Old 01-19-2013, 02:02 PM   #29
Member
 
Join Date: Dec 2011
Posts: 60
Update....

Wired 12g extension cord to the main breaker panel....Couple of observations.

If the main shorepower cord is connected to my 30a outlet, the GFI trips the moment
I try to connect the neutral of the "extension cord" to the neutral buss. I can wire directly to the inverter from the panel with no problem....I can connect the ground (green) of the extension cord to the ground buss and the hot and neutral to the inverter wiring and it functions.

If I disconnect shore power, I can then connect the neutral of the "extension cord" to the panel buss, green to the ground bus and the hot directly. Yet when I try to connect the neutral of the inverter to the neutral buss in the panel, GFI trips....

Im going to need therapy if I dont figure this out soon....Still open for suggestions...Voltages everywhere look fine.

Thanks
jwcgc629 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-26-2014, 04:39 PM   #30
Junior Member
 
Join Date: Dec 2013
Posts: 12
I have a similar problem. I have a Xantrex Freedom inverter. Things seem to work fine on shore power or on the genset, but when I disconnect, one of the GFCI circuits trip. The other side works fine. I'm usually connected to shore power so its not a big issue, but I will drydock once or twice a month and its really a pain. Have you had any success troubleshooting the problem?

P.S. As a note, the problem seemed to occur after we had discovered a rat in the MH. He was there a few days and chewed up the central vac hose. Could he have possibly chewed a wire?
__________________
Wayne & Roxane McClain w/ Danny the Wonder Dog
2007 Fleetwood Providence/2008 Rav4 Toad
wmcclain is offline   Reply With Quote
Old 03-26-2014, 04:52 PM   #31
Senior Member
 
Join Date: Feb 2010
Posts: 4,654
Inverters are switch mode devices and as such have high leakage currents.

Be certian it has large and clean grounds.

Grounded to ac load center safety ground buss.
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 03-24-2016, 04:56 PM   #32
Junior Member
 
Join Date: Mar 2016
Posts: 1
xantrex sw 3012 gfci

Similar issue here. Dedicated gfci 30amp circuit at house. All worked fine until new inverter install. Then gfci trip every time. RV guy called xantrex and was told that gfci cannot be used with inverter. Meaning an upstream gfci cannot be used. I called and was told the same by xantrex customer service.
Something about a floating ground in the inverter.
Does this sound plausible to the experts in the forum? thanks!
~sholom
sholom770 is offline   Reply With Quote
Old 03-24-2016, 05:00 PM   #33
Senior Member
 
palehorse89's Avatar
 
Newmar Owners Club
Join Date: Oct 2009
Posts: 10,310
Quote:
Originally Posted by sholom770 View Post
Similar issue here. Dedicated gfci 30amp circuit at house. All worked fine until new inverter install. Then gfci trip every time. RV guy called xantrex and was told that gfci cannot be used with inverter. Meaning an upstream gfci cannot be used. I called and was told the same by xantrex customer service.
Something about a floating ground in the inverter.
Does this sound plausible to the experts in the forum? thanks!
~sholom
In most, the neutral and the ground are tied together........un- like a house.
Inverters/charger's will make a GFCI trip wire like this............un-balance sensed.......
__________________
2012 Essex 4544 2011 Jeep JK, M&G Braking, 2014 MTI 27' Hog Hauler, Wireless brake control, 2006 Ultra & 1989 Springer, 2003 Harley-Davidson
FLHR Road King Anniversary
palehorse89 is offline   Reply With Quote
Old 03-24-2016, 08:05 PM   #34
Senior Member
 
Join Date: Feb 2016
Posts: 691
Same issue with my fifth wheel. Trips gfi every time. Fine anytime else. Was told it won't work with gfi
gtsum2 is offline   Reply With Quote
Old 11-04-2019, 02:36 PM   #35
Junior Member
 
Join Date: Feb 2011
Posts: 24
30 or 50 amp GFIs are trickier than 20 amp, because they must monitor current flowing through L1, L2, and neutral. Highly reactive loads such as those found in most modern converters often cause them to trip. If you are in a bind for power, try adapting down and connect to a 20 amp outlet, and it will usually work, even if the 20 amp outlet has a GFCI.
campgroundguy is offline   Reply With Quote
Old 11-04-2019, 03:21 PM   #36
Senior Member
 
Join Date: Jul 2014
Posts: 35,441
Quote:
Originally Posted by campgroundguy View Post
30 or 50 amp GFIs are trickier than 20 amp, because they must monitor current flowing through L1, L2, and neutral. Highly reactive loads such as those found in most modern converters often cause them to trip. If you are in a bind for power, try adapting down and connect to a 20 amp outlet, and it will usually work, even if the 20 amp outlet has a GFCI.
30 amp service is L1 only. Same as 15 or 20 amp service, just more amps.
twinboat is offline   Reply With Quote
Old 11-04-2019, 03:44 PM   #37
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 3,165
Quote:
Originally Posted by sholom770 View Post
Similar issue here. Dedicated gfci 30amp circuit at house. All worked fine until new inverter install. Then gfci trip every time. RV guy called xantrex and was told that gfci cannot be used with inverter. Meaning an upstream gfci cannot be used. I called and was told the same by xantrex customer service.
Something about a floating ground in the inverter.
Does this sound plausible to the experts in the forum? thanks!
~sholom
Yes, It is proven by myself and others that sometimes GFI's in series do not play nice. I believe it has to do with the quality of the GFI's. Your RV has GFI circuits.

