Quick generator start (AGS)

I don’t use the Auto Generator Start(AGS) function very often. While in for yearly maintenance I set the AGS to auto start not knowing how long we would be there. I went to retrieve some paper work and the generator was running. With the AGS set up as recommended the generator auto started after about 30 minutes on the batteries. This seems really quick with only the refrigerator on. The battery initial voltage is 13.2 VDC. Specific Gravity readings are 1.300 in all cells. I have the model MS2812 standard remote control / ME-AGS-N network, ME-RC remote control and MS 2812 series pure sine wave inverter/charge. Maybe I’m set too conservative or is this an indication of the batteries declining?

The ME-AGS-N is setup like this.

Run time (2.0 hours), Start Temperature (80 deg.), Start volts (12.2 volts), Quite time (OFF), Mode (Other)

The ME-RC is setup like this.

Searching watts (OFF), LBCO (12.0 VDC), Absorb time (1.5 hours), Battery type (Flooded),
Charge rate (80%), VAC dropout (80 VAC), Final charge setting (Multi)
__________________
2016 Newmar Ventana 4002
2020 Jeep Gladiator
stang37 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-14-2018, 04:30 PM   #2
Senior Member
 
lllkrob's Avatar
 
Join Date: Nov 2008
Posts: 3,648
Quote:
Originally Posted by stang37 View Post
I don’t use the Auto Generator Start(AGS) function very often. While in for yearly maintenance I set the AGS to auto start not knowing how long we would be there. I went to retrieve some paper work and the generator was running. With the AGS set up as recommended the generator auto started after about 30 minutes on the batteries. This seems really quick with only the refrigerator on. The battery initial voltage is 13.2 VDC. Specific Gravity readings are 1.300 in all cells. I have the model MS2812 standard remote control / ME-AGS-N network, ME-RC remote control and MS 2812 series pure sine wave inverter/charge. Maybe I’m set too conservative or is this an indication of the batteries declining?

The ME-AGS-N is setup like this.

Run time (2.0 hours), Start Temperature (80 deg.), Start volts (12.2 volts), Quite time (OFF), Mode (Other)

The ME-RC is setup like this.

Searching watts (OFF), LBCO (12.0 VDC), Absorb time (1.5 hours), Battery type (Flooded),
Charge rate (80%), VAC dropout (80 VAC), Final charge setting (Multi)
Reset your start volts to 11.9.
__________________
2024 KZ Durango Gold
lllkrob is offline   Reply With Quote
Old 02-14-2018, 05:10 PM   #3
Senior Member
 
vsheetz's Avatar


 
Fleetwood Owners Club
Ford Super Duty Owner
Join Date: Jun 2012
Location: SoCal
Posts: 15,749
13.2 was likely a charging voltage - not the actual start voltage. See chart I attached.

Setting the AGS start voltage can take some experimental time. Too low a voltage and the genny won't turn over when called - to high and you will get early/nusence starting. Around 12.0 is usually a good voltage.

Click image for larger version

Name:	FB_IMG_1506294056967.jpg
Views:	106
Size:	64.6 KB
ID:	192342
__________________
Vince and Susan
2011 Tiffin Phaeton 40QTH (Cummins ISC/Freightliner)
Flat towing a modified 2005 Jeep (Rubicon Wrangler)
Previously a 2002 Fleetwood Pace Arrow 37A and a 1995 Safari Trek 2830.
vsheetz is offline   Reply With Quote
Old 02-14-2018, 06:02 PM   #4
Senior Member
 
Join Date: Jul 2014
Posts: 35,413
11.9 volts is a popular setting.

Your batteries won't be down to 11.9 volts when the AGS starts, but will momentarily sag to that voltage, under the inverter draw when the fridge kicks on.

The actual battery resting voltage will be higher.
twinboat is offline   Reply With Quote
Old 02-15-2018, 06:20 PM   #5
Senior Member
 
stang37's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Join Date: Feb 2016
Location: Mississippi
Posts: 607
Thanks for the input from all. I will change the start voltage to 11.9. It just seems the batteries voltage should stay up longer with just a fridge drawing off them.
__________________
2016 Newmar Ventana 4002
2020 Jeep Gladiator
stang37 is offline   Reply With Quote
Old 02-16-2018, 05:52 AM   #6
Registered User
 
Join Date: Aug 2014
Location: western NC mountains!
Posts: 4,106
the LBCO(LowBatteryCutOut) should also always be a good bit lower than the start Voltage, maybe 11.5, as this will cut off the Inverter to save the batteries if the AGS fails to start the Generator, a failsafe backup 'just in case'.

the Voltage settings of 11.9 will prompt the AGS to start the generator after 2 minutes at this level.

the TEMP setting seems high, as your coach could be at 80 degrees easily during good weather, whether or not you have incoming electricity or not, it would prompt the AGS to start the generator, running for 2 hours even with incoming power. I would turn that to a very high number, like 90, unless you have pets or folks in there.

