Old 10-10-2006, 10:07 AM   #1
BIGRED1 is offline
Senior Member
BIGRED1's Avatar
Join Date: Apr 2006
Location: Marietta, GA
Posts: 332
I have a 7.5KW Onan diesel gen set in my Monaco Diplomat. I was wondering about the possibility of putting a receptacle on it so that it could be connected to my house for back up purposes during a power outage. Is this feasbile and has anyone done this that could share what was needed to do it?

TIA!

__________________
'00 Monaco Dip 38D

8.3L Cummins ISC
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-10-2006, 10:07 AM   #2
BIGRED1 is offline
Senior Member
BIGRED1's Avatar
Join Date: Apr 2006
Location: Marietta, GA
Posts: 332
I have a 7.5KW Onan diesel gen set in my Monaco Diplomat. I was wondering about the possibility of putting a receptacle on it so that it could be connected to my house for back up purposes during a power outage. Is this feasbile and has anyone done this that could share what was needed to do it?

TIA!

__________________
'00 Monaco Dip 38D

8.3L Cummins ISC
  Reply With Quote
   
Old 10-10-2006, 01:33 PM   #3
Tom N is offline
Senior Member
Tom N's Avatar


Appalachian Campers
Pond Piggies Club
Winnebago Owners Club
Mid Atlantic Campers
Join Date: Dec 2002
Location: Sarver, PA/Crystal River, FL/Hawthorn, PA
Posts: 3,779
You can do this but code requires that you use a transfer switch so it is impossible for the coach generator and the grid power to be hooked to the house at the same time. If you feed power back into the grid you could kill a lineman.
__________________
Sarver, PA/Crystal River, FL/Hawthorn, PA · FMCA 335149 · W3TLN
2005 Suncruiser 38R · W24, no chassis mods needed · 2012 Honda Accord SE · 2008 Honda Odyssey EX-L

  Reply With Quote
   
Old 10-10-2006, 02:58 PM   #4
rhkh is offline
Member
Texas Boomers Club
Join Date: Mar 2005
Posts: 41
I do this sucessfully as follows.
First, I installed a trasfer switch in the motorhome panel that allows the output of the generator to be connected to the shore power cable.
Second, one must disconnect the house from the power grid. I do this by opening the main power disconnect breaker on my house power panel.
Next, start the motorhome generator, flip the transfer switch on the motorhome panel and it will power one leg of the house circuits.
I have to be carefull that I do not put too much load on the generator, else I will pop the generator output breaker.
When our house power goes out I merely power the house from the generator easily. However, none of the house 220 volt loads will operate.
__________________
  Reply With Quote
   
Old 10-10-2006, 04:21 PM   #5
Tom N is offline
Senior Member
Tom N's Avatar


Appalachian Campers
Pond Piggies Club
Winnebago Owners Club
Mid Atlantic Campers
Join Date: Dec 2002
Location: Sarver, PA/Crystal River, FL/Hawthorn, PA
Posts: 3,779
rhkh;

What you are doing is illegal. You need a transfer switch so it is impossible for you to feed power to the grid if you or someone else closes the main breaker on you panel.

Call your local electric provider for further information if you want to be legal.
__________________
Sarver, PA/Crystal River, FL/Hawthorn, PA · FMCA 335149 · W3TLN
2005 Suncruiser 38R · W24, no chassis mods needed · 2012 Honda Accord SE · 2008 Honda Odyssey EX-L

  Reply With Quote
   
Old 10-10-2006, 05:48 PM   #6
NeilV is offline
Senior Member
Join Date: Nov 2005
Posts: 1,910
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by Tom N:
rhkh;

What you are doing is illegal. You need a transfer switch so it is impossible for you to feed power to the grid if you or someone else closes the main breaker on you panel.

Call your local electric provider for further information if you want to be legal. </div></BLOCKQUOTE>


Tom's right you need to make this right before someone gets hurt.

