Old 06-28-2009, 07:08 PM   #15
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,697
I agree with Mike - something is overloading the inverter that is pushing the 80+ amps and it shuts itself down. Typically that would mean a shorted cell in one or more of the batteries, but any short in the battery wiring could do it to.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-28-2009, 10:22 PM   #16
Senior Member
 
slabman's Avatar
 
Freightliner Owners Club
Join Date: Oct 2002
Location: Fairview TX
Posts: 2,463
Are you guys of the opinion 80+ amps is too high? When I had the old batteries in there I'd always get from 80-110 amps going into those batts. I don't think this is the real problem, though. I've cut the charge amps down to 40-50 amps and the inverters/chargers still do the same thing with these new batteries.
__________________
Slabman
2019 Newmar Ventana 3717
2007 Lexus LX470 Toad
slabman is offline   Reply With Quote
Old 06-29-2009, 10:54 AM   #17
Senior Member
 
hamguy's Avatar
 
Workhorse Chassis Owner
Join Date: Nov 2003
Location: Mesa, AZ USA
Posts: 1,806
Bob, how did you reduce the charge current?

Quote:
Originally Posted by slabman View Post
Are you guys of the opinion 80+ amps is too high? When I had the old batteries in there I'd always get from 80-110 amps going into those batts. I don't think this is the real problem, though. I've cut the charge amps down to 40-50 amps and the inverters/chargers still do the same thing with these new batteries.
__________________
Wretched excess is just barely enough.

2002 Itasca Suncruiser - WH Chassis - 35U - 2006 Jeep Liberty
hamguy is offline   Reply With Quote
Old 06-29-2009, 01:08 PM   #18
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,697
80 amps is a bit high for bulk charge mode on a 4 battery bank - typically a 400 amp-hour battery bank should charge at about 50 amps in the preliminary (bulk) charge phase. Different experts have different numbers, but most say the max charge rate should be between C/10 and C/5, where C is the total amp-hours in the battery bank. 80A would be about C/5. The fact that you say it sailed right up to 80A-90A suggested to me that it was headed beyond that and quickly shut itself down. Had it stabilized at 80A I would have raised an eyebrow but probably not commented on it.

I notice you also say the inverters switch from charging to inverting and back. That seems bizarre. If shore or genset power is present, they should not indicate "inverting". If you see 80A and "inverting", that means to me the Magnum is pulling power from the batteries at a rate of 80A. Comments?
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 06-29-2009, 06:13 PM   #19
Senior Member
 
slabman's Avatar
 
Freightliner Owners Club
Join Date: Oct 2002
Location: Fairview TX
Posts: 2,463
For Hamguy...there is a setting called "percent charge" on the Magnum control panel and I can simply change that setting to around 50% and the charging amperage drops accordingly.

Gary, perhaps I didn't make myself clear. I wouldn't want to check/verify generator function when plugged in....so no, the 80 amps related to CHARGING is current going into the batteries from the generator. I think I also mentioned I have checked this problem using charge input amperages ranging from 20 to the max, which happens to be a bit over 100A. When the coach was new I would regularly find amps over 100 under charge, so I didn't think this was anything too out of the ordinary. The tech people at Travel Supreme said this was fine, although I'm with you...I'd like to keep it at C/5 to C/10.

Bottom line...The point I'm trying to make is it doesn't matter where I set those charging amps from the generator, the inverters/chargers cycle on and off for some reason and I don't know why. It seems the Magnums just don't like something, either input or output and are cycling from charge to invert as a result. To me, this would be consistent to an overload or error condition and this is some kind of self-protective measure built into them. And again, the Magnum guys were convinced this was NOT a Magnum product problem as their products either work or they don't.
__________________
Slabman
2019 Newmar Ventana 3717
2007 Lexus LX470 Toad
slabman is offline   Reply With Quote
Old 07-06-2009, 09:35 PM   #20
Senior Member
 
slabman's Avatar
 
Freightliner Owners Club
Join Date: Oct 2002
Location: Fairview TX
Posts: 2,463
I finally got under there and pulled the covers to both Magnums. With shore power off and the gen running, I measured 118.0v and 121.5 V RMS on the respective inverter inputs from the generator. Frequency was 60.5 HZ. Output voltages were essentially the same voltage...maybe a tenth less.

So then I went in and turned off the inverters and found the system to be charging continuously-the inverters not tripping out and the roof A/C's running, other loads applied, etc. But when turning the inverters to "on", they trip on/off, of course. Then I turned off the two 30 amp breakers downstream of the inverters' output and they still cycled on/off....however, for a brief second one of the remote display panels flashed in RED the words "A/C Overload". Again, this was with generator running and no shore power, inverters on and both downstream subpanel breakers (load) off.

So this appears to tell me the generator is OK, the transfer switch is fine, wiring to the inverters is OK, but something perhaps in the Magnums is amiss. If turning off the load downstream from the inverters doesn't help, it would appear downstream wiring is also OK.

Does this shed any light on the situation? I think I need to call Magnum once again and see what they think.
_________________
Bob J. from TX 2007 Travel Supreme Alante 45MS14 2006 Lexus LX 470 Toad Report Post
__________________
Slabman
2019 Newmar Ventana 3717
2007 Lexus LX470 Toad
slabman is offline   Reply With Quote
Old 07-07-2009, 02:56 AM   #21
Moderator Emeritus
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,060
Your getting warmer!
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Old 07-08-2009, 04:47 PM   #22
Senior Member
 
slabman's Avatar
 
Freightliner Owners Club
Join Date: Oct 2002
Location: Fairview TX
Posts: 2,463
I finally got to talk to another guy at Magnum who went through settings on my remote display panel. He had me lower the normal settings for "A/C Cutout Voltage" from 100V to 80V. Now under generator power the inverters/chargers run just fine with no cutting in/out. While I'm ecstatic the issue seems to be resolved, I'm a little miffed the first two guys I spoke with DID NOT find anything wrong with those settings I was operating under. I asked him why I should think to operate under such a low figure as 80V. when clearly the generator was putting out about 120V...who woulda thunk it? He said that was just the way it was and sometimes that is what was required to make the inverters perform properly. So be it......

My thanks go out to all on this board who exerted their brain power in trying to resolve this issue-I truly appreciate all the input. It's nice to have so many offering their sincere efforts to resolve issues such as this....
__________________
Slabman
2019 Newmar Ventana 3717
2007 Lexus LX470 Toad
slabman is offline   Reply With Quote
Old 07-09-2009, 03:13 AM   #23
Moderator Emeritus
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,060
Glad to hear that you have it working Bob. Keep us up dated if anything changes.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan 5.5 Marquis gold gas, shuts down at 15 min Shamong Shepherds MH-General Discussions & Problems 12 08-27-2008 05:39 PM
Onan Generator Quits On Start With No Load Birddog Pilot Alpine Coach Owner's Forum 26 08-11-2008 10:49 AM
Onan to Unveil the Next Generation of RV Power Solutions at RVIA DriVer Class C Motorhome Discussions 1 11-25-2006 01:52 PM
Onan Problems Stretch Alpine Coach Owner's Forum 12 06-23-2005 06:02 PM
High dollar ONAN Quiet Diesel not worth it! Dale Tomlinson Winnebago Industries Owner's Forum 2 05-17-2005 06:24 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:53 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.