If your batteries weren't fully charged(12.8 or so) when you arrived, dropping to 12.2 might happen fairly quickly. Seems like 13.2 is more of a number while the batteries are actually still being charged.


after you've tried the new settings, and if things don't seem to improve, you can 'equalize' the batteries, when on 50a shore power, by pressing the Charger button for several seconds, then the Equalize feature will be started, running for about 4 hours. Check your water levels before you do this.
I've tried this several times over the last 3 years, and it always seems to really extend the battery time during inverter usage.
MisterT is offline   Reply With Quote
Old 02-16-2018, 06:45 AM   #7
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,514
The Magnum AGS manual recommends 11.0 - 11.5. This is mainly for when the inverter is pulling heavier loads. Try running a coffee maker or microwave off the inverter and watch how low the voltage will drop. I've seen mine drop to 11.7V while the actual SOC was around 70%. As soon as the coffee maker was done, it jumped back to 12.3V.
__________________
Scotty and Kristen, Airedales Dagny and Wyatt
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison 4000, 8 Lifeline AGM's
2019 F250 King Ranch 4x4 Powerstroke - SOLD
2022 F350 DRW King Ranch 4 x 4
Scottybdivin is offline   Reply With Quote
Old 02-16-2018, 09:09 AM   #8
Registered User
 
Join Date: Aug 2014
Location: western NC mountains!
Posts: 4,106
right, a coffee maker, like ours, will consume a large amperage while in the 'brewing' or 'percolating' mode, dropping our Voltage level from, say, 12.5 to 11.5 or so, for several seconds, then it jumps back up to 12.5, until the 'brewer' kicks in again, back down to 11.5, etc... but near the end of the cycle, it actually keeps a constant heavy draw and the Voltage stays down near the 11.5 or so... even though it gets through it's brewer cycle 'relatively' quickly - a few minutes depending on how many cups you're making. Once done, the battery Voltage reading might be back up to a more 'normal' 12.3-12.4.... it's used some battery, but not as much as it might seem during the 'temporary' brewing period.

if you set your LBCO at 11.5, and your brewing last more than 30 seconds at that Voltage reading, you may see your Inverter cut out, loosing all inverter power, including the coffee maker...

so, when I know I want to brew coffee while strictly on the Inverter only, I will 'disable' the AGS for those minutes, knowing that the 'temporary' low Voltage reading won't last long, and isn't really dropping the batteries to that level.... it's just a current reading of the draw from the coffee maker.
MisterT is offline   Reply With Quote
Old 02-16-2018, 10:00 AM   #9
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,514
Correct. It could also apply to a microwave, hair dryer, or any other heavy load, assuming you are running off the inverter. Turning off the AGS during those times would solve the problem and allow you to have a higher start voltage. I no longer have to worry about the voltage drop since I use the SOC and temperature parameters for my AGS.
__________________
Scotty and Kristen, Airedales Dagny and Wyatt
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison 4000, 8 Lifeline AGM's
2019 F250 King Ranch 4x4 Powerstroke - SOLD
2022 F350 DRW King Ranch 4 x 4
Scottybdivin is offline   Reply With Quote
Old 02-16-2018, 03:43 PM   #10
Registered User
 
Join Date: Aug 2014
Location: western NC mountains!
Posts: 4,106
what I really should correct is that I turn DOWN the LBCO setting temporarily ... not the AGS.... though, the AGS could also kick on IF the temporary low Voltage during the brewing mode keeps it below for 2 continuous minutes... sorry : )

fun ain't it!?
MisterT is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Magnum ME-AGS-S Standalone AGS mikelm48 Newmar Owner's Forum 3 02-23-2016 08:28 AM
Xanbus Automatic Generator Start (AGS) JoeMoe Fleetwood Owner's Forum 0 06-06-2015 06:17 PM
AGS Issue: 2010 Paeton 40-QTH AGS Issue gjw Tiffin Owner's Forum 1 09-06-2013 04:46 PM
What Exactly is AGS (Automatic Generator Start) Willie300s Monaco Owner's Forum 11 06-15-2013 05:49 PM
AGS Auto Generator Start Jagraves Thor Industries Owner's Forum 9 10-19-2012 07:37 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 06:33 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.