Quote:
Originally Posted by OldJohnT View Post
Had I arrived earlier I would have recommended at least a 1000 Watt PSW Inverter,,,,,,,,,,,,, At least 100 Watts of Solar (preferably two in series for 200 Watts) no way Id mess with a wimpy measely 50 watts, that will barely charge a rubber chicken lol,,,,,,,,,,,,, a "Smart" 3/4 Stage MPPT Solar Charge Controller,,,,,,,,,,,,,, At least two 6 volt true deep cycle golf cart batteries in series.


Now lets do the math. A 1000 Watt Inverter operating at 12.6 volts would draw 1000/12.6 = 80 full load amps. Therefore, I would size the conductors from batteries to Inverter to have a minimum ampacity of 100 amps and Id locate it as close as possible to the Inverter to reduce line voltage drop but NOT (its a potential spark producing electrical device) in the same compartment as the battery where explosive gasses may be present during a high charge. I would use an overcurrent protection device to protect the wires located right at the energy source, the batteries and if it were rated at 80 amps it will limit the Inverter to drawing near its capacity plus adequately protect the wire. NOTE if the Inverter company recommends larger then 100 amp rated wire, fine bigger is better and reduces voltage drop. I still wouldn't use les then 100 amp rated wire however. NOTE the battery box needs adequate ventilation to vent the explosive gasses to the outside plus prevent overheating.



John T Retired Electrical Engineer


You forgot to adjust for efficiency. It will be more than 80 amps. ;-)

OTOH he may never need the 1000 watts. ;-))
nothermark is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-29-2015, 06:51 PM   #16
Member
 
Join Date: Jul 2011
Posts: 30
Had I arrived earlier I would have recommended AT LEAST a 1000 Watt PSW Inverter,,,,,,,,,,AT LEAST 100 watts of solar, preferably 200 wired in series for 24 volt operation, no way Id use a wimpy 50 watts, that's not enough to charge up a rubber chicken lol,,,,,,,,,,,,,, A "Smart" 3/4 Stage MPPT Solar Charge Controller,,,,,,,,,,,,,,,, AT LEAST two 6 Volt true Deep Cycle Golf Cart Batteries in series which yields around 200+ Amp Hours of stored energy,,,,,,,,,,,,,,I assume you already have a "Smart" 3/4 Stage Charger????????????

Now to the Inverter, here's how I was NEC trained to approach it:

A) Compute the load. A 1000 Watt Inverter operating at lets use 12.6 volts would draw around 80 full load amps.
B) SIZE THE WIRE I would size the wire to have an ampacity of at least 125% of the max continuous current, meaning Id use at least 100 amp rated wire from batteries to Inverter, BUT IF THE VENDOR SAYS USE BIGGER WIRE THEN USE IT BY ALL MEANS bigger wire = less voltage drop.
C) Size the overcurrent protection device to protect the wiring meaning it would be 100 amp rated

HOWEVER that assumes the Inverter has its own built in thermal protection such that if it draws much over 80 amps very long it will open to protect the Inverter. If such were not the case I may consider use of an 80 amp breaker AT THE ENERGY SOURCE BATTERIES, NOT DOWNSTREAM.

NOTE Id place the Inverter as close as possible to the batteries to reduce voltage drop in the cable HOWEVER NOT in the same compartment as the batteries where explosive gasses may be present especially during high charge rates. The battery box needs adequate ventilation to exhaust the explosive gasses to the outside plus provide some cooling

John T Retired AC Distribution Electrical Engineer
OldJohnT is offline   Reply With Quote
Old 05-29-2015, 07:02 PM   #17
Member
 
Join Date: Jul 2011
Posts: 30
nothermark, you asked

You forgot to adjust for efficiency. It will be more than 80 amps. ;-)

I used the 1000 watts as max INPUT energy and since no device is 100% efficient due to heat losses, the output would be a tad less then 1000 watts. If the device can produce 1000 watts OUTPUT, then it would take MORE then 80 amps on its input I AGREE WITH YOU. I see so many devices with hyped up advertised ratings, I'm used to figuring on the conservative side to be safe, just how I'm wired lol

Thanks for the input, no pun intended lol I used 1000 watts INPUT instead of 1000 watts OUTPUT.

John T
OldJohnT is offline   Reply With Quote
Reply

Tags
inverter, solar



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Installed inverter & solar, now what? Flanagan Going Green 11 12-13-2014 06:50 PM
Freedom 458 inverter voltage fluctuation Oakviewjeff RV Systems & Appliances 2 11-29-2014 09:27 PM
Solar Installer in Orange County California twohsieh Going Green 25 11-08-2014 10:57 PM
Solar help please GSGracie RV Systems & Appliances 10 03-15-2014 03:48 PM
Dimensions 2000Watt Inverter LJowdy Winnebago Industries Owner's Forum 8 02-10-2014 05:23 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:19 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.