Installing a generator output plug

We survived Irma. I had a small gas generator that kept the fridge going, some lights, coffee pot etc. on the second day, I was able to get the MH out of storage and parked it in front of the house. Ran my trusty Onan QD 8000 and we slept in comfort with AC, hot water etc.

But I'd like to have the option of powering my house with the MH generator. I've seen the previous posts on IRV2 on this subject. I don't want to get into transfer switches, "suicide" connectors and the like. I'm just looking for someone who has tapped off the rv generator and installed a socket so I can run a heavy gauge line to my house. I'm pretty sure my generator is 110 only. I do have a couple of std house outlets I could plug into, but I'd prefer a more secure twist lock type wired directly to the generator. I'll put together some sort of gang box outlet thing for the house side.

Long power outages for us are fairly rare. Irma was 5 days. Charlie 12 years ago was almost 3 weeks. My little 2000 watt enverter generator is fine for most things. Can't run power tools with it though.

Looking to see what others have done

Thanks
jondrew55 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-18-2017, 07:40 AM   #2
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
Relatively easy to do on the coach side, just tap the generator output(s) and route them to a 50 amp receptacle, just like your RV uses. The problem starts on the house side since that would normally use a male receptacle to connect to the female twist lock on a 50 amp extension cord, but that would mean that the male outlet's pins would be hot when your house is powered from the grid. You can make a double male 50 amp cord...but...that is the definition of a suicide cord!

You can remedy this and be OK with code if you install an automatic transfer switch in your house, with the generator side going to the outlet.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 09-18-2017, 08:03 PM   #3
Senior Member
 
Hgrace56's Avatar
 
Join Date: Jan 2016
Location: Northridge, CA
Posts: 1,218
Be VERY CAREFUL if you are not a QUALIFIED AND LICENSED electrician.
Connecting to your house without proper isolation to the grid can provide DEADLY his voltage feedback to the utility worker trying to restore your power.
Your 120/240 volt genset could become 4,000-16,000 volts to the lineman.
__________________
Harry Grace
KM6ZRG
Hgrace56 is offline   Reply With Quote
Old 09-19-2017, 11:09 AM   #4
Senior Member
 
Join Date: Jan 2014
Posts: 4,641
Like I said, not asking about how to backfeed into my house. Just looking to see if anyone has installed an outlet on their RV genset.


Quote:
Originally Posted by Hgrace56 View Post
Be VERY CAREFUL if you are not a QUALIFIED AND LICENSED electrician.
Connecting to your house without proper isolation to the grid can provide DEADLY his voltage feedback to the utility worker trying to restore your power.
Your 120/240 volt genset could become 4,000-16,000 volts to the lineman.
jondrew55 is offline   Reply With Quote
Old 09-19-2017, 11:26 AM   #5
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
House aside, install a standard 50 amp RV plug in the basement somewhere and tap off all 4 lines...that's it. Then get a standard RV 50 amp extension cord. Should be no problem.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 09-19-2017, 11:34 AM   #6
Senior Member
 
77Travco's Avatar
 
Join Date: Oct 2015
Location: Texas Hill Country
Posts: 1,793
Glad you are ok.
Just run a long extension cord from a 120V outlet on/in your coach to whatever it is that you're trying to power up. You're only going to be able to run a limited amount of items anyway.
77Travco is offline   Reply With Quote
Old 09-19-2017, 11:50 AM   #7
Senior Member
 
Join Date: Jul 2014
Posts: 35,317
After installing a 50 amp outlet, just after the generator output, but before the automatic transfer switch, as others suggested, everything you would need is on this site.

https://www.amazon.com/gp/aw/d/B000K...ID=71jScte0hfL

The spider box, the cord and the adaptor to plug into your newly installed MH outlet.

Bring the spider box inside and plug in what you want to power.
twinboat is offline   Reply With Quote
Old 09-19-2017, 12:19 PM   #8
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
Seems better to go a little further on the house, certainly no suicide cords but it should be pretty easy to get connected to both sides of the breaker panel and feather whatever he doesn't want to power (like all the double breakers!!!!) But that will require some sort of transfer switch.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 09-19-2017, 12:42 PM   #9
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 7,383
OP--there are [IMHO] some pretty good ideas here concerning safety. Agree, it would be fairly easy to just tap one or both leads/legs from your genset to provide remote power, eg, most rigs have a junction box near the genset. The harder part is safely distributing that power to your home. For example: tapping directly off genset leg gives you two 35 [40amp] legs at 120v[not phased???]--so you need to fuse/breaker these down to 15 or 20 amps circuits. The spider box example above is pricey put a good solution. Depending on amps and distance, you will need a power cable rated for that resistance--like maybe 8 gauge [10g probably too small]. Then use individual extension cords for each appliance. Yup--you could wire the cable directly into your house main breaker box but you would have to shut down most of the unneeded circuits to avoid overload. As mentioned, you would also need to develop a fool-proof protocol to make sure main breakers are off while hooked up to generator....Of course, none of this would be to code!!!!! So if you are seeking "permission" to by-pass code and do this on the cheap--you wont get it here.
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
Old Scout is offline   Reply With Quote
Old 09-19-2017, 01:04 PM   #10
Senior Member
 
Fredward's Avatar
 
Join Date: Feb 2016
Location: Minnesota
Posts: 462
Safety for those in your house and those working on the utility lines is the most important concern.

