Old 01-12-2013, 12:54 PM   #15
Senior Member
 
Join Date: Feb 2010
Posts: 4,489
Another possibility is an " active fault".

What I mean is when no power is applied all is well.

When power is applied things change.

Switch mode power supplies are funny beasts, inverters and some converters use them.

They generate magnetic fields that induce currents that are called leakage currents, if the chassis is not properly grounded a voltage will develop between an ungrounded chasis and ground, this also may show up on the neutral creating problem with GFI.

You may try getting an extension cord connected to a GFI outlet and use an old power cord attached directly to the unit see if it works.

You may have a poor connection on a wire that with the low current of the meter looks fine but fails on the higher load of the inverter.
__________________

__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-12-2013, 12:56 PM   #16
Senior Member
 
Join Date: Feb 2010
Posts: 4,489
Beat me to the cord...on the right track

Move your power connection Clouse to the source.

Normalize the inverter and locate the other end of the wires and make the connection there.
__________________

__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 01-12-2013, 01:20 PM   #17
Member
 
Join Date: Dec 2011
Posts: 60
Double checking all connections I can access.....some excess (slop) wire in the Transfer switch box, so I am cleaning up everything there...on to the interior House AC panels next.
Converter still working great on direct power cord....just went to float charge...
__________________
jwcgc629 is offline   Reply With Quote
Old 01-12-2013, 06:31 PM   #18
Senior Member
 
Mrchips's Avatar
 
American Coach Owners Club
Join Date: Nov 2012
Location: BCS, Texas
Posts: 506
Mine would go back and forth from bulk to absorb. Now that I have been sitting here the past few days waiting on parts from magnum before they pull it and run bench tests the danged thing seems to be working fine. It went to float the other day, and today i noticed it said full charge. It never did that before we did all the tests and magnum had me do a reboot. Heck, it may now be fixed...I think I will still let magnum test it though. Mysterious self fixes typically don't work too long.

jwcgc629, where you located? Don't know what jwcgc629 stands for, but where I come from cgc629 would be the CGC Decisive out of Pascagoula, MS....LOL
__________________
Command Master Chief (USCG, RET)
Full Timing in a 2007 American Coach Eagle 45H towing a 2015 Ford F150 4x4 hauling a 2015 Anniversary Edition Honda Goldwing
Mrchips is offline   Reply With Quote
Old 01-12-2013, 08:07 PM   #19
Community Moderator
 
"007"'s Avatar


 
Nor'easters Club
Workhorse Chassis Owner
iRV2 No Limits Club
Join Date: Oct 2004
Posts: 26,563
MRChips if you have been moving battery cables around checking things you may have a loose cable or dirty cable connection on the chassis frame.
There are also heavy #6 copper wires to chassis frame also off inverter/converter.
If battery cables are stranded to inverter they maybe loose under screw terminations because they flatten out under the screw.
__________________
98KSCA, 99MACA, 03 KSCA-3740- 8.1 Chev-- ALLISON Trans, now in good hands
VISIT the NEWMAR QUICK TIPS & EASYMODS 1 & 2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS --- TECH INFORMATION
"007" is offline   Reply With Quote
Old 01-12-2013, 09:07 PM   #20
Senior Member
 
Mrchips's Avatar
 
American Coach Owners Club
Join Date: Nov 2012
Location: BCS, Texas
Posts: 506
007, nope have not touched anything. All the tests Magnum had me do had to do with just changing settings on the remote and telling them what the outputs were, aside from doing a re-boot on the inverter/charger.
__________________
Command Master Chief (USCG, RET)
Full Timing in a 2007 American Coach Eagle 45H towing a 2015 Ford F150 4x4 hauling a 2015 Anniversary Edition Honda Goldwing
Mrchips is offline   Reply With Quote
Old 01-12-2013, 09:15 PM   #21
Community Moderator
 
"007"'s Avatar


 
Nor'easters Club
Workhorse Chassis Owner
iRV2 No Limits Club
Join Date: Oct 2004
Posts: 26,563
Just to confuse you more maybe, if you have the coach plugged in and the fridge is on electric, a bad electric element heater will trip your GFI outlet after it heats up and would be only one of the elements if a 1200 series.
I would monitor your problem maybe your reset has taken care of problem.
__________________
98KSCA, 99MACA, 03 KSCA-3740- 8.1 Chev-- ALLISON Trans, now in good hands
VISIT the NEWMAR QUICK TIPS & EASYMODS 1 & 2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS --- TECH INFORMATION
"007" is offline   Reply With Quote
Old 01-13-2013, 08:45 AM   #22
Senior Member
 
