Inverter/converter tripping GFI

Out of the blue, the inverter in our 2003 Mountain Aire DP has begun tripping the GFI on the dedicated outlet I installed at our home (30 amp circuit) I have isolated the issue to the inverter by the process of elimination, right down to connecting and disconnecting the input and output AC lines on the unit itself. Oddly, it works perfectly when powered by the generator and the
inverter function works fine as well. Head to FL in 4 weeks and dont want to risk having this issue at Fort Wilderness.....

Anyone with a similar experience ? or insight into what the issue may be ?
Thanks !!
__________________

__________________
jwcgc629 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-07-2013, 11:00 AM   #2
Senior Member
 
Excel Owners Club
Join Date: Nov 2010
Location: Farmington NM
Posts: 1,030
Are you sure its not a bad shore power cord or plug? I had a simular issue with a 30 amp cord. My GFI in the coach kept tripping. I finally changed out the shore power cord problem solved. Just a thought.
__________________

__________________
Bill & Char, Farmington NM
Retired Fire Chief
2010 Excel 30 RSO Limited
chief02 is offline   Reply With Quote
Old 01-07-2013, 11:15 AM   #3
Senior Member
 
HHIDan's Avatar


 
Join Date: Mar 2011
Location: Ottawa Ontario Canada
Posts: 679
I am curious, you disconnected AC from the converter on both the input and output. Disconnecting at the input, I suspect the breaker stopped tripping. Did it trip after you disconnected the output of the converter (this would imply the fault might be in the converter itself.) I would have suggested make sure the ground and neutral are tight but by removing them and re-connecting I suspect you made them tight...
You maw want to check ground and neutral in the transfer switch. Those go loose after a while shaking. I know it's downstream from converter but a loose ground might only cause the problem when more current is flowing (converter running).
__________________
DanielB
'06 Mountain Aire 4309
'13 Jeep Wrangler
HHIDan is offline   Reply With Quote
Old 01-07-2013, 03:12 PM   #4
Senior Member
 
Damon Owners Club
Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 13,902
A couple of issues with Inverters....

First: I have seen the connections in the terminal box on the inverter get a bit overheated.. A couple of times.

And many inverters have a "Bonding screw".. Now ideally when they are "Pass through" mode, all wires simply pass through, Other than tapping off a bit of power for battery charging and "operations" nothing happens.

but with the bonding screw in place. when it switches to INVERTER mode neutral and ground are bonded.

However, if someone messed in that box... They may have bonded neutral to ground "Full time' I did (And later fixed it)

There are other things that can cause it too.
__________________
Home is where I park it!
wa8yxm is offline   Reply With Quote
Old 01-08-2013, 03:25 AM   #5
Community Moderator
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 9,806
When on shore power the voltage passes through the inverter to the loads. If the GFCI holds when the output from inverter is open then the problem is after the inverter. If it does not hold the problem is in the inverter.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 350 ISC w/ Banks = 450Hp & 1330# torque
06 Saturn Vue & 06 Chevy Z71 4x4 toads
RV Wizard is offline   Reply With Quote
Old 01-08-2013, 07:38 AM   #6
Junior Member
 
Join Date: Feb 2011
Posts: 3
If you have an amprobe or other current measuring device, i would check the current on both hot and neutral into your rig. If they are the same, I wouldn't worry about it. GFCIs are very sensitive, and will frequently trip for less than 1mA. Futhermore, a gfci is not required on the 30amp outlet on an RV pedestal, and are,rarely seen, because they are so problematic, particularly with a highly reactive load, such as that presented by a converter. Try the same test you did before, Making sure all loads are off, and plug the rig into another cgfi protected outlet in the house. A word of warning- in general I would not recommend plugging ann RV into a 15 amp outlet, as the current inrush on some converters may damage the GFCI. For the purposes of this test, it is worth the risk. HAVE FUN!
__________________
campgroundguy is offline   Reply With Quote
Old 01-08-2013, 08:06 AM   #7
Senior Member
 
HHIDan's Avatar


 
Join Date: Mar 2011
Location: Ottawa Ontario Canada
Posts: 679
A GFCI or GFI is an electrical wiring device that disconnects a circuit whenever it detects that the electric current is not balanced between the energized conductor (black or red) and the return neutral conductor (white). ie current may be going thru your body into the ground, ie can be lethal.

To prevent electrocution, RCDs should operate within 25-40 milliseconds at leakage currents (through a person) of 30 milliamperes, before electric shock can drive the heart into ventricular fibrillation, the most common cause of death through electric shock.

I would say if it used to work and doesn't any more, there is something wrong. Yes it could be the GFI itself. But if the GFI is detecting a difference between hot and return, then current is getting lost somewhere.

