The DC wiring diagram is located at the bottom of page 5 of the manual (linked to above)
As shown in the diagram, power from the your coach DC fuse panel is fed to Terminal Board pin 1 (TB-1). Thats the +12V DC Supply red wire.
The documentation says there is a LED mounted on the ignition board (item 13 in parts drawing). It should flash on an error.
The error table (page 5) says the LED will:
DIAGNOSTIC CHART - FAULT LED INDICATION
Internal Circuit Board Failure.............. Steady on, no flashing
Limit switch/Airflow problems............. 1 flash with 3-second pause
Flame Sense Fault........................... 2 flashes with 3-second pause
Ignition Lockout Fault...................... 3 flashes with 3-second pause
I will add........... No lights
1) Internal Circuit Board Failure - Obvious meaning
2) Limit switch/Airflow problems - Command from Thermostat to turn ON recieved however:
__A) Sail switch is not being turned ON. Fan blows air across switch vane causing the switch to turn ON. Either the fan motor is not running, the switch is bad, or there is an air flow blockage (mouse nest, wasp nest, mud dauber nest, etc) blocking air flow through the unit. Fan could be bad or ignitor board bad or fuse (if there is one) on ignitor board blown, or wiring problem.
__B) Limit Switch - defective (opens when furnance is to hot [High temp safety])
3) Flame Sense Fault - Ignitor board does not sense flame - High tension lead is dual purpose. Provides spark voltage to ignite gas then is used to monitor flame condition.
__A) Dirty, misadjusted or worn/broken electrode.
__B) Bad/dirty ignitor lead connections
__C) Defective Ignitor Board
4) Ignition Lockout Fault - 3 failed attempts to light furnace.
__A) Low 12VDC voltage
__B) LP gas tank empty
5) No lights - No Fan operation
__A) No power to furnace from coach DC fuse panel
__B) ON/OFF switch or circuit breaker OFF
__C) Dirty/corroded electrical connection
__D) Defective Ignitor Board
Sequence of Operation:
1) 12VDC from coach DC fuse panel is comes into TB-1 (red wire) and is routed to Switch/CB then:
__A) to ignitor board (red wire) to PWR terminal at top of board
__B) Thermostat (blue wire) via TB-2 (+Thermo)
2) Thermostat is turned on routing 12VDC back (Thermo) to TB-5 and then to (other blue wire):
__A) Sail Switch
__B) Ignitor Board
3) The signal from the Thermostat to the ignitor board tells it to:
__A) Turn on the fan
__B) Check for signal from Sail Switch/Limit switch path. If no signal recieved then shut down and flash Limit switch/Airflow error code.
4) Ignitor board sees Limit switch signal so it waits a few more seconds (purge chamber of residule gas) then commands gas valve open and high voltage ignition spark.
5) Wait 5 seconds then monitor high tension lead for flame sense. No flame sense then set Flame Sense Fault error code then,
6) Go back to Step 3) and retry 2 more times to ignite furnace. If no joy, set Ignition Lockout Fault error code.
To reset Ignition Lockout Fault, turn thermostat OFF for 30 seconds then back ON and furnace will try again.
Make sure gas is ON at tank (good flame at oven top burner? {purge piping system of air by having good flame at stove top; applies to furnace and water heater})
Battery voltage above 12VDC - Fan runs to slow at lower voltage resulting in sail switch not coming ON.
I hope that answers your questions,
Dave