No Co stands for not cooling. If the control board does not see a change in resistance from the thermistor in a three hour period, the unit will shut down and give this fault code. There are many reasons why it may not be cooling. Turning the unit off and back on will allow it to start over again. If you have tried this and cannot clear it, a reset of the board will be needed. You will want to try to investigate the reason it did not cool first.
Was the coach level when the refrigerator was turned on?
Is the venting up the back and out the roof or side vent free flowing (not blocked)?
Do you smell any ammonia odor?
If using LP gas mode, has the burner assembly been cleaned recently?
We will need to know a lot more info to be much more helpful. Model number and how the unit is vented. Whether you can trouble shoot electrical 120 vac in and out of the control board. Check amperage on heating elements.
__________________

Mike, Certified Master RV Technician
Amy, RV Merchandiser; Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser w/ Banks & 2 toads
|