I was once told that electric panels in RV's used to have the neutral and the ground bonded together (like in your house). This would definitely trip a GFI upstream. Quite sometime ago, it was decided that an RV should be treated the same as an "appliance" with no bond in the panel. This might be why an inverter/converter has a "bonding plug" that is usually removed as it should be.

jwcgc629 please let us know how your situation was resolved...
__________________
DanielB
'06 Mountain Aire 4309
'13 Jeep Wrangler
HHIDan is offline   Reply With Quote
Old 01-11-2013, 09:47 AM   #8
Member
 
Join Date: Dec 2011
Location: Virginia
Posts: 40
Thanks for all the input...... This problem just arose after a single night of dry camping with the genset running most of the night. I have had the 50a (with a 30 amp breaker) outlet in place for a couple of years.....used it with our 5th wheel with no issues and with no issues with the Mountain Aire until returning home from our overnight DC....

Disconnecting the input line to the inverter eliminates the issue....doesnt matter if the output lines are connected or not, so the problem would appear to be in the inverter. The odd thing is that is charges and inverts with no issues when dry camping, so I am a bit suspect of the transfer switch. I have checked and redone all the connections at the inverter....I guess we look next at the TS......I have also rigged a cable to connect the inverter to a non GFI outlet in my home to see if it will operate correctly. I dont want to show up at Fort Wilderness and have it kick the 50a GFI on the pole....
__________________
jwcgc629 is offline   Reply With Quote
Old 01-11-2013, 11:03 AM   #9
Senior Member
 
Join Date: Feb 2010
Posts: 1,179
Leakage...

The inverter may have internal leakage.

Verify the green safety ground never is connected to the neutral white wire.

Unplug shore line and ohm out between green and white.

Can open load Center inside coach and do same.

Lift the white wires one at a time until reading goes from connected to open.

Do this while UNPLUGGED AND TURNED OFF, make sure no wire has voltage present first
__________________
Tony & Lori
1989 Country Coach Savannah SE
TQ60 is offline   Reply With Quote
Old 01-11-2013, 11:37 AM   #10
Senior Member
 
dsbike's Avatar
 
Winnebago Owners Club
Join Date: Jan 2010
Location: Concord, NC
Posts: 1,253
When I was having problems with my converter I found Best Converter to be a lot of help. Bestconverter.com call and ask Randy he seemed very knowlegable on rv electrical systems and has god prices if you actually need to replace something.
__________________
Dan Sees, Concord, NC & Where ever the DW is working
2013 Winnebago Journey 42e, 2008 Mazda MX5,
2008 Toyota FJ Cruiser
dsbike is offline   Reply With Quote
Old 01-11-2013, 02:15 PM   #11
Senior Member
 
Mrchips's Avatar
 
Join Date: Nov 2012
Posts: 400
You are having essentially the same issue as I am, and I also own a MADP. I don't know what inverter/charger you have. Mine is a ME 3112 Mangum, after talking to Magnum tech support who were great the walked me through alot of tests and determined my charger was bad and that is what keeps tripping my 20a breaker. I am waiting on the service center to finish bench testing so that we can figure out the way forward. Like you, mine works fine on gen or 50a CG power as well as inverts properly.
__________________
Command Master Chief (USCG, RET)
2007 American Coach Eagle 45H
2012 Victory Cross Country Tour (motorcycle)
Mrchips is offline   Reply With Quote
Old 01-12-2013, 10:16 AM   #12
Member
 
Join Date: Dec 2011
Location: Virginia
Posts: 40
My unit is a Trace Engineering (Xantrex) RV2012....going to take advantage of the crazy warm weather we are having in VA this weekend (70 today) to do some major troubleshooting... Thanks
__________________
jwcgc629 is offline   Reply With Quote
Old 01-12-2013, 11:03 AM   #13
Member
 
Join Date: Dec 2011
Location: Virginia
Posts: 40
TQ60.....inverter neutral (all inputs and outputs disconnected) to ground reads open....
neutral to hot reads 268 ohms which would appear to be the primary winding the the
converter (charger) Off to test some more...
__________________
jwcgc629 is offline   Reply With Quote
Old 01-12-2013, 11:48 AM   #14
Member
 
Join Date: Dec 2011
Location: Virginia
Posts: 40
Just connected the inverter directly to a 20a GFI outlet via a 12ga extension cord...no trip...functioning fine, so the problem must lie in the MH wiring....will start with the transfer switch, as that would seem to have the only moving part that could fail suddenly.....still open to suggestions, just glad the problem isnt the inverter itself...pricey to address.
__________________

__________________
jwcgc629 is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 12:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2014, vBulletin Solutions, Inc.