That being said, the Onan QD series Diesel generators are set up to produce two 30 amp 125 volt circuits as I understand it. It is a single breaker switch on the genset but it is actually a dual breaker. If you add a properly wired receptical to the the main circuit breaker panel in the motorhome; can you power both legs of the standard 100 or 200 amp household panel in order to run things like 230 volt pumps? Our house has a private well and septic.

Fred
__________________
2000 CC Magna #5734
C-10 Cat Allison 4060
MN
Fredward is offline   Reply With Quote
Old 09-19-2017, 02:10 PM   #11
Senior Member
 
Join Date: Jul 2014
Posts: 35,317
If it is 120 volts output only, both legs will be in phase and no 240 volt items will work.
twinboat is offline   Reply With Quote
Old 09-19-2017, 03:51 PM   #12
Senior Member
 
Fredward's Avatar
 
Join Date: Feb 2016
Location: Minnesota
Posts: 462
Yes that is what I have assumed. But I guess I should test it to be sure. Seems like I might have bench tested my last Onan QD when I had it apart but don't remember the outcome.
Fred
__________________
2000 CC Magna #5734
C-10 Cat Allison 4060
MN
Fredward is offline   Reply With Quote
Old 09-20-2017, 01:33 AM   #13
Senior Member
 
Join Date: Jun 2016
Posts: 113
Note: If your new circuit is not inspected by an electrician, and is found to be the cause of a fire, you may be out of luck depending on where you live and what your policy states.

With that said, whatever you choose to do, choose to do it safely. =)
wizechatmgr is offline   Reply With Quote
Old 09-20-2017, 05:08 AM   #14
Senior Member
 
xrated's Avatar
 
Join Date: Jan 2017
Location: "Murvul", TN
Posts: 1,653
Jondrew.....unless is am not following you and what you hope to do, it sounds to me like you are wanting to supply some amount of power to your house from your generator. That should NEVER, EVER be done without the proper equipment in place to isolate that generator power from feeding back into the existing power grid......the power company's lines coming into your house. Any external feed (your generator) that will supply power to you house without the proper isolating equipment installed, runs an extremely high risk of killing a power company lineman. Read that last sentence again.....an extremely high risk of killing a lineman. Not only is it illegal to do without the proper equipment, you will likely loose everything you own during the wrongful death lawsuit and you will have to live with the fact that you killed or seriously injured/burned a lineman....and all because you wanted some electric service and didn't want to spend the money to have it done correctly.

My response is meant to be very harsh and stern. I've been a Journeyman Electrician for 37 years and know first hand the dangers of Electricity when it is not done properly. People die...people are burned beyond recognition and survive, only to be disfigured for the rest of their lives. Your 120 volts, if it makes its way back to the transformer because you didn't install the proper equipment can be stepped up to approx. 7000 volts.........that's SEVEN THOUSAND VOLTS.

As I stated, I've been in this line of work for a long time, and didn't make it this long by being careless or stupid.....and I take stuff like this very seriously.

Hire a qualified Electrician that knows what they are doing and can provide you a way to have standby power if you need it. You obviously don't have the knowledge about residential electrical systems and the hazards that you could potentially to the power company employees.
__________________
2016 F350 Crew Cab Dually Diesel King Ranch 4x4
2018 Grand Design Momentum 394M Toy Hauler
Excessive Payload Capacity is a Wonderful Thing!
xrated is offline   Reply With Quote
Reply

Tags
generator, install



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Checking frequency output and voltage output of Onan 5000 Genset Generator. MajesticRV MH-General Discussions & Problems 4 11-07-2012 10:16 AM
NO AC Power output from Generac generator, still runs but ... talock RV Systems & Appliances 10 12-27-2010 09:21 PM
Generator output Belgian RV Systems & Appliances 3 08-01-2010 12:36 PM
Output problem with Generac 55G Primepact Generator purplbee MH-General Discussions & Problems 5 08-27-2008 06:14 PM
onan 5500 generator runs but no power output Jim RV Systems & Appliances 4 09-13-2007 04:41 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 11:20 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.