Old 07-06-2016, 05:24 PM   #1
Junior Member
 
Thor Owners Club
Join Date: Jun 2010
Posts: 27
Onan 4 KW overloaded possible??

Just returned from a 6 day dry camping. Battery was low. It was hot. Generator was on.
Air conditioner was on, Wife was using the convection oven.
I assume the fridge, the Air conditioner, converter charging the battery (55ADC converter spec), and the convection oven were drawing power. Generator died. I threw the breaker on the Converter and switched fridge to gas only and it worked OK.
Is this natural?? Or should I contact Cummings Onan??
Thanks
David
davidspixx is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-06-2016, 05:56 PM   #2
Senior Member
 
Ranger Smith's Avatar
 
Winnebago Owners Club
Ford Super Duty Owner
Join Date: Jul 2012
Location: Where the Rig is Parked
Posts: 1,389
Sounds like you just overloaded the generator with all that running.
__________________
Steve and Joy
2014 Itasca Suncruiser 38Q
Where we are Now
Ranger Smith is offline   Reply With Quote
Old 07-06-2016, 09:05 PM   #3
Junior Member
 
Thor Owners Club
Join Date: Jun 2010
Posts: 27
Naive

I just assumed that the generator included would be capable for all I had installed. Was that naive??
David
davidspixx is offline   Reply With Quote
Old 07-06-2016, 11:03 PM   #4
Senior Member
 
JFXG's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Join Date: May 2012
Location: Today? Clayton, North Carolina
Posts: 5,093
No, not naive, just unfamiliar. Electrical systems and circuits are designed with the assumption that the devices and appliances will not all hit their max load at the same time. The load is measured and limited by current (amperes, or amps). Any electrical thing that has a motor (fans, compressors, pumps) will draw about twice as many amps when starting as when it is stable running. Other devices like your converter or convection oven will cycle from low current draw to high when in use.
When you find yourself in extraordinary times and you're using all these things at once, it's possible that your ac compressor, water pump, converter, convection oven, etc, could all cycle on within a few seconds of each other, and this coincidence would slightly exceed the capacity of the circuit.
What you're seeing is just a very small scale example of why municipal grids experience brown outs on a hot summer day when everyone has their a/c on.


John & Diane, fulltiming since '12 02 DS, FL, Cat, '04 Element NHSO RVM103
__________________
John and Diane (RIP Lincoln, 21 FEB 22) RVM103 NHSO
Fulltimers since June, 2012
2002 Dutch Star 40, Freightliner, Cat 3126,
2004 Element
JFXG is offline   Reply With Quote
Old 07-07-2016, 09:56 AM   #5
Senior Member
 
Join Date: Aug 2014
Location: S.F. Bay Area
Posts: 201
JFXG, has made good points regarding cycling of the loads involved.
However, when I had problems with our 4k, running the A/C and microwave at the same the genny would bog down and die within about 20-30 seconds, The other fine members of this forum pointed out that the 30 amp breaker on the genny should trip before it grinds to a halt if overloaded.
I had mine serviced and it turned out it was running too rich. The tech suspected the genny may have had varnish/debris build up behind the needle valve and the previous owner had continued to open it up the mixture valve. Then when the debris cleared it started running too rich. I adjusted it several more times and it run perfectly since.
Considering the number of loads that were in use, it is possible it overloaded. Try it under several different loads and see how it handles it. If it gets worse, have service center look it over. Good luck!
Percival6 is offline   Reply With Quote
Old 07-07-2016, 03:53 PM   #6
Senior Member
 
tderonne's Avatar
 
Join Date: Dec 2003
Location: Motor City, Mich
Posts: 3,366
And keep in mind that the 30 amp breaker on the generator limits its output to 3600 watts (120 volts x 30 amps). I agree though, you'd think that would have tripped before the generator would stall.
__________________
Tim.

tderonne is offline   Reply With Quote
Old 07-08-2016, 08:58 AM   #7
Junior Member
 
Thor Owners Club
Join Date: Jun 2010
Posts: 27
Power vs. Altitude

I was reminded by Cummings that there is a 3.5% power decrease for every 1000 feet of altitude. I was at 7600 feet at the time. If I go from sea level, that is just over 3000 Watts.
David
PS My altitude knob on the generator was set to max. (I think 5000 feet)
davidspixx is offline   Reply With Quote
Reply

Tags
onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Information about tires - overloaded Renipladlo Alpine Coach Owner's Forum 2 08-18-2011 10:55 PM
Is it any wonder 1/2 ton trucks get overloaded? NLOVNIT Trailer Towing and Tow Vehicles Discussion 36 04-25-2011 08:36 AM
I can feel this coming...boy you is overloaded!!!! VeryHappy Trailer Towing and Tow Vehicles Discussion 12 11-18-2007 03:06 PM
RV Insurance and Overloaded Vehicles LIKENIT iRV2.com General Discussion 11 09-19-2006 02:48 PM
Just a bit overloaded Two Bit RV'ing Humor & Crazy but True Stories 3 08-19-2006 06:52 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:07 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.