No EMS or 110
My MH has the Intellitec 50 amp Smart Energy Management System. All worked fine while on a trip a short time ago. Now, sitting in my driveway, I noticed that the EMS display panel was not lit up. I was plugged into a 20a breaker to maintain batteries. The MH also has a Zantrex Freedom 458 inverter.
I disconnected power and started the generator to see if I would get display. Again nothing on the EMS.
AC's do not work. I do here a click in the ceiling when I turn them on but they will not run, fan only will not run either.
At the Transfer Switch, I have 120v on each line for the Gen. I also see a green indicator light on a board that indicates operational.
At the breaker box I have 120v on each leg of the 50a breaker.
The AC relays located next to the breakers have 120v at each breaker location (CB 1-4). There is no power on the relay side of 1-4, even if I try to start the AC's.
Any advice on the next couple of troubleshooting steps would be appreciated.
|