 09:15 PM   #10
Senior Member
 
Join Date: May 2017
Location: Metamora, MI
Posts: 2,556
If you have the stuff and a set of gauges and have or learn the knowledge, go for it. Nothing lost in trying if the unit isn't putting out rated cold air.
__________________
2002 Newmar Mountain Aire Limited 4370 w/ Spartan K2 and Cummins 500hp
ASE Master Certified (a long.....time ago...)
Dav L is offline   Reply With Quote
Old 09-08-2019, 06:59 PM   #11
Senior Member
 
Join Date: Sep 2015
Location: Houston, TX
Posts: 181
The previous thread indicates that our rooftop ac temperature differential was only 10 degrees and that the amp draw was below spec. According to the manufacture, at 100 degrees it is to be RLA + 1. Data tag states RLA should be 7.6 plus the 1 make 8.6. I was getting 6.6 amps.



I added a piercing tap the the low side line. Slowly added a few ounces of R22 and the amp draw increased to 8.6 and temperature differential increased to about 18-19 degrees. It seems to be working as designed. Hopefully the leak is really, really slow. Ha
Attached Thumbnails
Click image for larger version

Name:	IMG_2354.jpg
Views:	7
Size:	234.1 KB
ID:	259667  
Fugitive861 is offline   Reply With Quote
Old 09-09-2019, 06:17 AM   #12
Senior Member
 
Monaco Owners Club
Join Date: Sep 2013
Posts: 1,518
Quote:
Originally Posted by Fugitive861 View Post
I added a piercing tap the the low side line. Slowly added a few ounces of R22 and the amp draw increased to 8.6 and temperature differential increased to about 18-19 degrees. It seems to be working as designed. Hopefully the leak is really, really slow. Ha
I always think it's funny that a do-it-yourself forum consistently condemns the A/C unit based on age. I've charged many including one currently on my roof and they all worked for years afterwards.

Good job!
__________________
2007 Monaco Signature Noble III 45' ISX 600HP
hypoxia is offline   Reply With Quote
Old 09-09-2019, 11:59 AM   #13
Senior Member
 
Join Date: Nov 2014
Location: TEJAS
Posts: 671
I have the same AC/s and because I have to modify everything, I added hi and low ports along with a TXV valve.



Hi side ran around 300 and the low side was 77. Compressor pulling 7.7 amps in 95 degrees.
spyderRV is offline   Reply With Quote
Old 09-09-2019, 05:45 PM   #14
Senior Member
 
TriMoot's Avatar


 
Join Date: Oct 2013
Location: Spokane, WA
Posts: 884
Blog Entries: 1
WOW! I wish I was brave enough to do something like this!
Watching...
__________________

__________________
___________________
1997 RexAir 32' Ford F53 Chassis, Banks system.
1997 Suzuki Sidekick JX, Spokane, WA
TriMoot is offline   Reply With Quote
Reply

Tags
roof



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Important to check your charge rates IASM Class A Motorhome Discussions 10 03-14-2015 08:27 PM
Battery charge rate & absorb charge time loisjop Entegra Owner's Forum 0 11-01-2014 01:15 PM
EMS - how to check it's working properly? vsheetz Fleetwood Owner's Forum 7 06-18-2012 10:47 AM
check check check Braselton Nomad Test Your Changes 0 03-11-2009 08:31 AM
Check engine and Low Battery/alternator charge on gauge Aggiepi Workhorse and Chevrolet Chassis Motorhome Forum 4 05-06-2007 07:52 AM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 11:20 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.