Mrchips's Avatar
 
American Coach Owners Club
Join Date: Nov 2012
Location: BCS, Texas
Posts: 506
007, nothing turned on in the coach except the charger/inverter. The re-boot may have actually done something. Will see I guess.
__________________
Command Master Chief (USCG, RET)
Full Timing in a 2007 American Coach Eagle 45H towing a 2015 Ford F150 4x4 hauling a 2015 Anniversary Edition Honda Goldwing
Mrchips is offline   Reply With Quote
Old 01-13-2013, 04:24 PM   #23
Member
 
Join Date: Dec 2011
Posts: 60
Checked and tightened everything....hooked hot and neutral to the inverter one at a time....no trip (of course that is no use) No matter which is connected first, the moment I connect the other and the converter starts, (there seems to be a slight startup delay of a couple of seconds), it trips the GFI....Thought perhaps it is a startup surge and not a GFI issue, but the 20a test circuit doesnt trip, so it look like GFI and no an amperage related trip.

Im thinking of replacing the GFI breaker just to eliminate that....The charging circuit works fine when connected directly (to a 20a GFI outlet)...seems my 30a dedicated circuit has copped an attitude... Im stumped....

Jim
__________________
jwcgc629 is offline   Reply With Quote
Old 01-14-2013, 05:19 PM   #24
Member
 
Join Date: Dec 2011
Posts: 60
Disconnecting the 12v battery cable from the inverter eliminates the trip...
It does look for something to charge (blinking green LED) but does not trip...There is a rather healthy spark with connecting or disconnecting the cable from the inverter.....though the inverter is turned off...

What is all this telling me ??

Thanks
__________________
jwcgc629 is offline   Reply With Quote
Old 01-14-2013, 07:46 PM   #25
Senior Member
 
Join Date: Feb 2010
Posts: 4,489
Ground loop. ..

Battery ground is connected to frame as is the green safety ground.

Look for white wire to ground.

Could be bad charger, transformer maybe no isolation.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 01-14-2013, 07:49 PM   #26
Senior Member
 
HHIDan's Avatar
 
Join Date: Mar 2011
Location: Ottawa Ontario Canada
Posts: 1,252
If I understand correctly, the 30 amp GFI cord from the house is plugged in the shore power main RV plug. (That shore power goes thru the transfer switch then to the AC panel thru a breaker back to the converter (another set of breakers on the converter)). The 20 A GFI cord (that does not trip) you have connected to the converter's input directly. Is this correct?
If correct, then a bad connection in the transfer switch (loose screw) or AC panel would cause slight arcing which would trip a GFI. And the arcing would only happen when the current was significant enough, ie converter running...


Did the 30 A GFI connection use to work with this same RV?
If yes, could be the GFI itself, good idea to try another one just to see.
If not, check to make sure the neutral and ground are not connected together in the AC panel with a bonding screw (that should be removed).
__________________
DanielB
'06 Mountain Aire 4309, ISL 400-CM850, Spartan MMGT
'16 Jeep Wrangler
HHIDan is offline   Reply With Quote
Old 01-15-2013, 07:38 AM   #27
Member
 
Join Date: Dec 2011
Posts: 60
The dedicated 30a circuit I installed worked for a year with our 5th wheel and up until a few weeks ago on the Motorhome, so there isnt a wiring issue there, though I do think trying another GFI breaker may be worthwhile.

I have Checked/tightened all the connections in the transfer switch and AC panel that I can access.

It does work fine with an "extension cord" wired directly to the converter/inverter line input plugged into a 20a GFI outlet....charges the batteries..goes into float...all normal. Charges off the generator fine...inverts fine....

The ONLY thing that changed was we dry camped for a night (on some property we own close to home)...ran the genset most of the night....when we returned the next day and I connected the shore power, the problem manifest itself. It was connected to shore power until we left, 24 hours earlier...no issues. Thus I suspect it is related to the transfer switch itself ??

A real head scratcher.....
__________________
jwcgc629 is offline   Reply With Quote
Old 01-15-2013, 09:47 AM   #28
Senior Member
 
HHIDan's Avatar
 
Join Date: Mar 2011
Location: Ottawa Ontario Canada
Posts: 1,252
Is it easy enough to connect your 20 a cord to the RV plug and therefore go thru the exact same circuit that the 30 a goes thru? I would try that and I would also try a differenct 30 GFI.
After that test, you could move your connection to just beyond the transfer switch or before the AC panel (whichever is easier) to try to isolate the ground fault. Does your panel include EMS (load shedding)? I still think a loose connection or dirty contacts in your transfer switch might cause the "arcing" that would trip a GFI. Have you tried to clean the contacts?
And yes, I agree if it worked before your panel is wired fine. And the odds of arcing in the panel are slim.
Keep going, RV's can be as much fun as they can be a royal pain in the behind...
__________________

__________________
DanielB
'06 Mountain Aire 4309, ISL 400-CM850, Spartan MMGT
'16 Jeep Wrangler
HHIDan is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 01:33 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.