Even with a transfer switch you are still out of code. You never should provide power out the male end of a cord. I had a 50 amp outlet on my last coach which could be used to power a second coach when dry camping or to safely feed a transfer switch on a houses power panel. The outlet was off the 50 amp mains of the coaches power panel and protected by the main breaker in the coach.
__________________
Neil V
2001 Winnebago Adventurer WFG35U
  Reply With Quote
   
Old 10-14-2006, 05:24 PM   #7
Ray,IN is offline
Senior Member
Ray,IN's Avatar


Join Date: Aug 2001
Location: North America somewhere
Posts: 4,925
Tom, Neil, it depends upon what state regulations say. Indiana just says to disconnect from line power before using a genset.
To reinforce your advice though I'll add this: About 25 years ago a diary farmer in North Indiana used his brand new back-up genset to provide electricity for his milk cooling units during a ice storm. He forgot to throw the disconnect switch. When the linemen approached the downed lines up the road, they detected power in them. They used the approved shorting device to deaden the lines, in the process destroying the farmers genset. When the farmer complained to the REMC and demanded a new genset they called the sheriff. The farmer wound up losing his entire dairy business.
__________________
"As nightfall does not come at once, neither does oppression. In both instances there is a twilight where everything remains seemingly unchanged. And it is in such twilight that we all must be aware of change in the air - however slight - lest we bec
  Reply With Quote
   
Old 10-15-2006, 02:45 AM   #8
NeilV is offline
Senior Member
Join Date: Nov 2005
Posts: 1,910
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by Ray,IN:
Tom, Neil, it depends upon what state regulations say. Indiana just says to disconnect from line power before using a genset.
To reinforce your advice though I'll add this: About 25 years ago a diary farmer in North Indiana used his brand new back-up genset to provide electricity for his milk cooling units during a ice storm. He forgot to throw the disconnect switch. When the linemen approached the downed lines up the road, they detected power in them. They used the approved shorting device to deaden the lines, in the process destroying the farmers genset. When the farmer complained to the REMC and demanded a new genset they called the sheriff. The farmer wound up losing his entire dairy business. </div></BLOCKQUOTE>

Ray,

The National Electrical Code is the standard that is usually followed when there is a loss of life or property. The non-complient are found negligent for "failing to adhere to well known best practices for safety". The NEC or NFPA 70 are recognized as the most well know best practices and will be what the courts would most likely follow. Even if the negligent practice was allowed by the local buiding inspector and is allowed in the local buiding code this does not provide absolution.

According to the Encyclopedia writeup on the NEC:

"In the U.S., anyone, including the city issuing building permits, may face a civil liability lawsuit (be sued) for negligently creating a situation that results in loss of life or property."

So while the Indiana State Regs generically says to disconnect from line power before using a genset the "well known best practices for safety" outline how to disconnect from line power.

Putting power out of a male plug end is another matter.

Be safe and follow best practices no matter what poor practices local regs may let you get away with. We only end up cheating ourselves when we cheat on safety.

Kindest regards,
__________________
Neil V
2001 Winnebago Adventurer WFG35U
  Reply With Quote
   
Old 10-16-2006, 10:03 AM   #9
BIGRED1 is offline
Senior Member
BIGRED1's Avatar
Join Date: Apr 2006
Location: Marietta, GA
Posts: 332
So, I should have a transfer switch installed in the house, right? I assume one that would give the utility power priority, but if it wasn't present and the gen set power was it would allow it in? Would this be installed before the utility company's meter? Where would I need to tap into on the gen set to get the power over to the transfer switch?

TIA!
__________________
'00 Monaco Dip 38D

8.3L Cummins ISC
  Reply With Quote
   
Old 10-16-2006, 05:15 PM   #10
rick_od is offline
Senior Member
Join Date: Feb 2006
Location: Central NJ
Posts: 243
The right kind of x-fer switch does the following. It has two switches / breakers on it. One for commercial power and one for genset power. It is designed so that it is impossible to have both on at the same time. ie. when commercial power is on, genset power is off & when genset power is on, commercial power is off. The x-fer switch is placed between the meter and the electrical panel.

__________________
2003 Sightseer 30B riding on a P-32
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gen Set Issue - No House Power Okie Malibu Winnebago Industries Owner's Forum 9 04-28-2008 10:27 PM
gen set Bill Coleman Damon 4 03-24-2008 10:06 AM
Gen. set help trapshooter MH-General Discussions & Problems 7 12-07-2006 03:19 PM
Gen Set "Mystery" BIGRED1 Monaco Owner's Forum 3 11-09-2006 10:07 AM
Gen set= charge house batteries? WALLY NJ Winnebago Industries Owner's Forum 10 01-19-2006 04:58 PM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 07:18 AM.