There is nothing in the NEC that says your 30 amp outlet must be GFI protected. Remove the GFI at the shore power and your problem will go away.
__________________
2011 Keystone Sprinter 323 BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is offline   Reply With Quote
Old 11-17-2019, 04:00 PM   #38
Senior Member
 
Join Date: May 2019
Posts: 181
All these difficulties with gfi have me a bit concerned. I'm having a 50A outlet installed by my driveway and I'm sure the electrician will want to install a gfi breaker. I'm not looking forward to that discussion to convince him it's a feeder circuit and not a branch circuit and hence gfi is not required.

I've been reading about ground/neutral bonding on RVs and have no idea how mine is setup. Some posters have indicated that they always trip a gfi shore power connection and so I've started to look at my equipment.

Much to my surprise, my Freedom 458 dynamically manages bonding. While inverting or off, ground and neutral are bonded. When connected to shore power, the bonding is lifted. This is the last thing I expected and should work perfectly.

We'll see.
__________________
2003 Rexhall Vision DP
RVingNow is offline   Reply With Quote
Old 11-17-2019, 04:29 PM   #39
Senior Member
 
Join Date: May 2019
Posts: 181
So two quick comments regarding this bonding / gfi issue. 1. In none of the discussions I've been reading has anyone mentioned that the bonding is / might be dynamic based on the inverter mode and 2. The dynamic nature introduces another failure point which could unexpectedly go bad. Like after a few days boondocking. It worked when I left, but now...
__________________
2003 Rexhall Vision DP
RVingNow is offline   Reply With Quote
Old 11-17-2019, 07:41 PM   #40
Senior Member
 
Join Date: Jul 2014
Posts: 35,441
Quote:
Originally Posted by RVingNow View Post
All these difficulties with gfi have me a bit concerned. I'm having a 50A outlet installed by my driveway and I'm sure the electrician will want to install a gfi breaker. I'm not looking forward to that discussion to convince him it's a feeder circuit and not a branch circuit and hence gfi is not required.

I've been reading about ground/neutral bonding on RVs and have no idea how mine is setup. Some posters have indicated that they always trip a gfi shore power connection and so I've started to look at my equipment.

Much to my surprise, my Freedom 458 dynamically manages bonding. While inverting or off, ground and neutral are bonded. When connected to shore power, the bonding is lifted. This is the last thing I expected and should work perfectly.

We'll see.
The trick is to have the bonding relay open before the GFCI trips.
twinboat is offline   Reply With Quote
Old 11-18-2019, 03:33 AM   #41
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 3,165
Quote:
Originally Posted by RVingNow View Post
All these difficulties with gfi have me a bit concerned. I'm having a 50A outlet installed by my driveway and I'm sure the electrician will want to install a gfi breaker. I'm not looking forward to that discussion to convince him it's a feeder circuit and not a branch circuit and hence gfi is not required.

I've been reading about ground/neutral bonding on RVs and have no idea how mine is setup. Some posters have indicated that they always trip a gfi shore power connection and so I've started to look at my equipment.

Much to my surprise, my Freedom 458 dynamically manages bonding. While inverting or off, ground and neutral are bonded. When connected to shore power, the bonding is lifted. This is the last thing I expected and should work perfectly.

We'll see.
If the electrician is a real electrician he will not want to install a GFI because it is not required. Feeders and branch circuits have nothing to do with it. The only GFI 240 volt circuits per the NEC at home is on a pool pump/spas. If you have a boat dock on the other hand 240 volt motors are GFI required. A 240 circuit for you motor home is NOT required to be GFI protected.

120 volt 30 amp receptacles are not require to be GFI protected. Only 15 and 20 amp outlets within 6' of a water supply and circuits in the garage area.

All RV's are wired with neutrals and grounds separate. RV's are a sub panels and are required to be separate. All rv's are "set up" as you call it the same.

RV's do not ALWAYS trip the GFI's. Some do some do not. It seams to be a crap shoot with no definitive answer that I have found. It it happens there are two fixes. either plug into a non-GIF circuit or turn off the GFI circuits in the RV.

Inverters do not change neutral and ground bonding.
__________________
2011 Keystone Sprinter 323 BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is offline   Reply With Quote
Old 11-18-2019, 03:40 AM   #42
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 3,165
Quote:
Originally Posted by wa8yxm View Post
A couple of issues with Inverters....

First: I have seen the connections in the terminal box on the inverter get a bit overheated.. A couple of times.

And many inverters have a "Bonding screw".. Now ideally when they are "Pass through" mode, all wires simply pass through, Other than tapping off a bit of power for battery charging and "operations" nothing happens.

but with the bonding screw in place. when it switches to INVERTER mode neutral and ground are bonded.

However, if someone messed in that box... They may have bonded neutral to ground "Full time' I did (And later fixed it)

There are other things that can cause it too.
This is the first I have heard of this. Please explain how this works. It is not NEC code compliant.
__________________
2011 Keystone Sprinter 323 BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts