LPG for coach, and generator, or both...

Have a new fiver, five tanks. This is the basic setup that I can see:

Click image for larger version

Name:	RV gas now.jpg
Views:	60
Size:	59.2 KB
ID:	235387

About to install a new Onan LPG genset.

Comments I've heard: "You can run anything else when you're running the generator, there's not enough gas".

Onan recommends going at the start of the chain for the same reason, and kind of hints at turning everything else off hard in case the gas being consumed starves something else out.

Another post here mentioned having a dedicated LP system for the generator.

So, I thought of this:

Click image for larger version

Name:	RV gas future.jpg
Views:	55
Size:	75.0 KB
ID:	235388

Seems like with a couple of Y valves I could dedicate one take to generator and the rest to coach, vice versa, or almost anything. Is is a Bad Idea, or even hard?

Thanks, all!
__________________
2020 Ford F-350 6.7l 4x4 SRW LB
2019 Palomino Columbus 289RL
2003 Thor Jazz 2780BH (sold)
manowell is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-18-2019, 06:11 PM   #2
Senior Member
 
Unplanned Tourist's Avatar
 
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: May 2016
Location: Kamloops, BC, 60 miles from the Center of the Universe according to the Rinpoche, of the SF monks.
Posts: 7,305
Most likely your regulator is not made to flow enough for the genset and other loads. Talk to a propane shop about getting one with higher flow, not higher pressure.
Happy Glamping.
__________________
Happy Glamping, Norman & Elna. 2008 Winnebago Adventurer 38J, W24, dozens of small thirsty ponies. Retired after 40 years wrenching on trucks! 2010 Ford Ranger toad with bicycles or KLR 650 in the back. Easy to spot an RVer, they always walk around with a screwdriver or wrench in one hand!
Unplanned Tourist is online now   Reply With Quote
Old 02-18-2019, 10:30 PM   #3
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,643
Standard RV LP Regulator has a 160,000btu flow rating


SO....
40K btu furnace
12K Water heater
9k and two 5k stove top burners
2k oven
2k fridge
2k outside grill


That's 77,000 btu/hr demand (IF you ran everything at same time)


5.5K Onan LP Gen
.8 gallon/hr at half load & 1.1 gallon/hr at full load
1 gallon propane has 91,600btu


77,000 plus 91,600 -------168,600 btu demand (runnign everything at same time)


SO Two standard 160k btu 2 stage LP Regs on a split system WILL handle the demand
One side primary for RV and one side primary for gen with cross tie so either can supply RV and/or Gen


High capacity auto changeover regs are also available in 350k and 400k flow rates
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is online now   Reply With Quote
Old 02-19-2019, 06:52 AM   #4
Senior Member
 
Join Date: Aug 2016
Location: Payson, AZ
Posts: 1,270
what you are thinking would obviously work. but you may need to install another regulator so that each tank feeds a low pressure regulator. in your diagram i believe the regular on the 30 lb tank is a high pressure regulator. but before you go to the effort to do it i'd just get the generator installed and then install the dedication valves if you find that you are actually starved for lpg fuel. for what it's worth we have a lpg onan 5500 and have not yet run into a situation where we were starved for fuel. but we don't push it to the limits either. we did have a regulator failure but that had nothing to do with the generator.
bigchick is offline   Reply With Quote
Old 02-19-2019, 09:10 AM   #5
Senior Member
 
khocke's Avatar
 
Join Date: Sep 2014
Location: Franklin, NY
Posts: 152
FWIW .. my Sprinter Class C had an LPG Onan genny and had 2 separate regulators. I don't recall if the Onan was on it's own or not, but the coach also had a gas/electric fridge, gas/electric water heater, furnace & stove.
__________________
2019 Winnebago Forza 34T
2022 Airstream Interstate 24GT
khocke is offline   Reply With Quote
Old 02-19-2019, 03:27 PM   #6
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,643
Quote:
Originally Posted by khocke View Post
FWIW .. my Sprinter Class C had an LPG Onan genny and had 2 separate regulators. I don't recall if the Onan was on it's own or not, but the coach also had a gas/electric fridge, gas/electric water heater, furnace & stove.

Motorhomes have stacked LP Regs so one feeds coach and the other feeds the gen
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is online now   Reply With Quote
Old 02-20-2019, 09:52 AM   #7
Senior Member
 
manowell's Avatar
 
Join Date: Jul 2018
Location: Dallas, TX
Posts: 198
Quote:
Originally Posted by Old-Biscuit View Post
40K btu furnace
12K Water heater
9k and two 5k stove top burners
2k oven
2k fridge
2k outside grill
No fridge on gas. Would likely be running nothing on that list while on generator other than the water heater, maybe one or two top burners. Generator will be a little-used use case for us, but there are one or two days a year we're in a location with no shore power and requirement to drive both A/C units. In that case likely none of the other loads. I woudn't be running it in a cold weather situation unless the batteries needed to be recharged to keep the furnace blower spinning.

Quote:
That's 77,000 btu/hr demand (IF you ran everything at same time)

5.5K Onan LP Gen
.8 gallon/hr at half load & 1.1 gallon/hr at full load
1 gallon propane has 91,600btu

77,000 plus 91,600 -------168,600 btu demand (running everything at same time)

SO Two standard 160k btu 2 stage LP Regs on a split system WILL handle the demand
One side primary for RV and one side primary for gen with cross tie so either can supply RV and/or Gen
6.5K Onan QG
0.8 gal/h half load
1.2 gal/h full load

with 2x20 = 1x30 I have 70 lbs LPG, doing full load math that seems like a little more than 13 hours for generators only, and I can't see them running full power more than an hour or two, then half power to maintain. I think I'm good.

Seems like I'll be fine in any case with that math. I need to document the regulators I have. Need to find out size of gas line (looks like heavy rubber at that point) to determine fittings.

Quote:
High capacity auto changeover regs are also available in 350k and 400k flow rates
I'd appreciate any pointers. I like to improve and have spares.
__________________
2020 Ford F-350 6.7l 4x4 SRW LB
2019 Palomino Columbus 289RL
2003 Thor Jazz 2780BH (sold)
manowell is offline   Reply With Quote
Old 02-20-2019, 09:54 AM   #8
Senior Member
 
manowell's Avatar
 
Join Date: Jul 2018
Location: Dallas, TX
Posts: 198
Quote:
Originally Posted by bigchick View Post
what you are thinking would obviously work. but you may need to install another regulator so that each tank feeds a low pressure regulator. in your diagram i believe the regular on the 30 lb tank is a high pressure regulator. but before you go to the effort to do it i'd just get the generator installed and then install the dedication valves if you find that you are actually starved for lpg fuel. for what it's worth we have a lpg onan 5500 and have not yet run into a situation where we were starved for fuel. but we don't push it to the limits either. we did have a regulator failure but that had nothing to do with the generator.

Sounds about like I use case. I like the "install it and see how it goes" approach, I need to find out if there's a gas line for a valve that will be blocked once the genset is in the nose. I'm not dying to pull it back out.
__________________
2020 Ford F-350 6.7l 4x4 SRW LB
2019 Palomino Columbus 289RL
2003 Thor Jazz 2780BH (sold)
manowell is offline   Reply With Quote
Old 02-20-2019, 09:49 PM   #9
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,643
Quote:
Originally Posted by manowell View Post
No fridge on gas. Would likely be running nothing on that list while on generator other than the water heater, maybe one or two top burners. Generator will be a little-used use case for us, but there are one or two days a year we're in a location with no shore power and requirement to drive both A/C units. In that case likely none of the other loads. I woudn't be running it in a cold weather situation unless the batteries needed to be recharged to keep the furnace blower spinning.



6.5K Onan QG
0.8 gal/h half load
1.2 gal/h full load

with 2x20 = 1x30 I have 70 lbs LPG, doing full load math that seems like a little more than 13 hours for generators only, and I can't see them running full power more than an hour or two, then half power to maintain. I think I'm good.

Seems like I'll be fine in any case with that math. I need to document the regulators I have. Need to find out size of gas line (looks like heavy rubber at that point) to determine fittings.



I'd appreciate any pointers. I like to improve and have spares.

Those High Capacity Regs should be used as the 'only' supply for the WHOLE system


Oversizing does NOT make it better....
Regs are used that CAN provide FULL Flow but actually are operating within the mid-range area so reg has ability to control pressure in system


Oversized reg would be operating at the bottom end vs mid-range UNLESS huge demand was placed on it.
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is online now   Reply With Quote
Old 02-21-2019, 08:41 AM   #10
Senior Member
 
manowell's Avatar
 
Join Date: Jul 2018
Location: Dallas, TX
Posts: 198
Quote:
Originally Posted by Old-Biscuit View Post
Those High Capacity Regs should be used as the 'only' supply for the WHOLE system

Oversizing does NOT make it better....
Regs are used that CAN provide FULL Flow but actually are operating within the mid-range area so reg has ability to control pressure in system

Oversized reg would be operating at the bottom end vs mid-range UNLESS huge demand was placed on it.
Not really interested in over-sizing, but auto-fail over. RIGHT-sizing. I've order a set of Mopeka Tank Check monitors, have read good things about them. If they're accurate enough that allows advance planning to not need auto-switch or just leaving all the valves feeding. I like a reserve somewhere.
__________________
2020 Ford F-350 6.7l 4x4 SRW LB
2019 Palomino Columbus 289RL
2003 Thor Jazz 2780BH (sold)
manowell is offline   Reply With Quote
Old 02-21-2019, 09:03 AM   #11
Senior Member
 
consolenut's Avatar
 
Join Date: Nov 2014
Posts: 1,345
i dont know that its enough gas. it the demand on the bottle created by the generator. using only one bottle (20lb) it may cause the bottle to freeze and loose pressure. the better alternative is to get a manifold so you can draw from both bottles same time. Larger regulator may cause this to happen sooner. Especially in cold temps.
__________________
08 GMC C-4500 w/Custom bed. 8.1L
45ft 2007 Teton Reliance Experience XT-4
TSLB Trailer Saver w/ 3rd airbag
consolenut is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
2008 Discovery. Replaced oil and filters on both motor and generator and don't know h mrrebel77 Fleetwood Owner's Forum 11 11-10-2018 12:28 PM
Running both electric & LPG to the water heater?? KF5UMC Fleetwood Owner's Forum 16 01-03-2016 02:24 PM
A/C units both work well for 15 t0 45 min then BOTH shut down baustin RV Systems & Appliances 2 09-26-2014 06:57 PM
Which LPG Generator is Best? Kutch's Pack Gear and Product Discussions 7 09-08-2006 03:30 AM
LPG Generator starting dsnook MH-General Discussions & Problems 4 03-07-2005 06:04 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 11:01 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.