Smile Suburban Furnace SF 35 Problems

I have pulled my furnace out and checked that the igniter is working , fan is running and I checked to see if the orifice was clear, it was, I think the problem is that it's not getting propane, When I took off the propane connection I could smell the propane but it isn't getting to the igniter,everything is very clean . any suggestions? It's in a 2003 Rexhall Aerbus
2seniors is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-23-2019, 01:57 PM   #2
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,820
DO other propane appliances work....Stove top burners, water heater???


Could be furnace gas valve solenoid bad....
*check that it is getting 12V DC at same time ignitor is sparking (gas valve only has power for 6-8 seconds during ignition cycle)
*gets 12V DC then check resistance on solenoid....should be 40-50 ohms


Could be lack of gas flow....if furnace hasn't been used in a while the ignition cycle may take several attempts before full propane flow is established (only 0.4 psi in system) 5-6 attempts common...then should light off w/o issue


Could be bad LP Reg....low system pressure
11"WC is 0.4 psi
9" WC is 0.32 psi
Can NOT visually tell that system is 0.08 psi low....have to measure using a manometer
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 03-23-2019, 02:48 PM   #3
Senior Member
 
Bucky573's Avatar
 
Newmar Owners Club
Join Date: Jul 2014
Posts: 242
Quote:
Originally Posted by 2seniors View Post
I have pulled my furnace out and checked that the igniter is working , fan is running and I checked to see if the orifice was clear, it was, I think the problem is that it's not getting propane, When I took off the propane connection I could smell the propane but it isn't getting to the igniter,everything is very clean . any suggestions? It's in a 2003 Rexhall Aerbus

Go here and download this manual. There is a troubleshooting guide that will walk you through steps to isolate the problem.
I used it on a friends furnace last week to find a faulty limit switch.
http://www.bdub.net/manuals/Suburban_Service_Manual.pdf
__________________
Tom Sawyer
2010 Ventana 4333, Spartan w/Cummins ISC 360HP
Bucky573 is offline   Reply With Quote
Old 03-23-2019, 03:20 PM   #4
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,820
Troubleshooting guides & service manuals are very helpful




OP posted some clues that narrow troubleshooting down to gas valve circuit

Fan runs....spark electrode fires (Sparks)
That means furnace has DC power.......Sail Switch/High Temp Limit switch are closed (only way for DC to get to circuit bd)


Issue is with gas valve
No DC from circuit bd...bad connection/contact or bad circuit bd
Is getting DC from circuit bd.....bad solenoid(s)


Everything else is working.....so gas valve is issue (provided propane is working for other appliances)
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 03-24-2019, 07:39 PM   #5
Junior Member
 
Join Date: Apr 2014
Posts: 27
Furnance

Quote:
Originally Posted by Old-Biscuit View Post
DO other propane appliances work....Stove top burners, water heater???


Could be furnace gas valve solenoid bad....
*check that it is getting 12V DC at same time ignitor is sparking (gas valve only has power for 6-8 seconds during ignition cycle)
*gets 12V DC then check resistance on solenoid....should be 40-50 ohms


Could be lack of gas flow....if furnace hasn't been used in a while the ignition cycle may take several attempts before full propane flow is established (only 0.4 psi in system) 5-6 attempts common...then should light off w/o issue


Could be bad LP Reg....low system pressure
11"WC is 0.4 psi
9" WC is 0.32 psi
Can NOT visually tell that system is 0.08 psi low....have to measure using a manometer



I did get 12V and I heard a click, was that the valve opening? All I did was clean the connections
2seniors is offline   Reply With Quote
Old 03-24-2019, 10:54 PM   #6
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,820
Quote:
Originally Posted by 2seniors View Post
I did get 12V and I heard a click, was that the valve opening? All I did was clean the connections

YES....
Solenoids 'click' 'clunk' make noise when getting energized


Dirty/loose connections will STOP 12V DC
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Reply

Tags
ace, ems, furnace, problem, problems, suburban



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Suburban Furnace Issue Problem also with Suburban Cliffy RV Systems & Appliances 1 10-23-2018 02:09 PM
Suburban NT-45S Furnace or Furnace motor Ronbstewart Monaco Owner's Forum 7 05-25-2018 08:15 PM
Suburban Furnace problems our15allegro RV Systems & Appliances 7 01-14-2016 06:20 AM
Suburban furnace problems heybc RV Systems & Appliances 2 05-04-2011 09:02 AM