Onan Generator Question
Hello
I have an Onan BGM Marquis I am wiring it to its own Power panel. The panel consists of an RV 50A plug and a 20A GFI. I know the RV 50A power plug and how it works. My question is this. The generator has a pair of 25A breakers on the side. No big deal. The question lies in the fact that It has the pair of hots which I expected. But the snag is it has a pair of neutrals as well. And the ground which is green. When I put the meter between the two neutrals they oHm out to 0. So can I tie the two neutrals on the generator together. Twist them together and connect to the neutral bar in the panel. I would like to use both 25A legs to feed the 50A plug in the box.
As a side note I do know that with the generator running. If you meter the two hot legs together like in a pedestal. They only read 120. So there not out of phase like in the pedestal.
Any information gladly appreciated
__________________
08 GMC C-4500 w/Custom bed. 8.1L
45ft 2007 Teton Reliance Experience XT-4
TSLB Trailer Saver w/ 3rd airbag
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
10-24-2016, 08:48 AM
|
#2
|
Senior Member
Winnebago Owners Club Freightliner Owners Club
Join Date: Oct 2009
Location: E WA or S TX
Posts: 4,046
|
My Service Man. for the HDKAJ, HDKAK, HDKAT shows the Neutrals tied together internally. I expect your ohm meter is telling the same.
__________________
04 Horizon QD, 12 Ford Flex, Excalibar, Brakemaster, Winter Texan, RVin! since 1974
Norm, Donna & Tinker Kat(RIP) 01 Z3
Life is a Timed Event, you only get One Go Around!
|
|
|
10-24-2016, 06:50 PM
|
#3
|
Senior Member
Join Date: Nov 2015
Posts: 335
|
You don't get 240 out of the Onan rv product line. The commercial mobile you can. The rv line is usually green, while the commercial mobile units are white.
__________________
2016 Fleetwood Bounder 36E
|
|
|
10-25-2016, 07:27 AM
|
#4
|
Senior Member
Join Date: Nov 2014
Posts: 1,345
|
I understand no 240. But in a pedestal if you put a meter between the two vertical spades you get 240. Its only 120V per leg and never 240 in the rv. I was just saying that between the two hot legs on the generator I only see 120 so that indicates there in phase the opposite of the the rv pedestal. If my thinking is correct Each leg to ground is 120V to clear up confusion if any in my wording.
__________________
08 GMC C-4500 w/Custom bed. 8.1L
45ft 2007 Teton Reliance Experience XT-4
TSLB Trailer Saver w/ 3rd airbag
|
|
|
10-25-2016, 09:03 AM
|
#5
|
Senior Member
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,587
|
Quote:
Originally Posted by consolenut
I understand no 240. But in a pedestal if you put a meter between the two vertical spades you get 240. Its only 120V per leg and never 240 in the rv. I was just saying that between the two hot legs on the generator I only see 120 so that indicates there in phase the opposite of the the rv pedestal. If my thinking is correct Each leg to ground is 120V to clear up confusion if any in my wording.
|
What you are proposing to do should work ok. Just be aware that, unlike true 50/240 power, if you run close to max on both legs you will have nearly 50 amps on the neutral. If you wire up with 6 AWG you will be ok.
The Onan QD 10kw and 12.5kw do produce 50/240 and can be used as such if needed.
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
|
|
|
10-25-2016, 10:11 AM
|
#6
|
Senior Member
Join Date: Nov 2014
Posts: 1,345
|
Max amps is 41.7 according to the manual but I won't pull max power. One air conditioner and the norm appliances TV etc if I'm on Genny power. Refrig to gas, water heater to gas. Bare necessities lol
__________________
08 GMC C-4500 w/Custom bed. 8.1L
45ft 2007 Teton Reliance Experience XT-4
TSLB Trailer Saver w/ 3rd airbag
|
|
|
10-25-2016, 10:21 AM
|
#7
|
Senior Member
Country Coach Owners Club Solo Rvers Club iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
|
Quote:
Originally Posted by pchuckie
You don't get 240 out of the Onan rv product line. The commercial mobile you can. The rv line is usually green, while the commercial mobile units are white.
|
Actually you can, but they are the 10K and 12.5K units and they are green too. I have the 12.5 unit and the 240 is needed to run my dryer.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|