Quote:
Originally Posted by RJay
All inverters have an efficiency rating falling somewhere between 80 to 90%. The more expensive inverters have a higher efficiency. Assuming an efficiency of 90% for the OP's inverter the most that can be expected at the output is 13-14 amps continuous and 27 amps short time.
|
It is amazing some of the things I see here.
Yes, 90 percent it typical of inverter efficenties
That does not mean that I should multiply my Prosine 2.0's rated 2000 by 90 percent to get 1800 max. It means that if it's sucking 2200 watts out of the batteries,, It's delivering 1980 watts to the loads.
Work it out,
You have confused input with output.
For the original poster:
The microwave draws like 1100-1300 watts RUNNING, the starting surge can be a real kick but the inverter should haul the load.
The coffee maker is likely a few hundred watts less and again the initial surge, though longer, is way slower.
HOWEVER... I think 4/0 is the recommended short run 12 volt cable for my Prosine. your 1.8 kw should likely use about the same size. I deciced to upgrade my cable after some initial issues.
Go to the manual, measure your cable run, choose 1-2 sizes larger cable, TAPE THE TWO CABLES TOGETHER, run both cables back to the battery save for the Positve cable should run to a "T" fuse of the size specified in the manual near the battery. Keep the run as short as possible and keep the wires taped together as much as possible.
Beyond that clean all connections.. Note that at 1.8 KW.. two pair of golf car batteries in good condition might be a better idea.